Fan condensation - stumped pls help

Users who are viewing this thread

miruca

New Member
Messages
3
Reaction score
0
Points
0
Everyone is stumped. I remembered Terry Love Plumbing and this forum from when i was doing a design project years ago ...and thought if this can be resolved this is the place to get the solution! I have alread done some searches of the forums but have not found anything more than we've already done. Stumped. Please help.

New construction with 8'8" x 14' 8" bathroom with fan condensation dripping on the floor and ceiling and walls. To date, here has what been done to try and address the problem:
- 157 cfm panasonic fan
- pitched metal pipe to exterior about 9' long
- insulated the pipe
- sealed gaps at fan

These actions improved but did not solve the situation - although it is somewhat less and can be intermittent depending upon the time of day etc (perhaps temperature changes dewpoint?). It appears, from observing, is tht the condensing is occuring at the fan housing ( obviously can't see the pipe now that it is fully insulated).

The shower is 43 x 48 tiled with glass walls/door that stop about 12" short of the ceiling. The shower head is the serenity shower panel (Valore from Costco).

At this point, the contractor is thinking the showerhead may be the issue - I find that odd since others have this showerhead with out similar problems.

All suggestions more than welcome.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
What kind and amount of insulation is there in the attic? How much is there on top of the fan and ductwork? What size ductwork did you use? Are you sure that the vent cap is fully opening?
 

miruca

New Member
Messages
3
Reaction score
0
Points
0
jadnashua - yes the vent cap is fully open when the fan is running. There is about 24" of insulation - both batt and cellulose. Ductwork pipe is 6" .
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
If it is on the walls and ceiling, then it is an insulation problem causing the wall temperature to be below the dew point of the air in the shower.
 

JohnfrWhipple

BATHROOM DESIGN & BUILD
Messages
3,225
Reaction score
102
Points
48
Location
North Vancouver, BC
Could the problem be air flow coming in from the outside? Perhaps switching out the style of or location of the vent grill might help?

Odd problem - wish I had some experience here.

I would try and rule out any airflow coming into your home via the piping of the fan.

It might be possible to add some kind of wind shield or wind screen to test out this theory....

Good Luck.


Another crazy idea might be to try and keep the fan and duct line warm - or warmer. MAybe a simple pipe wrap heater will solve this issue for you.

JW
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
IF the condensation were in the fan duct, then the water would ONLY drip from the fan, but he states tnat it is on the wall and ceiling, however, condensation ONLY occurs on surfaces which are colder than the water's dew point.
 