    Default Help - wiring wrong

    Hi All,

    I'm hoping someone can help me out here. I've now had three companies out to service my boiler and one of my zones still doesn't function properly.

    I have three zones, zone 1 and zone 2 works fine, but zone 3 only achieves heat when another zone 1 or 2 fires up the burner. Zone 3 will continue to cycle the circulator pump until another zone fires the burner and desired temperature is achieved. I'm 99% sure that the boiler was never wired correctly and I may not have the correct aquastat and relays to achieve the job. I have a Honeywell L8148J Aquastat/Relay, Honeywell RA832A-1041 Relay, and White Rodgers 829A-832 Relay.

    Attached is a wiring diagram of my current setup. I'm 99% sure that this is not correct. Can anyone/someone please provide advice on how I should proceed?

    Thanks again and looking forward to your response - BostonDan.
    Name:  Heating_System_Wiring_Diagram.jpg
Views: 111
Size:  26.0 KB

  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,938

    Default

    Yea, the wiring is wrong.

    https://customer.honeywell.com/resou...0s/60-2278.pdf

    Pull the wires off b and b2 and off the x terminals. Make sure there are jumpers between terminals 1 & 3 on the relays.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    DIY Junior Member BostonDan's Avatar
    Join Date
    Dec 2013
    Location
    Boston, MA
    Posts
    3

    Default Confused by response

    Quote Originally Posted by Tom Sawyer View Post
    Yea, the wiring is wrong.

    https://customer.honeywell.com/resou...0s/60-2278.pdf

    Pull the wires off b and b2 and off the x terminals. Make sure there are jumpers between terminals 1 & 3 on the relays.
    Wouldn't pulling the wires off b1 and b2 disconnect control to the boiler, causing it to never fire for any zone and placing jumpers between terminals 1&3 cause the blower on RA832A to never stop running?

  4. #4
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,938

    Default

    Leave the internal blue and red! pull the wires running to x,x. You need to jumper between 1&3 on the relays.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  5. #5
    DIY Junior Member BostonDan's Avatar
    Join Date
    Dec 2013
    Location
    Boston, MA
    Posts
    3

    Default

    After going through the relay block diagrams, I wired the (X - X) terminals on the White Rodgers 829A-832 in parallel with the (X - X) terminals on the Honeywell RA832A. I now have heat in all 3 zones. I did not add the jumpers between 1 & 3.

  6. #6
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,938

    Default

    If you didn't add them they are already in place. 3&4 make the switch.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

Similar Threads

  1. What Am I Doing Wrong?
    By lcsmall in forum Pumps and Tanks Well Forum & Blog
    Replies: 4
    Last Post: 09-26-2013, 07:45 PM
  2. What Went Wrong
    By Zoomboy in forum Pumps and Tanks Well Forum & Blog
    Replies: 33
    Last Post: 07-26-2012, 06:26 AM
  3. What's wrong here..
    By albertadave in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 04-05-2012, 09:48 AM
  4. too much is going wrong!
    By amw04004 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 09-05-2009, 06:24 AM
  5. Please tell me what I am doing wrong!!!
    By csims723 in forum Pumps and Tanks Well Forum & Blog
    Replies: 6
    Last Post: 07-16-2009, 02:45 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •