    Default Pipe size

    I have installed new copper under my house... It's a small house so I used 3/4 inch for all main lines and a small amount of 1/2 for risers.

    Now I have to run a new line from the street meter to the house foundation and connect it all. The connection at the street meter is 3/4. Would it make any difference to increase to a 1 inch line from the 3/4 inch street meter, have that run to the house foundation and reduce back down to 3/4? Does that increase performance or is it pointless?

    Thanks in advance.

    Paul

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    12,448
    Blog Entries
    1

    Default

    I would never run a 3/4" from the meter to the house.

    1" is always better.
    If you have more than one bath, is required that it be 1" or larger.
    Even with the 3/4" meter.

    http://www.terrylove.com/watersize.htm

  3. #3
    In the Trades Bob NH's Avatar
    Join Date
    Oct 2005
    Location
    New Hampshire
    Posts
    3,308

    Default It Depends on Demand and Pressure

    The required size of pipe depends on flow demands, supply pressure, and length.

    A 1/2" pipe, which has an inside diameter of 0.622" (about 5/8") has a pressure loss of about 40 psi per hundred feet of length at 10 GPM.

    A 3/4" pipe has an inside diameter of 0.824" (about 13/16") and has a pressure loss of 10 psi per 100 feet at 10 GPM and 20 psi per 100 ft at 15 GPM.

    If the length of pipe from meter to your house is 50 ft, you will use 50% of those lossses.

    A 3/4 OD tube has an ID of about 5/8" so it is like a 1/2" pipe.

    If the street pressure is 100 psi, it probably doesn't matter except that you will notice more pressure loss when the washing machine cycle runs or your sprinkler system comes on. If your street pressure with no flow if only 50 psi, you probably want the larger pipe.

  4. #4
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,329

    Default Supersize or Would you like 1in with that pipe for a few bucks more?

    FWIW, I have an old house with 1" galvanized from the city, reduced to 3/4 and then to 5/8 for the meter and then 1/2" throughout the whole house.

    Shower pressure is so-so to adequete (but its a rainfall too so that doesn't help). Simultanious shower and kitchen sink or toilet or bathroom sink sucks and if the washing machine is on, count anything else out.

    I've thought of replacing the easily accessable pipe with 3/4" but its just not really worth it in an old house that I'm going to see in few years.


    Jason