    Default Do I need Primary / secondary piping?

    I am having a peerless purefire PF-50 put in to replace an old electric boiler. Its a single zone all cast Iron radiator system. I am trying to make sure its installed correctly. I don't think the installer intends to install primary secondary but to just pull out the old system and tie in the new boiler. Is this OK or will it cause problems? The system install instructions all have diagrams of central heat plus DHW or multiple zone piping.Name:  boiler piping1.jpg
Views: 221
Size:  43.9 KB
    Picture is of old system. Return on left.

  2. #2
    DIY in AZ emd36's Avatar
    Join Date
    Jan 2010
    Location
    Arizona
    Posts
    22

    Default

    You don't need primary/secondary. It is the way most systems are plumbed in the U.S. Your photo is a bit difficult to interpret. It appears that the pump etc. are out of the photo below the boiler.
    If you have multiple zones, a differential pressure by-pass valve is recommended. I believe that keeps the pump operating at the same pressure no matter what the call for heat. What did your installer do?

  3. #3
    DIY Junior Member Crooz1n's Avatar
    Join Date
    Sep 2013
    Location
    Roanoke VA
    Posts
    26

    Default

    Yes its a 2 pipe system with just a single zone. All the radiators get flow all the time. I contacted Peerless and they said that they didn't have to do primary/secondary as long as we had enough flow. They used a B & G NRF-22 which is 22 GPM so I think its OK. (Min flow of 2.2 for heat exchanger) I was just concerned that the Peerless manual did not show a simple direct piping diagram making me think that piping that way may void the warranty.

    The contractor has since come back and changed the pump orientation.

    Name:  IMAG1065.jpg
Views: 141
Size:  54.1 KB

  4. #4
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,713

    Default

    Hopefully you're not pounding 22 gpm through the heat exchanger! Anything more than 5 would be way overkill as far as the boiler is concerned, but you may need higher flow on the radiation to keep the balance dialed in. Did Peerless spec a MAX flow?

    It's worth air-sealing around the old flue where you've run the venting, since it's a large parasitic heat load due to the infiltration it is driving (even if it's sorta-sealed at the top of the flue, it still needs to be sealed at the basement.)

  5. #5
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,933

    Default

    I don't see any temperature gauge on the return so I imagine the return temps are coming back pretty darn cold on start up and throughout most of the cycle. At the very least it should have a bypass with a valve running from the feed to the return. There isnt and inspector in the state that would pass the wiring and the gas piping either but maybe VA is less stringent. Also, where does the condensate get pumped too? and is the condensate pump securly fastened to anything or just set on the basement floor.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  6. #6
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,713

    Default

    I was just going to edit-in that he should check the delta-T it's running, to make sure that it stays within spec under all operating conditions as well.

    The gas plumbing really needs to be looked at too- looks like it could be compromized by the house flexing in a high wind, and the teed-off stub should be at the bottom, below the gas input to the boiler to really work as a crud-trap, like on this water-heater hookup, not up at the ceiling well before the stretched out flex:

    Last edited by Dana; 11-13-2013 at 09:01 AM.

  7. #7
    DIY Junior Member Crooz1n's Avatar
    Join Date
    Sep 2013
    Location
    Roanoke VA
    Posts
    26

    Default

    The chimney has been sealed since I took the picture. The peerless manual says min system pressure of 14.5 and min flow rate of 2.2 but I did not see a max flow. The pump is spec'd from their chart page 20 Table 4.5. I suppose that's where the installer chose the pump from. Condensate pump runs into sewer line you can see just behind top right corner of plywood. And no not secured just sitting there . There is a floor drain 4 feet from the pump as well.I'll ask the inspector about the gas trap. The thermostat wire has a splice in it that I will rectify this weekend. I looked at the return temps earlier in the week and they seemed OK but I forgot to look this morning.

    You have to remember boilers in this area are not to common anymore, everything has gone to forced air. I went thru 6 different contractors before I found one that had at least a little bit of sense when it comes to boilers. Everyone else wanted to put in really large systems and had no idea how to properly size a hot water boiler. I had to insist that we put in the PF-50 instead of the 80. This contractor suggested the Purefire as he was familiar with it. I guess being familiar with it and reading the manual don't need to go together.

  8. #8
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,933

    Default

    Take a picture of where the condensate line enters the sewer pipe. Just curious.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  9. #9
    DIY Junior Member Crooz1n's Avatar
    Join Date
    Sep 2013
    Location
    Roanoke VA
    Posts
    26

    Default

    Tom its just the vinyl line inserted into what looks like a cleanout plug and sealed w/ RTV. I'll take a picture tonight when i get home.

    Dana I see no max on flow. Should I throttle back one of the service valves near the pump to reduce flow?

  10. #10
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,713

    Default

    Before making any flow adjustments, what is the delta-T across the boiler looking like? (Hockey tape on the output and return plumbing makes it easy to get consistent readings with an IR thermometer.)

  11. #11
    DIY Junior Member Crooz1n's Avatar
    Join Date
    Sep 2013
    Location
    Roanoke VA
    Posts
    26

    Default

    Sorry but whats Hockey tape. I live too far south to know hockey maybe masking tape or duct tape. I could also just see what the controller is reporting as there is a thermistor on supply and return.

  12. #12
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,374

    Default

    For a reliable reading with an IR thermometer, you want something that is both non-reflective, and in good contact with the copper pipes - the flat black tape used on hockey sticks or maybe the grip of a baseball bat works pretty well. If you have an IR thermometer that can take a plug-in sensor, you could use that, or if it's has adjustable emissivity, you could dial in that value to get a more accurate reading; otherwise, trying to get an IR reading off of a copper pipe is not that reliable - it is repeatable, but not reliable without help.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  13. #13
    DIY Junior Member Crooz1n's Avatar
    Join Date
    Sep 2013
    Location
    Roanoke VA
    Posts
    26

    Default

    just went down (11:54)and boiler is running right now the supply temp is 113 and return 97.
    Its been running for 7 days and has had 22 ignitions 1 failed and run time is 52 hrs.
    When I got home from work it was in standby and supply temp was at 85 I think.

    7 am- Supply is at 120 53%input return @109.
    Last edited by Crooz1n; 11-14-2013 at 04:18 AM.

  14. #14
    DIY Junior Member Crooz1n's Avatar
    Join Date
    Sep 2013
    Location
    Roanoke VA
    Posts
    26

    Default

    Here's the picture you wanted Tom.
    Name:  IMAG1089.jpg
Views: 122
Size:  41.9 KB

    Here is supply/return temps from this AM.


    Name:  IMAG1093.jpg
Views: 119
Size:  40.1 KB

  15. #15
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,713

    Default

    A ~10-20F delta at condensing temps is fine- sounds like the guy picked the right pump. The system flow is almost certainly not anything like 22 gpm, but high enough that it probably won't be an issue on a cold-start during colder weather when the reset curve is calling for a higher output temp, and low enough to support an efficient delta-T at the boiler. (Does this boiler have an internal flow meter you can call up on the display?) Without looking it up, the max operating delta on the HX is probably something like 50F. Keep an eye on it- if you see sustained burns with delta-Ts over 40F it's worth looking up the specified max just to make sure, but my best guess is it'll never hit that in normal operation.

Similar Threads

  1. Setting D/T on primary
    By tom3holer in forum Boiler Forum
    Replies: 3
    Last Post: 06-20-2013, 06:54 PM
  2. Secondary condensate drain installation
    By Atom in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 06-30-2011, 12:50 PM
  3. Secondary loop doesn't heat!
    By jadnashua in forum Boiler Forum
    Replies: 4
    Last Post: 12-31-2009, 07:45 PM
  4. Secondary (supply) line question
    By HockeyFan in forum Electrical Forum discussion & Blog
    Replies: 14
    Last Post: 02-27-2008, 06:03 AM
  5. secondary stack
    By jeffrey in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 11-10-2004, 10:34 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •