Thread: Cost estimate for Generator Power Transfer Switch installation

  1. #1
    DIY Member GG_Mass's Avatar
    Join Date
    Aug 2013
    Location
    Massachusetts
    Posts
    47

    Default Cost estimate for Generator Power Transfer Switch installation

    I know that labor prices vary between areas, I'm located in Massachusetts. A rough estimate is very much good for me, at this point.

    I would like to have this unit installed - Reliance Controls 31406CRK http://www.reliancecontrols.com/Prod....aspx?31406CRK.
    Aside from the unit's cost, what's the price I should be ready for as far as labor is concerned ?
    I'm going to probably opt out from the input power socket and connect a cable from the generator to the transfer switch unit directly, the probable area where such socket would be fit to be installed - is not the optimal area where I'd like to place the generator at.

    Thank you.

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    976

    Default

    Maybe 2-3 hours tops. I can do small ones like that, with the inlet right on the panel, in about an hour start to finish.
    Expect to pay $150-400.

  3. #3
    DIY Member GG_Mass's Avatar
    Join Date
    Aug 2013
    Location
    Massachusetts
    Posts
    47

    Default

    Quote Originally Posted by Speedy Petey View Post
    Maybe 2-3 hours tops. I can do small ones like that, with the inlet right on the panel, in about an hour start to finish.
    Expect to pay $150-400.
    I understand,
    Thank you.

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Be careful when using something like this as the code official has many different things that can be called out on this type of installation.
    Table 310.15(B)(3) (raceway fill)
    200.4 (shared neutral)
    702.5 (AIC rating of the unit)
    702.7 (signage)
    225.36 (disconnect also see 702.12)
    702.11 (depending on the manufacturer of the generator)
    590.6(A)(3) (GFCI protection which will cause the GFCI to trip with this setup)
    406.9(B)(1) (in-use covers on receptacle)

    And the list goes on and on. It will depend on just how bad you inspector wants to keep this from happening. The good thing is that here in NC the generator cannot be connected to the premises wiring without it being listed. This means that this transfer will not meet the rules for an installation in NC.

Similar Threads

  1. Connecting Outside Generator to Transfer Switch
    By SAS in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 11-07-2011, 01:15 AM
  2. Rough estimate of the cost to switch from gas to electric
    By chubyball in forum Tankless Water Heater Forum
    Replies: 5
    Last Post: 06-10-2009, 12:46 PM
  3. Generator Transfer Switch
    By ddagsyn in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 09-24-2008, 02:55 PM
  4. Generator Transfer Switch
    By seaneys in forum Electrical Forum discussion & Blog
    Replies: 13
    Last Post: 09-17-2007, 11:33 PM
  5. Need help for estimate cost
    By norvi in forum Toilet Forum discussions
    Replies: 2
    Last Post: 04-22-2006, 07:20 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •