    Default Re-working Basement Fixture Drain System (WS, AN, RO, and WM)

    Hello All!

    I am looking to bring my basement fixtures' drain plumbing up to snuff. Long story short, things are not correct (happy to explain as needed). I want to make sure everything is safe (think: air gaps, p-traps, backup) and hopefully (but not necessarily) up to code (2003 IPC). The fixtures are a water softener, acid neutralizer, clothes washer, and reverse osmosis. The basement is not, and never will be finished.

    Ive attached current and proposed drawings. There is one update to the proposed drawing that I did not re-draw: The proper double fitting should be a double fixture tee not a double san-tee.

    Questions/comments:

    • Air Gaps
      - On one of the 18 standpipes Im planning to use THIS air gap, which will receive the reverse osmosis and water softener drainage
      - On the other 18 standpipe Im planning to use THIS air gap, which will receive the acid neutralizer and clothes washer
      - Do these two air gaps look okay?
    • If I use 18 of standpipe, I will probably be up into the space between the joists; is this okay?
      - This would still be less than the max height (96) that the clothes washer can pump per the owners manual
    • Do all of the fittings, pipe sizes, and lengths look okay?
      - Can 2" pipe handle an acid neutralizer and washing machine? They will likely never run at the same time.
    • Do I understand correctly that the trap arm for the 2 standpipes must be greater than 4 (and less than some other number?)?
    • Do I need vents for the new 2 standpipes and traps? (this would be very difficult unless I used an AAP/tudor)
    • Am I missing anything? Anything else to consider?
    • Shouldn't the horizontal 4x3" san-tee actually be a wye + 45 or combination wye?


    Thanks in advance for your help!

    -ace

  2. #2
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    You do no want to use any 3/8" connection for your water treatment equipment, it is too small for most softeners and any back washed filters.

    And if there has been no problem with draining any of those things, I'd find something else to 'fix'....
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  3. #3
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,936

    Default

    I concur.

    Merry Christmas Gary.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  4. #4
    DIY Junior Member ACEschborn's Avatar
    Join Date
    Nov 2009
    Location
    Pennsylvania
    Posts
    14

    Default

    Hi guys, thank you for the replies Gary and Tom.

    Unfortunately, there are problems with the current setup. 1. the softener, for a reason beyond me (it was okay for years), has been overflowing the current standpipe, 2. there are no air-gaps, and 3. there are no traps.

    Gary, my plan was to use the 3/8" for the reverse osmosis discharge; is it not big enough? I believe the discharge line is 1/4".

  5. #5
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    The 3/8" is fine for an RO. A backup means there is blockage in the drain system. That will not be cured by lengthening the standpipes or adding air gaps etc.. You should first check the DLFC button that it is installed correctly or not worn out/damaged. You might have a blocked standpipe trap for some reason. Or the connection of the trap to the sewer line pipe.

    As you say it has worked wel for years, so find the cause of it not working right before you change things and create another problem.

    Merry Christmas everyone.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  6. #6
    DIY Junior Member ACEschborn's Avatar
    Join Date
    Nov 2009
    Location
    Pennsylvania
    Posts
    14

    Default

    Merry Christmas to you too, Gary!

    The current standpipe is only 3/4" copper, and as such, I figured it wasn't properly sized. Wouldn't cleaning it out would only be a temporary fix? That is, isn't 3/4" too small for the WS discharge? I understand the air gaps will not prevent backups, but they will ensure my drinking water stays clean should any other problem arise. I have not inspected the DLFC button and will do so, thank you for that idea.

  7. #7
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    The standard softener drain line is 5/8" OD. It is called 1/2" but the ID is not true 1/2" like 1/2" PE. So 3/4" copper tubing is more than enough. And you said things worked well for years, so it is not the drain line size, it means there is a blockage.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

Similar Threads

  1. One zone not working in my heating system
    By samthedog99 in forum Boiler Forum
    Replies: 1
    Last Post: 03-27-2013, 01:13 PM
  2. 7000SXT water softner system not working
    By dc5itr329 in forum Water Softener Forum, problems, installation and reviews
    Replies: 18
    Last Post: 03-07-2013, 10:26 AM
  3. Kinetico System Not Working At All.
    By Nomad in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 01-14-2011, 03:05 PM
  4. help: parent's sprinkler system stopped working
    By blankie in forum Irrigation / Sprinkler Forum
    Replies: 3
    Last Post: 07-03-2010, 11:51 PM
  5. 2 stations not working on my Rainbird system
    By BT1911 in forum Irrigation / Sprinkler Forum
    Replies: 8
    Last Post: 03-27-2008, 09:04 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •