    I have a 1990 ICP gas furnace model# NUGE100BG01 with honeywell controls. The furnace comes on fine but after 5 minutes the flame goes out due to the fan limit switch rising above 200 degrees. I have a new filter and opened all of the supply vents. I checked the temperature at the first supply vent and it was a consistent 122 degrees. I pulled out the temp probe on the limit switch and immersed it into boiling water to gauge if it is accurately depicting a temperature. It was actually lower than 212 degrees. I put a 4" temperature probe in the spot where the limit switch was and it only registered a 141 degrees. I did some research and some people with the same problem stated that it was from having to big of a furnace to their house. Can these limit switches temperature probes go bad or is there something that be causing the probe to actual see that high of a temperature.

  2. #2
    DIY Senior Member guy48065's Avatar
    Join Date
    Sep 2013
    Location
    SE and north MI
    Posts
    111

    Default

    They do go bad but most fail outright so it's probably rare for one to be "off" so much. It's more likely the limit switch is positioned closer to the heat exchanger than your probe was. Try drilling a hole in the limit mounting plate & position your temp probe so it's touching the face of the limit, then re-insert the limit and see what your reading is then.
    Have you had your furnace cleaned lately? Your blower could be gummed up with clinging dust, maybe you have many registers or dampers closed or blocked with furniture. The furnace needs to breathe or the plenum temperature will rise.

    That said--I have that issue (inadequate flow) and don't know what to do to correct it.
    Romeo and Atlanta, MI

  3. #3
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,653

    Default

    Air Flow can cause problems.

    Wrong Blower speed caused by a blower Motor problem or low voltage. A incorrectly programed or wired t-Stat could affect blower speed.

    It sounds like you need to increase the air flow.

    The limit sounds like it is doing its job.

    How long is your Gas Valve ON before the Blower kicks on ? How long does the Blower run after the call for heat is gone ?


    Good Luck.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    The furnace will have a means to adjust the fan speed, it may be switches, jumpers, or require moving a belt on the pulleys (if it isnt' direct drive). Based on the BTU, it will have a recommended speed. It may be a range...setting it outside of that range will generate problems.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. Hot Water Heater High Limit Switch Continualy Trips
    By rshackleford in forum Water Heater Forum, Tanks
    Replies: 5
    Last Post: 05-11-2010, 09:26 AM
  2. High Limit Question
    By shawninolympia in forum Water Heater Forum, Tanks
    Replies: 10
    Last Post: 12-26-2009, 04:53 PM
  3. is there a limit to reheating copper?
    By ceebee59 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 02-25-2009, 05:11 AM
  4. White Rodgers 535 Limit Switch Replacement
    By Wrex in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 04-14-2008, 08:06 AM
  5. Up File Size Limit
    By Lakee911 in forum Terry's Corner
    Replies: 0
    Last Post: 07-12-2006, 10:00 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •