    10 feet elevation causes a 4.33 PSI drop. Add to that any frictional losses due to the water flowing. If you are measuring 52 PSI at the house while you are not using significant water, the pressure at the meter is a lost less than 70 PSI, or the elevation change is a lot more than 10 ft.

    Once the supply pipe is filled, as much water comes out of it at the house as goes into it at the meter for all practical purposes.

  2. #17
    DIY Junior Member AlexS's Avatar
    Join Date
    Oct 2013
    Location
    Seattle
    Posts
    20

    Default

    Quote Originally Posted by Reach4 View Post
    If you are measuring 52 PSI at the house while you are not using significant water, the pressure at the meter is a lost less than 70 PSI, or the elevation change is a lot more than 10 ft.

    Once the supply pipe is filled, as much water comes out of it at the house as goes into it at the meter for all practical purposes.
    I'll be measuring the PSI with a gauge tomorrow. I called the local water utility company and they looked in their computer system and told me my meter produces 52 PSI. I know I shouldn't take their word for it, but they are probably close to actual PSI. My point was: If pressure is strong at the meter, say 70 PSI, than I'm thinking the meter will be able to replace water in a 1 1/4" line much easier when water comes out of the line at the house as opposed to a meter producing 52 PSI. Does that make sense? I'm concerned my pressure might be too low at the meter for a 1 1/4" line with a 10' gain in elevation. Maybe I'm making this too complicated in my own mind.

  3. #18
    DIY Senior Member Reach4's Avatar
    Join Date
    Sep 2013
    Location
    IL
    Posts
    1,273

    Default

    Quote Originally Posted by AlexS View Post
    I'll be measuring the PSI with a gauge tomorrow. I called the local water utility company and they looked in their computer system and told me my meter produces 52 PSI. I know I shouldn't take their word for it, but they are probably close to actual PSI. My point was: If pressure is strong at the meter, say 70 PSI, than I'm thinking the meter will be able to replace water in a 1 1/4" line much easier when water comes out of the line at the house as opposed to a meter producing 52 PSI.
    Yes. If the meter pressure was lower, that would be a reason to use bigger pipe.

    Quote Originally Posted by AlexS View Post
    Does that make sense? I'm concerned my pressure might be too low at the meter for a 1 1/4" line with a 10' gain in elevation. Maybe I'm making this too complicated in my own mind.
    I presume at this point, an doubts would be about whether you need something larger than 1-1/4. Terry said "With 300 feet, you would be better off using 1-1/4" Poly ". That's a good indication that 1-1/4 would be up to the job.

    http://www.engineeringtoolbox.com/pe...oss-d_619.html may be of use to you.
    Now how much pressure drop would be too much? Remember you are going to lose 4.33 PSI due to the rise. Losing another 10 PSI during max water use would seem to me to be not so bad. You would be using about 22 GPM at that point if I read that right.
    Last edited by Reach4; 10-22-2013 at 05:06 PM.

  4. #19
    DIY Junior Member AlexS's Avatar
    Join Date
    Oct 2013
    Location
    Seattle
    Posts
    20

    Default

    I presume at this point, an doubts would be about whether you need something larger than 1-1/4. Terry said "With 300 feet, you would be better off using 1-1/4" Poly ". That's a good indication that 1-1/4 would be up to the job.
    I do recall Terry said 1 1/4". I'm taking all the risk and I want to be sure.

    http://www.engineeringtoolbox.com/pe...oss-d_619.html may be of use to you.
    Now how much pressure drop would be too much? Remember you are going to lose 4.33 PSI due to the rise. Losing another 10 PSI during max water use would seem to me to be not so bad. So if your water pressure dropped to 35 PSI, that would not be ideal, but not terrible in my opinion. You would be using a lot of water at that point.
    In summary, a 1 1/4" pipe would mitigate the pressure drop due to a 10' elevation gain and 300' of friction better than a 1" pipe considering 52 PSI from the meter? I looked at the engineeringtoolbox link, but I don't know how to use the charts. Thanks for sending it.

    Also, I'm not considering 1 1/2".
    Last edited by AlexS; 10-22-2013 at 05:17 PM.

  5. #20
    DIY Senior Member Reach4's Avatar
    Join Date
    Sep 2013
    Location
    IL
    Posts
    1,273

    Default

    Quote Originally Posted by AlexS View Post
    In summary, a 1 1/4" pipe would mitigate the pressure drop due to a 10' elevation gain and 300' of friction better than a 1" pipe considering 52 PSI from the meter?
    Yes. I am shocked that you are asking that question.
    Quote Originally Posted by AlexS View Post
    I looked at the engineeringtoolbox link, but I don't know how to use the charts. Thanks for sending it.

    Also, I'm not considering 1 1/2".
    Please do not think that 1 inch would be a performance improvement over 1-1/4 in any way.

  6. #21
    DIY Junior Member AlexS's Avatar
    Join Date
    Oct 2013
    Location
    Seattle
    Posts
    20

    Default

    Quote Originally Posted by Reach4 View Post
    Yes. I am shocked that you are asking that question. Please do not think that 1 inch would be a performance improvement over 1-1/4 in any way.
    I consider calculating pipe size the hardest part, not the actual work. I really appreciate all your posts Reach. I'm going with 1/1/4". I already have a 300' roll of 1 1/4". I bought 200 PSI CTS. Did I make a mistake? Should I have purchased IPS? I think the inside dimensions are the same, but the walls are a little thicker on the IPS.

  7. #22
    Sprinkler Guy Wet_Boots's Avatar
    Join Date
    Mar 2007
    Location
    Metro NYC
    Posts
    798

    Default

    Quote Originally Posted by AlexS View Post
    I consider calculating pipe size the hardest part, not the actual work. I really appreciate all your posts Reach. I'm going with 1/1/4". I already have a 300' roll of 1 1/4". I bought 200 PSI CTS. Did I make a mistake? Should I have purchased IPS? I think the inside dimensions are the same, but the walls are a little thicker on the IPS.
    You have it backwards, but it doesn't matter. You have the 1-1/4 CTS poly, so use it in good health. You WILL purchase waterworks compression fittings for it, that include the stainless-steel internal stiffener, as there is no other usable choice available. (insert fittings are definitely not sized for CTS poly tubing)

  8. #23
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,207
    Blog Entries
    1

    Default

    It looks like 1-1/4" CTS has a 1.05" Inside diameter.

    So the chart below for 300 feet, more closely would be for the 3/4" meter, and 1" pipe.

    In the 70's I run 350 feet with 1" poly and was a bit stunned to see how little water came out the end.
    I was used to hooking for water services between 40 and 80 feet, where the water would just shoot out the end of the pipe like a fire hose.
    The 350 foot line was running at 72 PSI and there wasn't much there at the end. Friction does take it's toll.

    That's the last time I ever even considered using 1" for that distance.
    The house next door, years later when that was replaced, we went with 1.5" PVC.

    Last edited by Terry; 10-28-2013 at 09:54 AM.

  9. #24
    DIY Junior Member AlexS's Avatar
    Join Date
    Oct 2013
    Location
    Seattle
    Posts
    20

    Default

    Thank you all. Trenching was the hardest part, not calculating proper pipe size as I said earlier.

Similar Threads

  1. Can I connect PEX directly to water meter in basement? (NJ)
    By gil716 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 09-14-2011, 06:20 PM
  2. Where to connect hot water recirculation line at water heater?
    By gplumb in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 16
    Last Post: 02-06-2011, 07:51 AM
  3. Connect a new line to a water softener
    By marky in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 11-28-2008, 02:07 PM
  4. Replacing water line from meter to house...
    By gdog in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 07-03-2008, 10:35 PM
  5. Guesstimates for new water line from meter to house
    By bronsonb in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 04-10-2005, 07:11 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •