    Question LPG Tankless Water Heater Trouble with Ignition

    I have an Eccotemp L10 Tankless Water Heater. This unit was installed two years ago and it has been used since for all our hot water. It worked great for 6 months and then we had to replace the gas-water valve assembly. About 6 months later I had an issue with it periodically/randomly not igniting (no spark) and that I was able to fix by trimming the wire that leads to the flame sensor. Other than these two issues the unit has performed well until October of this year. Then an unusual issue occurred for which Eccotemp tech support has no answer.

    In October, the water heater started having ignition failures on a periodic basic. When the water was turned on it would flare for a second and then go out. Sometimes it would not even flare up at all. This problem only occurred first thing in the morning and after 30-40 minutes the unit would work normally. Removal of the cover showed that the unit was getting sparks, just not igniting or sometimes igniting and not staying lit. I reset the gas-water valve assembly back to factory settings per tech support instructions, to no avail. We installed a new hose and regulator but after a couple of days the problem reoccurred. We then installed another new gas-water valve assembly, but after about 10 days the problem reoccurred.

    Through careful observation we have determined that the failure to ignite (or stay lit) occurs when the ambient temperature gets below 55 degrees F. The water heater is mounted in an outdoor kitchen that is semi-enclosed so the temperature in most of the area rarely gets below 40, even when its in the 20s outside. This happens even though this unit is made to be installed outdoors with strong admonitions to drain it during freezing temperatures. And I am also sure that there is no ice in the water flowing into the unit.

    After experimenting with different water temperature and flow rate settings, we discovered that at 55 degrees or less, the water heater will ignite only if the heaters temperature setting is turned to its coolest level. Then the temperature can be turned up, with the water still running, and it will continue burning. If the room is really cold (40s to low 50s), the heater wont even light on the lowest setting. At that point, we light our tank top propane heater and place it so that it is almost underneath the water heater, until the unit warms up and then the unit will operate again. Since this problem started, Ive also noticed that when its cold and the unit does light with the temperature set on medium or higher settings, there is somewhat of a pop sound when it first ignites, as if gas is accumulating before ignition occurs. We have had NO issues lighting a tank top heater or burners on our cook top that are in the same room. All of these appliances use 20lb propane tanks that we have filled at the same place. The water heater problem has occurred with multiple different tanks of the past two months.

    Eccotemp tech support has no answers other than to send the unit to them. They say there are no issues with this heater that can be temperature related. However our experience with this water heater has shown the issue to be consistently related to the temperature. Looking back on the troubleshooting in October, we can see that the days where we had no problems were days that followed warmer fall nights.

    I have since bought another L10 water heater but I would like to have this one repaired to keep as a spare. I also want to know what went wrong. Ive considered sending it to Eccotemp for repair, but the manager of the tech department seemed to not have a clue what the problem could be which makes me leery of sending it to them since I will have to pay by the hour for them to troubleshoot the issue. I really dont think theyll even be able to replicate the problem if they have the unit in a shop that is warmer than 55 degrees.

    Does anyone here have a suggestion as to what the problem could possibly be or what I could try to fix it?

    Thank you.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,403

    Default

    If you are using a 20# tank for the LG, that in itself is most of your issue when it is colder...the unit is being starved of enough gas. That tank's size is too small to evaporate enough gas fast enough to provide the tankless system enough fuel...basically, it needs a bigger tank so there's enough 'head' above the liquid to have enough gas to make the thing work right. Smaller burners may work okay since they use less fuel.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Member techinstructor's Avatar
    Join Date
    Apr 2009
    Location
    North Carolina
    Posts
    81

    Default

    Quote Originally Posted by jadnashua View Post
    If you are using a 20# tank for the LG, that in itself is most of your issue when it is colder...the unit is being starved of enough gas. That tank's size is too small to evaporate enough gas fast enough to provide the tankless system enough fuel...basically, it needs a bigger tank so there's enough 'head' above the liquid to have enough gas to make the thing work right. Smaller burners may work okay since they use less fuel.
    Interesting idea. This makes sense. We've always used a 20 lb tank and didn't have any issues with the past two winters, but at this point I'm willing to try anything that's reasonable. I don't have larger tank, but I do have a fitting the will hook two 20's together so I'll get that hooked up and give it a try.

    Thank you for the suggestion. I'll let you know how it works.

  4. #4
    DIY Member techinstructor's Avatar
    Join Date
    Apr 2009
    Location
    North Carolina
    Posts
    81

    Default

    I hooked two 20# tanks together and connected them to the water heater. I had high hopes but alas, they were squelched, as it did not work. The same problem persisted; in fact it seemed to be worse with the problem continuing to occur at even warmer ambient temperatures.

    Any other ideas?

  5. #5
    DIY Senior Member Reach4's Avatar
    Join Date
    Sep 2013
    Location
    IL
    Posts
    1,254

    Default

    I suspect that the surface of your tanks is well below freezing. However that does not explain why things worked for so long. Are the batteries fresh?

  6. #6
    DIY Senior Member lifespeed's Avatar
    Join Date
    Apr 2007
    Location
    California
    Posts
    319

    Default

    Put a manometer on the heater fuel inlet to confirm adequate pressure while drawing gas.
    Lifespeed

  7. #7
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,646

    Default

    Quote Originally Posted by lifespeed View Post
    Put a manometer on the heater fuel inlet to confirm adequate pressure while drawing gas.

    That would be the best way to do it.

    One way to test if tank pressure is a problem in cold weather, is to put the tank in warm water to bring it up to 70 degs or so.


    Good Luck.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  8. #8
    DIY Member techinstructor's Avatar
    Join Date
    Apr 2009
    Location
    North Carolina
    Posts
    81

    Default

    Thanks for the suggestions guys, but I found my problem. The problem was WEAK batteries. Unfortunately I didn't figure it out until I installed the new water heater and heard the difference in the sparking pattern at ignition. The relationship with the colder temperatures should have also pointed me to the batteries, as batteries are always sensitive to cold. (I had wrongly surmised it was not a problem with batteries because it was getting spark - I just didn't realize how SLOW and feeble the spark was.) I think that at the higher temperature settings, the unit was accumulating too much gas due the slow spark, so that when it did ignite, it extinguished itself. Then other times it just wasn't getting spark at all, which I could see because of the cover. In any event, I feel pretty stupid for not changing the batteries early in the troubleshooting. I should know from past experiences that one should ALWAYS try the simple (cheap) strategies first. Oh well, hopefully I learned my lesson.

  9. #9
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,646

    Default

    Great that you have it going.

    As temp drops battery voltage drops.

    Spark temperature is important.


    Enjoy.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  10. #10
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,403

    Default

    Try using lithium batteries...they not only last longer than alkaline, but work better at low temps, too.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  11. #11
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,646

    Default

    Quote Originally Posted by jadnashua View Post
    Try using lithium batteries...they not only last longer than alkaline, but work better at low temps, too.
    They would sure work better.

    Lithium batteries have a lot more power, But the voltage is a little different for that chemistry.

    They are the way to go, if you can afford them. I hate buying disposable batteries.

    I use rechargeable Lithium, they have great shelf life and plenty of power.


    The best brand to buy is yet to be seen. Only time will tell.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  12. #12
    DIY Senior Member lifespeed's Avatar
    Join Date
    Apr 2007
    Location
    California
    Posts
    319

    Default

    Batteries? Wow, didn't see that one coming. What a PITA! But I guess you know that now . . . Obviously AC power is a much more robust solution. Which you could implement with a DC power supply, although I don't know why the manufacturer didn't do this.
    Lifespeed

Similar Threads

  1. Trouble Emptying Water Heater
    By foxhome01 in forum Water Heater Forum, Tanks
    Replies: 6
    Last Post: 02-22-2009, 10:06 PM
  2. gas water heater- delayed ignition
    By Clint380 in forum Water Heater Forum, Tanks
    Replies: 5
    Last Post: 01-29-2009, 08:24 PM
  3. Hot water heater trouble
    By needsomefun283 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 07-01-2007, 03:32 PM
  4. water heater trouble
    By kbailey45us in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 12-19-2006, 05:20 AM
  5. Hot Water Heater trouble
    By soccergirl in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 09-11-2004, 09:04 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •