Thread: Check Valve Shutoff Loud

  1. #1
    DIY Member monty's Avatar
    Join Date
    May 2006
    Location
    San Francisco
    Posts
    41

    Default Check Valve Shutoff Loud

    Hi,

    We are having a problem that was isolated to our check valve at our cold water input to our hot water heater.

    Whenever we have a quick shutoff of water (toilet, sink, dishwasher, clothes washer etc...) the check valve has a thump/bang that is fairly noticeable. The biggest problem is this valve is right on the wall next to my child's bed - so he hears this thump or thump/thump that sounds like someone knocking on the wall - the wall is almost acting like a speaker and amplifying the sound. I am having my plumber look into it at the moment, but so far no solution has been determined.

    So since I have received such great help on this forum over the years I wanted to ask!

    Our hot water re-circulate loop connects to this same area as well, however it does have a proper expansion tank above this check valve. The current check valve is brass and sitting horizontally.

    I would love to find a different check valve that is silent - I will need to get the actual valve type spring or swing, size etc... figured out and will take a picture later today.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default

    You must be getting a "huge" cold water pressure drop when you open any faucet, so that the pressure in the expansion tank is "slamming" the valve closed, assuming it is open. Check your cold water pressure WHEN a faucet is running and also when everything is shut off.
    Licensed residential and commercial plumber

  3. #3
    DIY Member monty's Avatar
    Join Date
    May 2006
    Location
    San Francisco
    Posts
    41

    Default Update - Photo Enclosed

    The pressure is very stable. This is a brand new home - all modern fixtures, mostly pex tubing, and should be compliant with the applicable plumbing codes.

    I guess the local inspector insisted on this check valve - including the actual part number to use.

    Here is a photo I just took (it is a swing check valve). I would like to put in a spring check valve to see if that helps.

    The noise is not terrible - it just attenuates through the stucco wall in the background - right to the bedroom wall.

    Name:  IMAG0023.jpg
Views: 108
Size:  39.3 KB

  4. #4
    DIY Senior Member Smooky's Avatar
    Join Date
    Apr 2011
    Location
    NC
    Posts
    479

    Default

    Here is a silent check valve that should work:
    Watts LF600

    http://www.watts.com/pages/_products...s.asp?pid=6837

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default

    The thing is that it should NOT even happen in the first place so you should find out exactly WHY it is occurring, before you spend time and money eliminating the symptoms. "Pressure is stable" may be a subjective opinion, ( I had a gas unit yesterday that the pressure "looked proper" but was actually quite low), rather than fact. You will not know until someone actually does a proper test of the system.
    Last edited by hj; 12-10-2013 at 06:01 AM.
    Licensed residential and commercial plumber

  6. #6
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    Quote Originally Posted by monty View Post
    Our hot water re-circulate loop connects to this same area as well...
    If the swing valve is part of a gravity recirc, a spring-loaded one will defeat the recirc.

    As was mentioned, you need to find and treat the cause, not the symptom.

  7. #7
    DIY Member monty's Avatar
    Join Date
    May 2006
    Location
    San Francisco
    Posts
    41

    Default

    Quote Originally Posted by LLigetfa View Post
    If the swing valve is part of a gravity recirc, a spring-loaded one will defeat the recirc.

    As was mentioned, you need to find and treat the cause, not the symptom.
    Thanks for the help...

    The picture is the 60psi cold water supply coming into the house from city water (coming in from the left) - the check valve is the first component in the chain at that point. The lower larger line feeds the water heater down and back to the left - the smaller copper line coming back in from the top of the photo is the recirculate hot water line - our recirculate is a pump based system, an expansion tank is just above the photo on this smaller copper line.

    The explanation to me was that it has nothing to do with the recirculate line itself - but the noise is from the quick shutoff of the various fixtures in the home (toilets, auto faucets, electronic shutoffs). These are fast shutoffs - and a small amplified hammer type effect is occurring.

    The sound isn't even very noticeable standing right in front of the check valve - it is more amplified on the other side of this wall (after passing through the stucco wall and into the stud bay on the other side).

    I have read a bunch of stories of these swing check valves having some noise - I just want something to be quieter to appease a 4 year old and his parents!!!

  8. #8
    DIY Member monty's Avatar
    Join Date
    May 2006
    Location
    San Francisco
    Posts
    41

    Default

    Quote Originally Posted by hj View Post
    The thing is that it should NOT even happen in the first place so you should find out exactly WHY it is occurring, before you spend time and money eliminating the symptoms. "Pressure is stable" may be a subjective opinion, ( I had a gas unit yesterday that the pressure "looked proper" but was actually quite low), rather than fact. You will not know until someone actually does a proper test of the system.
    Thank you for the help.

    Is it possible to have a small sound that we are just (too) sensitive to with this swing check valve? I think there is more sound because it is somehow right into a stucco wall - it is much more noticeable inside the home - I think the stud bay is acting like a speaker box...

    I have a pressure gage that I attach to various hose bibs while having faucets, toilets and other things turned on/off? What should I be looking for? Pressure up/down 1 psi/5psi/10psi?

  9. #9
    DIY Member monty's Avatar
    Join Date
    May 2006
    Location
    San Francisco
    Posts
    41

    Default

    Quote Originally Posted by Smooky View Post
    Here is a silent check valve that should work:
    Watts LF600

    http://www.watts.com/pages/_products...s.asp?pid=6837
    Thanks for the suggestion - in the description of this part I see the following (my emphasis added)

    "Series 600 Bronze Silent Check Valves efficiently perform all of the functions of a swing check or vertical lift check valve and at the same time operate silently to prevent the effects of water hammer."

    I kind of feel like this is my condition - and a solution then? Based on the other comments above I need to figure out why the hammer is occurring. Is that the consensus then?

  10. #10
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default

    IF you put the pressure gauge in the right location so it registers the cause of the sound, you may find that when it occurs the gauge needle goes to the maximum, regardless of what the gauge has as a high limit, for a millisecond or so. Your check valve is horizontal and the "flap" is on an angle, so it is normally CLOSED and can only create a sound if something opens it and then it bangs shut. In your description, there is NO flow to open it when you are using code water so it could not "close" to make the sound.
    Licensed residential and commercial plumber

  11. #11
    DIY Member monty's Avatar
    Join Date
    May 2006
    Location
    San Francisco
    Posts
    41

    Default

    Quote Originally Posted by hj View Post
    IF you put the pressure gauge in the right location so it registers the cause of the sound, you may find that when it occurs the gauge needle goes to the maximum, regardless of what the gauge has as a high limit, for a millisecond or so. Your check valve is horizontal and the "flap" is on an angle, so it is normally CLOSED and can only create a sound if something opens it and then it bangs shut. In your description, there is NO flow to open it when you are using code water so it could not "close" to make the sound.
    Hi HJ,

    I am not understanding what you are saying above. Could you help me understand it better?

    The check valve is on the incoming city cold water service and precedes all cold water feeds into the house - the pipe then branches off and one line goes up to the cold water distribution throughout the house, another branch is the cold water feed to the hot water heater.

    The sound occurs only after cold water is supplied to a toilet, sink, clothes washer, or dishwasher - so the check valve would then be open while the fixture is on I think - when the fixture turns off (abruptly in this case) that is when the sound occurs. I can prevent the sound from happening by turning on a sink and leaving it running just as a toilet turns off. I believe the sudden shutoff and closing of this valve (no more cold water called for) is creating the sound.

    Note: I can post a bigger picture of all of the pipes if that would help. THANKS!!!

  12. #12
    DIY Senior Member Smooky's Avatar
    Join Date
    Apr 2011
    Location
    NC
    Posts
    479

    Default

    Backing up and taking a photo to show the complete system might help. Generally this type of back flow preventer is used to isolate the hot water return water from the cold water distribution system. From your description it sounds like the swing check is just preventing water from backing up into the city supply. Swing checks are not usually acceptable to protect the source from contamination. Usually a dual spring check is used to protect the source for a house, when it comes in from the city supply. Location and type of back-flow preventer is important in preventing hot water from getting into the cold and vice versa.

  13. #13
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default

    Originally, you said the cold water goes down and to the water heater with the return coming from the top, which is correct since the check valve would ONLY be on the line to the water heater. Now you are saying that there is an additional connection which supplies the whole house after the check valve, (which does not show in your photo), which COULD cause the sound, because of the expansion tank, but which should also send hot water from the return line through the cold water system if it is actually connected that way.
    Licensed residential and commercial plumber

  14. #14
    DIY Member monty's Avatar
    Join Date
    May 2006
    Location
    San Francisco
    Posts
    41

    Default

    Quote Originally Posted by hj View Post
    Originally, you said the cold water goes down and to the water heater with the return coming from the top, which is correct since the check valve would ONLY be on the line to the water heater. Now you are saying that there is an additional connection which supplies the whole house after the check valve, (which does not show in your photo), which COULD cause the sound, because of the expansion tank, but which should also send hot water from the return line through the cold water system if it is actually connected that way.
    Well now I am not totally sure, looking at the pipes again, where the cold water supply to the house comes and goes. The valve is certainly on the cold supply the hot water heater...

    I have taken 2 more photos that show the side of the system with the valve and recirculate line. Hope it helps - Thanks again for the advice!

    Name:  waterheater2.jpg
Views: 62
Size:  68.6 KB

    Name:  waterheater1.jpg
Views: 61
Size:  51.9 KB

    Shown kind of stitched together - so the top photo is shot above the lower one...

  15. #15
    DIY Member monty's Avatar
    Join Date
    May 2006
    Location
    San Francisco
    Posts
    41

    Default

    Quote Originally Posted by DonL View Post
    Where is the pressure regulator for the input ?
    AFAIK there isn't one - as the water at the street in our location is 60psi.

Similar Threads

  1. a separate flow check valve or a circulator with a flow check valve?
    By diyfun in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 02-08-2012, 08:31 PM
  2. Swing Check vs. dual check vs. double check valve
    By colbymom in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 25
    Last Post: 05-10-2011, 01:19 PM
  3. Replies: 5
    Last Post: 09-19-2010, 08:48 PM
  4. leaky fill valve AND shutoff valve
    By moray in forum Toilet Forum discussions
    Replies: 8
    Last Post: 03-22-2009, 11:12 AM
  5. Why is sink shutoff valve still leaking after main water valve turned off?
    By kimana517 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 09-18-2008, 06:28 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •