    Right now I only have two wires coming from the control board on my furnace to the thermostat in the living room. "R" and "W".

    I want to be able to run fan only. Do I only need to connect a wire from "G" on furnace control board to "G" on back of thermostat?

    Also, whoever hooked it may have wired it wrong. The red wire on the control board goes to the "W" on the thermostat along with the white to the "R".

    It's a Rheem oil burning furnace. I can give more details including schematics and pics if needed. Thank you for any information

  2. #2
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by skoby View Post
    I want to be able to run fan only. Do I only need to connect a wire from "G" on furnace control board to "G" on back of thermostat?
    I believe you are correct there.

    Also, whoever hooked it may have wired it wrong. The red wire on the control board goes to the "W" on the thermostat along with the white to the "R".
    That should not make any difference since the voltage is AC, but I prefer matching things properly at both ends.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  3. #3
    DIY Member skoby's Avatar
    Join Date
    Jun 2012
    Location
    Massachusetts
    Posts
    36

    Default

    Do you know if I can just hit the red oil burner switch off and back on when working on this?

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,403

    Default

    When you are only using two wires in the thermostat, it normally doesn't matter which one goes to which - the thermostat just connects the two together when it calls for heat. But, it won't work properly when you throw in a second function, as power is only on the R wire normally, and it needs to be connected to the G if you want the fan to turn on separately.

    Most of the time, the 24vac control voltage comes from a transformer in the heating unit, so shutting down power to it should kill the power. There are situations where the 24vac could be supplied from another source - when working with electricity, it's always safer to check.
    Last edited by jadnashua; 12-11-2013 at 12:07 PM.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    DIY Member skoby's Avatar
    Join Date
    Jun 2012
    Location
    Massachusetts
    Posts
    36

    Default

    Quote Originally Posted by jadnashua View Post
    When you are only using two wires in the thermostat, it normally doesn't matter which one goes to which - the thermostat just connects the two together when it calls for heat. But, it won't work properly when you throw in a second function, as power is only on the R wire normally, and it needs to be connected to the G if you want the fan to turn on separately.

    Most of the time, the 24vac control voltage comes from a transformer in the heating unit, so shutting down power to it should kill the power. There are situations where the 24vac could be supplied from another source - when working with electricity, it's always safer to check.
    Ah ha, that makes sense with the wire switch. Since I'm putting in new wire anyway I will switch them so the red and white are correct.

    Another question. The thermostat has a cool setting also. Will the fan to come on if I program it to or does there need to be some type of central A/C unit attached? Thanks

  6. #6
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by jadnashua View Post
    When you are only using two wires in the thermostat, it normally doesn't matter which one goes to which - the thermostat just connects the two together when it calls for heat. But, it won't work properly when you throw in a second function, as power is only on the R wire normally, and it needs to be connected to the G if you want the fan to turn on separately.
    Yes, and I thank you for that clarification. I was thinking of transformer connections while talking about a thermostat.

    Quote Originally Posted by skoby View Post
    Another question. The thermostat has a cool setting also. Will the fan to come on if I program it to or does there need to be some type of central A/C unit attached? Thanks
    If you put a jumper between "G" and that "Cool" connection on the thermostat, the fan should run whenever the thermostat tries to cool the house. But other than that, you would need some kind of controller at the other end.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  7. #7
    DIY Member skoby's Avatar
    Join Date
    Jun 2012
    Location
    Massachusetts
    Posts
    36

    Default

    Quote Originally Posted by leejosepho View Post

    If you put a jumper between "G" and that "Cool" connection on the thermostat, the fan should run whenever the thermostat tries to cool the house. But other than that, you would need some kind of controller at the other end.
    Alright, I'm going to give a shot tomorrow. Thanks

Similar Threads

  1. Having trouble connecting 3/4" copper pipe to 3/4" fittings.
    By cyelrah1 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 03-20-2013, 07:28 AM
  2. Question about connecting 2" wet vent to the 3" branch that it will serve
    By James Andereggen in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 10-23-2012, 12:40 PM
  3. Help solve an "argument" about a DPST thermostat for my ceiling heat?
    By Blind Frog in forum HVAC Heating & Cooling
    Replies: 7
    Last Post: 08-23-2012, 06:45 PM
  4. Connecting 1/2" copper to old 3/4" brass pipe
    By sean farrell in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 06-08-2012, 12:46 PM
  5. Faucets connecting with 1/2"D IPS or with 3/8"D IPS (Flex lines)
    By geniescience in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 06-16-2010, 11:19 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •