Thread: main burner BLOWS blows out pilot

  1. #1
    DIY Junior Member oscar1989's Avatar
    Join Date
    Oct 2013
    Location
    northeast ohio
    Posts
    2

    Default main burner BLOWS blows out pilot

    I have a newyorker rg170 3 closed loop standing pilot boiler in my basement.didnt use it for the first year , tried to fire it up last season and had to replace a gas valve,thermalcouple,and pilot it worked for all of two hours and the pilot went out. called service guy again he adjusted flame, installed a shield, still the same thing. the company said that they don't have any info says its to old, any help would be greatly appreciated. was wondering if it could be the main burner itself,thats about the only thing that didn't get replaced

  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,938

    Default

    Quote Originally Posted by oscar1989 View Post
    I have a newyorker rg170 3 closed loop standing pilot boiler in my basement.didnt use it for the first year , tried to fire it up last season and had to replace a gas valve,thermalcouple,and pilot it worked for all of two hours and the pilot went out. called service guy again he adjusted flame, installed a shield, still the same thing. the company said that they don't have any info says its to old, any help would be greatly appreciated. was wondering if it could be the main burner itself,thats about the only thing that didn't get replaced
    You most likely have a draft condition that's blowing the pilot out
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    DIY Junior Member oscar1989's Avatar
    Join Date
    Oct 2013
    Location
    northeast ohio
    Posts
    2

    Default

    from the chimney?

  4. #4
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,644

    Default

    Quote Originally Posted by oscar1989 View Post
    I have a newyorker rg170 3 closed loop standing pilot boiler in my basement.didnt use it for the first year , tried to fire it up last season and had to replace a gas valve,thermalcouple,and pilot it worked for all of two hours and the pilot went out. called service guy again he adjusted flame, installed a shield, still the same thing. the company said that they don't have any info says its to old, any help would be greatly appreciated. was wondering if it could be the main burner itself,thats about the only thing that didn't get replaced


    So a shield was left out of place ? Or it got blown off ?

    If the pilot is not positioned properly then the burner can fill the chamber with gas , then when it does ignite the explosion can blow the flame out. The pilot flame also has to be heating the thermocouple when the Fan is running or not. If the fan affects the pilot then the fan may be creating a draft.

    If you have Exchanger problems, you can look at the flame when the fan is running, to make sure the fan is not pushing air into the burn chamber. If it does then the heat exchanger has holes in it, and can be hazardous to your health.

    The color of the flame should tell you if your Burner is burning properly.


    Be careful playing with Gas.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  5. #5
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,938

    Default

    Quote Originally Posted by DonL View Post
    So a shield was left out of place ? Or it got blown off ?


    Not likely. The shield is an aftermarket fix for a pilot that is being effected by either a draft condition or a burner that is poorly adjusted.

    If the pilot is not positioned properly then the burner can fill the chamber with gas , then when it does ignite the explosion can blow the flame out. The pilot flame also has to be heating the thermocouple when the Fan is running or not. If the fan affects the pilot then the fan may be creating a draft.

    There is usually not much chance to position the pilot improperly, On his boiler the pilot assembly is attached to one of the burners. There's not much margin for screwing that up

    If you have Exchanger problems, you can look at the flame when the fan is running, to make sure the fan is not pushing air into the burn chamber. If it does then the heat exchanger has holes in it, and can be hazardous to your health.

    The color of the flame should tell you if your Burner is burning properly.


    Be careful playing with Gas.
    The boiler is a 30 plus year old, open log burner style. Chimner draft issues can cause the problem as can combustion air starvation. The boiler itself is so old and inefficient that putting another dime into it is a waste of money.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  6. #6
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,644

    Default

    Quote Originally Posted by Tom Sawyer View Post
    The boiler is a 30 plus year old, open log burner style. Chimner draft issues can cause the problem as can combustion air starvation. The boiler itself is so old and inefficient that putting another dime into it is a waste of money.

    I guess I need to learn how to read better.

    Excuse me for having my Head up my Ass.


    It is a tough decision when you should give up on something Old.

    The new stuff is yet to impress me, but they do have plenty of safety controls.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

Similar Threads

  1. GFCI blows on jacuzzi
    By Carl Fredricksen in forum Electrical Forum discussion & Blog
    Replies: 10
    Last Post: 08-08-2012, 01:14 PM
  2. Takagai TM-1 blows fuse on circuit board
    By magconpres in forum Tankless Water Heater Forum
    Replies: 5
    Last Post: 04-20-2012, 02:39 PM
  3. Replies: 41
    Last Post: 11-14-2010, 03:46 PM
  4. Cold air blows in with the heat through vents...
    By pestario76 in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 03-05-2010, 03:57 PM
  5. Pensotti blows out
    By Pensotti in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 08-26-2008, 04:20 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •