    Default pressure surge

    Hey everyone, have a 30 50 pressure switch, when the pump kicks on it produces pressure on cold side,
    just blows out like a air gun, it actually blew out toilet valve in tank.
    I have drained the pressure tank and its at 28 which is where it should be, anybody out there have any idea
    what may be and how to fix

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,678

    Default

    Is it blowing out air? If so, I suspect you have a checkvalve at the tank and water falling back to the well creating a vacuum sucking air in. Was there a galvanized tank before with an airmaker/snifter?

  3. #3
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    Quote Originally Posted by louie 44 View Post
    Hey everyone, have a 30 50 pressure switch, when the pump kicks on it produces pressure on cold side,
    just blows out like a air gun, it actually blew out toilet valve in tank.
    I have drained the pressure tank and its at 28 which is where it should be, anybody out there have any idea
    what may be and how to fix
    I have never seen a pressure tank with a hot side.
    John

  4. #4
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    This seems to be a day in which many people are learning about the problems a second check valve in a pump system can cause.

    You probably have a bad check valve on the pump or a hole in the drop pipe. But it would not be getting air if you didn’t have an extra check valve, most likely above ground.

    Remove the above ground check valve. It is masking the real problem. Then if the pressure drops with the pump off and no one using water, the check on the pump or the hole in the drop pipe will need to be fixed.

Similar Threads

  1. Thermal expansion tank / pressure surge
    By purduephotog in forum Water Heater Forum, Tanks
    Replies: 2
    Last Post: 12-24-2012, 08:25 AM
  2. pump surge
    By Doubler in forum Pumps and Tanks Well Forum & Blog
    Replies: 4
    Last Post: 11-19-2009, 12:13 PM
  3. TR Surge Receptacle
    By dhla in forum Electrical Forum discussion & Blog
    Replies: 0
    Last Post: 04-02-2009, 03:21 PM
  4. Whole house surge . . .
    By sjh in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 12-30-2007, 10:49 AM
  5. Pump chatter/surge at pressure switch
    By jmdeng13 in forum Pumps and Tanks Well Forum & Blog
    Replies: 12
    Last Post: 11-29-2006, 11:36 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •