Results 1 to 8 of 8
Thread: Need some help figuring out what to do....
    DIY Junior Member Touchthewindrider's Avatar
    Dec 2013
    North Carolina
    Default Need some help figuring out what to do....
    I was just given a 14' x 24' Leonard metal garage. It has already been wired with overhead lights,
    outlets, wall switches, exhaust fans and two 240volt outlets. It's got an old (funky looking) panel with
    two 15 amp breakers. The building has been moved to my property (I live in the county) and is just at
    150' from the house, which, happens to have the electric meter, and a panel with three breakers; one for
    our well pump, one for the hot water heater, and a 30 amp breaker for a "steamer" attached to the wall.
    My question: can I run wire from the outside panel (using the 30 amp breaker for the "steamer") to this
    building? If so, do you think I should replace the panel with the two 15 amp breakers in the garage with a
    new panel? Should I run what size wire from the house and should it be in conduit? PVC okay?
    Electrician ActionDave's Avatar
    Feb 2009
    Colorado
    You can't use the steamer breaker to feed your garage and your steamer.
    Don't know about the funky looking panel. What brand is it?
    Nov 2006
    Quote Originally Posted by Touchthewindrider View Post
    ...overhead lights, outlets, wall switches, exhaust fans and two 240volt outlets...an old (funky looking) panel with
    Does that mean all the 120V stuff is on two circuits and there are no breakers for the 240V outlets?
    ...150' from the house, which, happens to have the electric meter, and a panel with three breakers;
    Is there room for another breaker there so you can run a sub-feed over to the garage?
    Conduit is typically optional, although often suggested, and I think #8 wire would be best for running a 30A 240V circuit that far if you might ever want to run a welder out in your new garage.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt
    Dec 2013
    North Carolina
    Thanks for the reply guys.
    No, the steamer hasn't worked in years, so it would not be connected.
    I think one of the breakers (in the garage) is dedicated to just the 240v outlets. (two of them, side by side...240v outlets)
    Here is a photo of the panel on the house with the steamer breaker I thought about using and a photo
    of that "funky" panel box (sorry ActionDave about the technical jargon...)
    Name:  House panel.jpg
Size:  43.7 KBName:  panel in garage.jpg
    Jun 2007
    North Carolina
    First step is to do a calculation of the power needed for the building. Second step is to size the four wire feeder by this load using 225.39
    225.39 Rating of Disconnect.
    The feeder or branch-circuit disconnecting means shall have a rating of not less than the calculated load to be supplied, determined in accordance with Parts I and II of Article 220 for branch circuits, Part III or IV of Article 220 for feeders, or Part V of Article 220 for farm loads. Where the branch circuit or feeder disconnecting means consists of more than one switch or circuit breaker, as permitted by 225.33, combining the ratings of all the switches or circuit breakers for determining the rating of the disconnecting means shall be permitted. In no case shall the rating be lower than specified in 225.39(A), (B), (C), or (D).
    (A) One-Circuit Installation. For installations to supply only limited loads of a single branch circuit, the branch circuit disconnecting means shall have a rating of not less than 15 amperes.
    (B) Two-Circuit Installations. For installations consisting of not more than two 2-wire branch circuits, the feeder or branch-circuit disconnecting means shall have a rating of not less than 30 amperes.
    (C) One-Family Dwelling. For a one-family dwelling, the feeder disconnecting means shall have a rating of not less than 100 amperes, 3-wire.
    (D) All Others. For all other installations, the feeder or branch-circuit disconnecting means shall have a rating of not less than 60 amperes.
    When installing this disconnect at the building we must also adhere to 225.36
    225.36 Suitable for Service Equipment.
    The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
    Don’t forget that this disconnect is required to be connected to an electrode system as outlined in 250.32
    250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s).
    (A) Grounding Electrode. Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250. The grounding electrode conductor(s) shall be connected in accordance with 250.32(B) or (C). Where there is no existing grounding electrode, the grounding electrode(s) required in 250.50 shall be installed.
    If you decide to install rods at this building it will require two rods as outlined in 250.53(A)(2)
    (2) Supplemental Electrode Required. A single rod, pipe, or plate electrode shall be supplemented by an additional electrode of a type specified in 250.52(A)(2) through (A)(8). The supplemental electrode shall be permitted to be bonded to one of the following:
    When dealing with remote buildings on our property we must remember that what works may not be safe. There is only one way to install this system in a safe manner as outlined in this post.
    The panel and wiring that is in the building must go. It is nothing less than a fire waiting to get started. To ensure a compliant installation be sure to permit and get it inspected for your protection. To fail to follow the proper procedures could result in a loss of homeowner’s insurance for your home.
    Jan 2008
    To meet the minmum requirements of the NEC, you can only run a single 20A circuit to the building unless you are putting in a proper sub panel with ground rods at the outbuilding.
    Sep 2013
    What is a "steamer" in this context? Sauna, clam cooker, steam heat boiler, steam cleaner?
    Dec 2013
    North Carolina
    A steamer is pretty much a sauna.
  1. Help figuring out what this piece is
    By creese in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Last Post: 05-31-2012, 10:12 AM