    Default Venting of Standard Vent Boiler

    Hi, I have been told that I have a standard vent boiler installed (I purchased the house a year back) with side of house venting. Is this a problem? Does it need a vertical Line Chimney/can the side way vent be modified? Or do we have to change it to a direct vent boiler?

    Thanks

    Sam

  2. #2
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    Atmospheric drafted boilers need a vent stack sufficiently tall to achieve the necessary draft pressures, and must extend above the ridge line of the house to limit the risk of back-drafting due to wind. If your side-vented atmospheric boiler has a tall enough stack it can still work. If it simply terminates at the wall somewhere between grade and the eaves, it's a hazard.

    Do you have a model name/number for the boiler, and a picture of the venting arrangement from both the inside and outside of the house?

  3. #3
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,942

    Default

    Quote Originally Posted by ssen105 View Post
    Hi, I have been told that I have a standard vent boiler installed (I purchased the house a year back) with side of house venting. Is this a problem? Does it need a vertical Line Chimney/can the side way vent be modified? Or do we have to change it to a direct vent boiler?

    Thanks

    Sam
    That depends. If it's an atmospheric vented boiler it needs either a chimney or a power vent.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  4. #4
    DIY Junior Member ssen105's Avatar
    Join Date
    Oct 2013
    Location
    virginia
    Posts
    2

    Default

    >
    Quote Originally Posted by Dana View Post
    Atmospheric drafted boilers need a vent stack sufficiently tall to achieve the necessary draft pressures, and must extend above the ridge >line of the house to limit the risk of back-drafting due to wind. If your side-vented atmospheric boiler has a tall enough stack it can still work. If it simply >terminates at the wall somewhere between grade and the eaves, it's a hazard.

    >Do you have a model name/number for the boiler, and a picture of the venting arrangement from both the inside and outside of the house?
    Thanks. Below is the model detail. The venting system is (sorry I could not attach photos) direct vent which turns to the wall 2 feet above the upper
    side of the Heater.

    Apollo Hydro Heater, Automatic Storage Water Heater, Model A650YRRTL5, capacity 50G
    Input BTU/HR 65000
    Max Inlet 14.00
    Min Inlet 5.00Max Work Pressure 150 PSI

    Hope

Similar Threads

  1. standard vent vs. direct vent
    By karter56 in forum Water Heater Forum, Tanks
    Replies: 4
    Last Post: 03-13-2013, 03:22 PM
  2. Side venting a gas boiler
    By williambonetto in forum Boiler Forum
    Replies: 1
    Last Post: 11-14-2010, 07:43 PM
  3. Direct Vent Boiler Into A Standard Flue?
    By plunger76 in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 10-05-2008, 07:21 AM
  4. Standard Vent (line chimney) vs Direct Vent
    By mjbardel in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 21
    Last Post: 09-13-2007, 05:23 PM
  5. Boiler Combustion Air venting question
    By theaggie in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 10-08-2005, 11:23 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •