Pipe size

Users who are viewing this thread

Yersmay

Writing, constructionDIY Member
Messages
61
Reaction score
0
Points
0
Location
Los Angeles
I have installed new copper under my house... It's a small house so I used 3/4 inch for all main lines and a small amount of 1/2 for risers.

Now I have to run a new line from the street meter to the house foundation and connect it all. The connection at the street meter is 3/4. Would it make any difference to increase to a 1 inch line from the 3/4 inch street meter, have that run to the house foundation and reduce back down to 3/4? Does that increase performance or is it pointless?

Thanks in advance.

Paul
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
I would never run a 3/4" from the meter to the house.

1" is always better.
If you have more than one bath, is required that it be 1" or larger.
Even with the 3/4" meter.

pipe_size_2.jpg



pipe_size_1.jpg


https://terrylove.com/watersize.htm
 
Last edited:

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
It Depends on Demand and Pressure

The required size of pipe depends on flow demands, supply pressure, and length.

A 1/2" pipe, which has an inside diameter of 0.622" (about 5/8") has a pressure loss of about 40 psi per hundred feet of length at 10 GPM.

A 3/4" pipe has an inside diameter of 0.824" (about 13/16") and has a pressure loss of 10 psi per 100 feet at 10 GPM and 20 psi per 100 ft at 15 GPM.

If the length of pipe from meter to your house is 50 ft, you will use 50% of those lossses.

A 3/4 OD tube has an ID of about 5/8" so it is like a 1/2" pipe.

If the street pressure is 100 psi, it probably doesn't matter except that you will notice more pressure loss when the washing machine cycle runs or your sprinkler system comes on. If your street pressure with no flow if only 50 psi, you probably want the larger pipe.
 

Lakee911

I&C Engineer (mostly WWTP)
Messages
1,254
Reaction score
1
Points
0
Location
Columbus, OH
Supersize or Would you like 1in with that pipe for a few bucks more?

FWIW, I have an old house with 1" galvanized from the city, reduced to 3/4 and then to 5/8 for the meter and then 1/2" throughout the whole house.

Shower pressure is so-so to adequete (but its a rainfall too so that doesn't help). Simultanious shower and kitchen sink or toilet or bathroom sink sucks and if the washing machine is on, count anything else out.

I've thought of replacing the easily accessable pipe with 3/4" but its just not really worth it in an old house that I'm going to see in few years.


Jason
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks