    Hi everyone. Here's another "can I do this" thread.

    I want to add a utility sink into my basement. Ideally, it will be positioned next to the washer and dryer, and I would like to tie it into the existing drain line from the washer discharge. It currently has 2" Sch. 40 PVC washing machine standpipe and P-trap, going to a Sani-Tee and drain with an AAV on the top, like this (pardon my horrendous drawing):

    Name:  plumbing.jpg
Views: 192
Size:  10.7 KB

    I want to add the sink between the washing machine and the Sani-Tee. I'm thinking Sch. 40 P-trap, trap arm going to a 90 elbow that connects to a combo wye added to the existing drain line. Like this:

    Name:  plumbing2.jpg
Views: 176
Size:  11.9 KB

    Will this work? Is it legal? And will it vent properly? I'm not sure if I'd have to add another AAV between the sink trap and the combo wye. Thanks!

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    The sink trap will get sucked dry when the WM drains.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    What you have drawn is not permitted. You can install another sanitary tee over the existing one and run your sink to it. Both the washer and the sink should be 2" pipe, and the trap to vent distance cannot exceed 5' if it is under UPC.

  4. #4
    DIY Junior Member Sylvester's Avatar
    Join Date
    Jan 2014
    Location
    Maryland, USA
    Posts
    5

    Default

    Cacher_chick, is it not permitted to tie in to the existing WM drain, period? Or just because of the siphoning issue?

    I clearly see what you mean now, Jadnashua.

    Another concern I have is, looking at things now, I might not have the vertical clearance I need anyway. The bottom of the P-trap might be at the level of the existing horizontal drain run. Could I flip-flop the arrangement, and do this?
    Name:  plumbing3.jpg
Views: 131
Size:  10.3 KB

  5. #5
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    You have not one but two illegal S traps. Vents must be in the trap arm prior to the arm turning downward.

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,195
    Blog Entries
    1

    Default



    Putting the sink above the washer works best.
    The washer will always siphon a sink if the sink is below.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    They are NOT "S" traps unless they are connected to the vertical line with Ys or combos. The sink can connect to the horizontal line if the trap is PROPERLY vented. You cannot connect the sink the vertical line UNDER the washing machine, unless you properly vent the sink line to prevent both positive and negative pressures, which means, but definition, you cannot use an AAV.
    Last edited by hj; 02-01-2014 at 07:13 AM.
    Licensed residential and commercial plumber

  8. #8
    DIY Junior Member Sylvester's Avatar
    Join Date
    Jan 2014
    Location
    Maryland, USA
    Posts
    5

    Default

    Quote Originally Posted by Gary Swart View Post
    You have not one but two illegal S traps. Vents must be in the trap arm prior to the arm turning downward.
    Forgive me, my morning coffee is still trying to work in. I thought the S-trap was defined by having too short of a trap arm (not 2x the diameter), not necessarily by its venting.

  9. #9
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    Gary is mistaken. You should be able to lower the sanitary tee for the washer so that the washer trap is lower, and the sanitary tee for the sink will go above the washer's. You do not want a major drain over the top of a minor one.

  10. #10
    DIY Junior Member Sylvester's Avatar
    Join Date
    Jan 2014
    Location
    Maryland, USA
    Posts
    5

    Default

    Quote Originally Posted by hj View Post
    They are NOT "S" traps unless they are connected to the vertical line with Ys or combos. The sink can connect to the horizontal line if the trap is PROPERLY vented.
    To connect the sink to the horizontal line, could I vent the trap arm with an AAV? Given the location, I do not have another way to vent.

  11. #11
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    You could do that, but both of the AAV's need to be installed higher than the flood rim of the higher fixture. Not doing so will cause the AAV's to fail if a backup of laundry suds comes up the vent.

  12. #12
    DIY Junior Member Sylvester's Avatar
    Join Date
    Jan 2014
    Location
    Maryland, USA
    Posts
    5

    Default

    Ok, great. Now, if I did it the other way - basically as I drew most recently but with the sink draining ABOVE the washer - that will be a wet vent of the washer, yes?

  13. #13
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    Correct- it is a vertical wet vent, which is a common practice with a washer and utility sink.

Similar Threads

  1. Adding a utility sink here?
    By coconutpete in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 15
    Last Post: 02-04-2013, 08:46 AM
  2. Adding a utility sink
    By Dbhyslop in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 11-14-2011, 01:11 PM
  3. Adding Utility Sink - Drain and Vent Help Please!
    By jshrop in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 12-30-2010, 03:36 PM
  4. Adding sink in in utility room
    By basementbrewer in forum Remodel Forum & Blog
    Replies: 2
    Last Post: 01-10-2007, 11:27 AM
  5. Adding a utility sink in my Garage
    By manzo in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 03-03-2005, 03:59 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •