    Default do AAVs expel sewer gases?

    This may be a stupid question but if an AAV remains closed until it receives negative pressure from water going down the drain then how does it expel sewer gases? What happens to them if you use an AAV?

  2. #2
    DIY Senior Member Reach4's Avatar
    Join Date
    Sep 2013
    Location
    IL
    Posts
    1,247

    Default

    A properly-operating AAV only admits air. Sewer gases will make it out of the sewer after or during the sewage passage. Eventually it will go by a vent.

  3. #3
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    An AAV needs a proper vent somewhere in system for postive pressure. There should be at least one vent through the roof for that.


    Last edited by Terry; 11-12-2013 at 11:07 AM.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,374

    Default

    Only when they fail...
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default

    I question item E, because there is no way to "engineer design" the installation to vent trapped air in an ejector pit if there is no "atmospheric vent" and/or the water in the pit rises above the inlet piping.
    Licensed residential and commercial plumber

  6. #6
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,933

    Default

    Well now HJ, if you log on to the Studor web site you can find an engineered drawing for just such a thing. Of course, as you look at it you will note that the way they have the AAV installed it pretty much does nothing. LOL
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  7. #7
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    I think most of the plumbers would refuse to use them on a pumped system.
    I remember on one basement installation where I went to the next floor and used the 2" toilet vent.

  8. #8
    DIY Senior Member asktom's Avatar
    Join Date
    Nov 2009
    Location
    Victor, MT
    Posts
    459

    Default

    AAVs are lazy plumbing. They will eventually fail, no matter how the Studor folks frame it. AAVs are from the "wham bam thank you mam" school. Gravity, which includes atmospheric pressure, will continue to work indefinitly. Vent it right and it is a done deal.

  9. #9
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,933

    Default

    Honestly, other than an island sink and even there I'd rather waste stack vent, I have never in near 40 years of plumbing installed one and never will. I have always been able to find a way to properly vent the fixture and if the homeowner doesn't want the expense or possibility of having to do sheet rock repairs, I walk away from the job. Not interested in hack work and better than that, I don't need it either. Then again I feel the same way about PEX, flexible supply tubes and plastic J hook hangers. We don't stock any of the above, don't use any of the above and I would probably fire any plumber working for me that did. Add CSST for gas piping to the list LOL
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

Similar Threads

  1. Connecting Collapsed Storm Sewer to Sanitary Sewer?
    By amkjud in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 07-30-2013, 07:02 AM
  2. Connecting Hot Water Heater Drain Pan to Sewer - Will Swing Check stop sewer gas?
    By Jim109 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 15
    Last Post: 05-21-2011, 12:43 PM
  3. Pros and Cons of Using AAVs
    By dondiy in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 10-18-2007, 05:22 AM
  4. Why do I need vents? (How about AAVs?)
    By talkingdog in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 35
    Last Post: 08-28-2007, 08:50 PM
  5. Sewer line to city line (sewer lateral) question r/o
    By H20Melon in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-11-2005, 05:12 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •