p trap plumbing question. pic included.

Users who are viewing this thread

aharami

New Member
Messages
21
Reaction score
0
Points
0
Location
New Jersey
Is this legal? Existing 3" pipe is the vent.
IMAG1066.jpg
IMAG1068.jpg
Water is draining from right to left in existing 3" pipe currently. I want to connect new shower drain to this pipe. Location of shower pans drain won't give me enough space to install p trap right to left because of existing 3" fitting.
 
Last edited:

aharami

New Member
Messages
21
Reaction score
0
Points
0
Location
New Jersey
I guess what I'm asking is if drain water always has to flow in one direction? Or can the p trap take the water to the right and then connect to a main pipe where the water is flowing to the left.

Appreciate your help.
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
Not legal. You have an S trap. You must have a vent in the area where you left hand is located in the first photo. That's before the pipe turn downward.
 

aharami

New Member
Messages
21
Reaction score
0
Points
0
Location
New Jersey
Oh, that 3" pipe is the main vent stack. That existing 1.5" wye you see in the 2nd pic is for the old tub drain. I'm moving the drain from a right hand configuration to a center configuration. Past that existing wye, to the right, the 3" pipe makes a 90 degree turn upward and vents out the attic.

After I posted this thread, I read that a p trap must have a horizontal section after the weir. So if I take the p trap to the right, then have a horizontal section for 6", then make a 90 degree turn downward toward the 3" pipe, then connect it to the new wye via a 45 turn angled down appropriately so it meets the new wye, is that legal?
 
Last edited:

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
No. The fixture vent MUST rise vertically off the trap arm, and must remain vertical until it reaches a point at least 42" above the floor, or 6" above the flood rim of the highest fixture served, whichever is greater. No section of the vent may be horizontal before the minimum height is reached.

Time to rethink your plan.
 

aharami

New Member
Messages
21
Reaction score
0
Points
0
Location
New Jersey
So how are shower drains plumbed then? If the vent must rise vertically directly off the p trap and the p trap is in the center of a 5'x3' shower pan...how is that possible? The shower pan won't allow the vent to rise vertically directly off the p trap which will be under the center of the pan. Confused...
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
The pipe from the trap to the vent connection, wherever that is, MUST be horizontal, (other than the slope due to pitch), It cannot turn up OR down until then, and your pipe appears to turn downward into the "Y". Also, if there is a toilet 'upstream" from the shower connection, that is also illegal unless the shower has its own dedicated vent.
 

aharami

New Member
Messages
21
Reaction score
0
Points
0
Location
New Jersey
Ok so this is all existing plumbing. That wye in the center of the pic is where the old tub was plumbed to. As you can see, the p trap arm was connecting directly to a horizontal vent pipe. My new shower drain location has to be where that elbow is sitting on the ground. The farthest to the left I can cut the 3" pipe is 1.5" to the right of wye on the left of the pic. How would I go about connecting the p trap properly so that everything is legal?IMAG1072.jpg
 
Last edited:

aharami

New Member
Messages
21
Reaction score
0
Points
0
Location
New Jersey
The pipe from the trap to the vent connection, wherever that is, MUST be horizontal, (other than the slope due to pitch), It cannot turn up OR down until then, and your pipe appears to turn downward into the "Y". Also, if there is a toilet 'upstream" from the shower connection, that is also illegal unless the shower has its own dedicated vent.

Ok thanks for that. I'm getting it now. So if I run the p trap left to right but make it so that the arm is same level as vent pipe, have a horizontal run for about 6 or so inches, then pretty much make an u turn using a 90 and a 45 to connect to the new wye, would that be ok? Something like this drawing. Pardon the horrible diagram.View attachment 22747

Toilet connection is downstream to shower. Still don't understand how I'm supposed to have a vertical vent directly off the p trap arm. I guess the existing plumbing wasn't done to code...or maybe the code changed in the past 20 yrs.
 
Last edited:

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
I see what you have there now. What you are trying to do is to pipe a fixture into the house stack. You can't do that. You need a separate stack that runs all the way to below the fixtures on the first floor.
 

aharami

New Member
Messages
21
Reaction score
0
Points
0
Location
New Jersey
I see what you have there now. What you are trying to do is to pipe a fixture into the house stack. You can't do that. You need a separate stack that runs all the way to below the fixtures on the first floor.

What is the reasoning behind that? As long as everything is joined properly, vent is vent, no?
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
No vent is not vent. That stack serves the fixtures below it. If you use it the way you are trying to use it, you would need to re-vent all the lower fixtures to a point above the flood level rim of the 2nd story fixtures. In short, you can't tie into that 3" pipe with waste water. You need to run a separate 3" pipe all the way to probably the basement and tie into the waste there. Absolutely do not continue to do what you are doing or you will have big problems.
 

WJcandee

Wise One
Messages
3,182
Reaction score
170
Points
63
Location
New York, NY
Last edited by a moderator:

aharami

New Member
Messages
21
Reaction score
0
Points
0
Location
New Jersey
No vent is not vent. That stack serves the fixtures below it. If you use it the way you are trying to use it, you would need to re-vent all the lower fixtures to a point above the flood level rim of the 2nd story fixtures. In short, you can't tie into that 3" pipe with waste water. You need to run a separate 3" pipe all the way to probably the basement and tie into the waste there. Absolutely do not continue to do what you are doing or you will have big problems.

Uh-boy. Dude, study this for some help. Helpful Plumbing Hints for Residential Construction by Bert Polk Plumbing Inspector Lincoln County
Then, look at p. 9 where there is a picture of a correctly-vented tub p-trap.

Also, p.3 of this guide may be helpful to you: Plumbing-and-Trenching-for-Homeowners---2018 (klickitatcounty.org)
Also look at p.6, and p.4 and 5.


Thank you for the links and thank you for taking the time to educate such a novice like me. One thing I'm trying to understand is if this is such a big no-no, then how was the old tub draining into this stack without causing problems? I'd assume the builder of this townhouse would've needed to build it all to code, albeit 20 yrs ago. By no means I'm saying you guys are wrong, but maybe with my limited knowledge, I'm not explaining things correctly.

Btw, only fixtures on first floor is a toilet, bathroom sink and kitchen sink.
 
Last edited by a moderator:

aharami

New Member
Messages
21
Reaction score
0
Points
0
Location
New Jersey
I just went up to the attic to check how everything is vented, and this 3" pipe is the main vent stack. But from this pipe, there is a 2" vent offshoot going into the second bath. The kitchen and downstairs half bath are below the second bath. So maybe the 2" vent is venting both second bath as well as downstairs. The reason i think that is true is because all three old fixtures in master bath (the one I'm renovating) were plumbed to drain into this 3" pipe, as seen below. First connection is for toilet, second for sink (sink has separate vent), and third (bottom of pic) is for old tub. Builder wouldn't have drained toilet into vent stack for downstairs fixtures.

IMAG1078.jpg
 
Last edited:

Caduceus

Master Plumber
Messages
139
Reaction score
4
Points
18
Location
Pittsburgh, PA
It's okay to pipe the shower into the stack. That is the main soil stack and fixtures can drain into it as long as they have their own independent vent. Any fixtures connecting to the stack below should already have their own vents.
If that 3"x3"x2" wye is the highest connected fixture, then the remainder of the soil stack becomes the stack vent and will also serve as the vent for the 2" shower p-trap. Meaning this...it looks like upstream of the shower the 3" 90 bends vertically and may go through the roof from there. As long as no fixtures flow in from another higher level than the shower.
 

aharami

New Member
Messages
21
Reaction score
0
Points
0
Location
New Jersey
It's okay to pipe the shower into the stack. That is the main soil stack and fixtures can drain into it as long as they have their own independent vent. Any fixtures connecting to the stack below should already have their own vents.
If that 3"x3"x2" wye is the highest connected fixture, then the remainder of the soil stack becomes the stack vent and will also serve as the vent for the 2" shower p-trap. Meaning this...it looks like upstream of the shower the 3" 90 bends vertically and may go through the roof from there. As long as no fixtures flow in from another higher level than the shower.

Yes, that's right, no other fixture upstream of the shower wye. Thank you for explaining.

Now the question is: can I take the shower ptrap left to right and then make a u into the 3"main using a 3x3x2 wye? See picture
IMAG1074.jpg
 

aharami

New Member
Messages
21
Reaction score
0
Points
0
Location
New Jersey
Also, I'm assuming I did this incorrectly, right? Since the drain on the left goes down before hitting the vent, it would be considered an s trap. I'd need to take out that 90 degree turn and put in a T, and then connect to the main vent in the attic, right?