    Default Generator size for submersible pump

    What's the minimum size generator (surge watts/continuous watts) that I would need
    to start and run a 1/2 hp, 240 volt, 4 amp (FLA) submersible pump ?

    I'm looking at the Harbor Freight 4000 watt surge/3200 watt continuous model
    and was wondering if it would do the job.

    Thanks,
    Arky

  2. #2
    In the Trades Texas Wellman's Avatar
    Join Date
    Feb 2010
    Location
    SE Texas-Coastal
    Posts
    487

    Default

    It should. Are you using a 3-wire pump? FYI a Franklin 3 wire uses about 1/2 the starting power of a Franklin 2-wire.

    Faradyne motors have the capacitor in the motor so there is no difference between 2-wire and 3 wire I'm told.

    Quote Originally Posted by Arky217 View Post
    What's the minimum size generator (surge watts/continuous watts) that I would need
    to start and run a 1/2 hp, 240 volt, 4 amp (FLA) submersible pump ?

    I'm looking at the Harbor Freight 4000 watt surge/3200 watt continuous model
    and was wondering if it would do the job.

    Thanks,
    Arky

  3. #3
    DIY Member Arky217's Avatar
    Join Date
    Jan 2008
    Location
    Arkansas
    Posts
    40

    Default

    Quote Originally Posted by Texas Wellman View Post
    It should. Are you using a 3-wire pump? FYI a Franklin 3 wire uses about 1/2 the starting power of a Franklin 2-wire.

    Faradyne motors have the capacitor in the motor so there is no difference between 2-wire and 3 wire I'm told.

    Well, I've tossed it back and forth a dozen times or more on 2 wire vs 3 wire and
    after reading pros and cons till my eyes crossed, I'm leaning toward the 2 wire.
    Can't really give a definitive reason why; there's good arguments on both sides.
    The actual pump I've decided on is a Gould, 7gpm, 230v, 4amp, 2 wire, model # 7GS05422C.

    I want to go as cheap as possible on the generator since it's main use will be to power the pump during power outages.
    I'll just be running it only long enough to refill the pressure tank (about 15 gal. of water) and then off again til I've emptied the tank again.
    And the Harbor Freight 4000/3200 watt model is on sale for $289.99.
    Just want to make sure it will do the job for the pump.
    ( I already have an efficient Honda EU2000i to power other small 120 volt items.)

    Arky

  4. #4
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,153

    Default

    I have a Honda 3500 that I use to test wells with a 1.5 HP pump. It will start the three wire, with control box pump easily. I don’t think it would start a 1 HP in 2 wire.

    There is a company that makes controls that will start and stop a generator using the pressure switch on the pressure tank. Pretty cool. I will post the link tomorrow when I get to my office.

    Also, if you use the longest length of the smallest wire recommended for the motor horsepower, it makes a soft start and is much easier on the generator.

  5. #5
    DIY Senior Member VAWellDriller's Avatar
    Join Date
    Sep 2012
    Location
    Richmond, VA
    Posts
    161

    Default

    You mentioned you already have a honda EU 2000...I know for a fact that you can run a Grundfos 1/2 hp 115 volt 3" SQ pump on the 2000 eu with no problems whatsoever. You can also run that same grunfos on a 1000 running / 2000 surge inverter with no problems at all. If you spend a little more on getting that pump, you won't have to buy what is sure to be a very poorly made Harbor Freight generator.

  6. #6
    DIY Member Arky217's Avatar
    Join Date
    Jan 2008
    Location
    Arkansas
    Posts
    40

    Default

    Quote Originally Posted by VAWellDriller View Post
    You mentioned you already have a honda EU 2000...I know for a fact that you can run a Grundfos 1/2 hp 115 volt 3" SQ pump on the 2000 eu with no problems whatsoever. You can also run that same grunfos on a 1000 running / 2000 surge inverter with no problems at all. If you spend a little more on getting that pump, you won't have to buy what is sure to be a very poorly made Harbor Freight generator.
    You make a very interesting point.

    For some reason, I was thinking that I had to buy the wire locally (don't know why I didn't check online, brain lapse I guess) and the
    largest available submersible pump wire locally is 12 ga.

    And according to the Goulds specs for their 1/2 hp, 115 v, 2 wire pump, the FLA is 7.9 amps and the maximum wire run should not exceed 178'
    which is just under my run of 180'. That is the reason that I thought that I needed to go with 240 volts.

    But if I go with 10 ga. wire, it would be a different story.

    Now, If I'm figuring this right, the total dynamic head that the pump would see for my desired 30 to 50 psi pressure
    would be 173 feet (100' to pump + 4' uphill + 69'(30psi) to 219 feet (100' to pump + 4' uphill + 115'(50psi).

    So, in order to keep this total dynamic head (173' to 219') within the performance curve of either a Goulds or Grundfos 1/2 hp, 115v, 2 wire pump:

    The Goulds pump would be the 7gpm, mod#7GS05421C with a FLA rating of 7.9 amps and a locked rotor rating of 28 amps.

    And the Grundfos pump would be the 5gpm, mod#5SQ05-180-115v with a FLA rating of 7.7 amps
    and a overload (locked rotor ?) rating of 11 amps.

    Now, as I mentioned, my wire run is 180'.
    For the Goulds pump, their max recom. run for 12 ga. is 178', and for 10 ga. is 284'.
    For the Grundfos pump, their max recom. run for 12 ga. is 220' and for 10 ga is 360'.

    These figures seem a little odd, however,
    since Grundfos is allowing for a longer wire run even though their pump FLA is practically the same as the Goulds.

    Also, I'm confused by what Grundfos is calling the overload amps; surely this is not the locked rotor or start current,
    or is it, since one of the features of the Grundos pump is stated as:

    "Excellent starting capabilities
    The integrated electronic unit of the motor features soft starting. Soft start reduces the starting current and thus gives the pump a smooth and steady acceleration.
    The soft starter minimizes the risk of wear on the pump and prevents overloading of the mains during start-up.
    The excellent starting capabilities are a result of the high locked-rotor torque of the permanent magnet motor together with the few pump stages. The high starting reliability also applies in case of low voltage supply."

    At any rate, my main question is: is this model Grundfos the same one that you are referring to that you said that your Honda EU2000i
    can start without any problems ?

    And is their overload rating of 11 amps really the start current ?
    If so, I can see how the Honda will start it with no problems.

    I can't see the Honda, however, starting the Goulds pump with its 28 amp start current
    (that's 3220 watts, Honda is only rated for 2000 watts surge)

    One more question: Even though it appears that I might be able to use the 115v Grundfos pump successfully
    and start it with the Honda, is there any major downside (besides not being able to use the Honda)
    in my particular situation, for using a 115v pump rather than a 230v pump ?

    Thanks,
    Arky

  7. #7
    DIY Senior Member craigpump's Avatar
    Join Date
    Apr 2012
    Location
    ct
    Posts
    710

    Default

    You're thinking this thing to death.

    Use a 230 volt pump, Goulds or Grundfos with #12 wire and be done with it. We install 2 and 3 wire pumps, they both seem to have the same reliability. Given the thunderstorms in Ar, I would probably go with a 3 wire and keep an extra control box handy.

    And forget about a Harbour Freight generator, it will let you down when you need it the most.

  8. #8
    In the Trades Texas Wellman's Avatar
    Join Date
    Feb 2010
    Location
    SE Texas-Coastal
    Posts
    487

    Default

    Craig, it's in a home that is "off-grid" so I can see why he's interested in these numbers.

  9. #9
    DIY Senior Member craigpump's Avatar
    Join Date
    Apr 2012
    Location
    ct
    Posts
    710

    Default

    He said the generators main purpose is to power the pump during power outages.

    He isn't going to save any money by using a 115v unit, in fact it may cost him more when you consider that #12 is good for about 160' before he would have to up his wire size to #10. In addition, the 230v unit will draw less current which in theory should run cooler and provide a longer life, plus he can run #12 up to 650,' or for more savings he could use #14 and run it 400'.

    I'd go with a 230volt unit

  10. #10
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,153

    Default

    Here is the link to that generator that will start and stop using the pressure switch for the pump.

    http://dietschmanufacturing.com/

  11. #11
    In the Trades Texas Wellman's Avatar
    Join Date
    Feb 2010
    Location
    SE Texas-Coastal
    Posts
    487

    Default

    Oops, got the OP confused with another poster from Ark. that was off-grid. My mistake.

    I would probably go with the 230V 3 wire pump and spend a little extra coin and get the Honda 3500 generator. That harbor freight unit isn't worth buying.

    Quote Originally Posted by Texas Wellman View Post
    Craig, it's in a home that is "off-grid" so I can see why he's interested in these numbers.

  12. #12
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,632

    Default

    You do not really need to spend a lot on a generator.

    Any 8 HP with a briggs will work good.

    That one at HF looks like 6.5 HP and you would be happier with a 8 horse.


    Good Luck
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  13. #13
    DIY Senior Member guy48065's Avatar
    Join Date
    Sep 2013
    Location
    SE and north MI
    Posts
    111

    Default

    Quote Originally Posted by craigpump View Post
    You're thinking this thing to death.

    Use a 230 volt pump, Goulds or Grundfos with #12 wire and be done with it. We install 2 and 3 wire pumps, they both seem to have the same reliability. Given the thunderstorms in Ar, I would probably go with a 3 wire and keep an extra control box handy.

    And forget about a Harbour Freight generator, it will let you down when you need it the most.
    Not always. I bought a Champion 3500/4000W genny, chosen because it far exceeded the ratings for my submersible. I connected to my panel with everything shut off and when I threw the breaker for the well the generator stalled like I had shoved a crowbar in it. My guess is the rotating mass of these cheap & light Chinese generators is insufficient to push through the startup current of a submerged pump.

    It's probably best to do the math and make the best selection rather than buy on price or convenience.
    Romeo and Atlanta, MI

  14. #14
    In the Trades Texas Wellman's Avatar
    Join Date
    Feb 2010
    Location
    SE Texas-Coastal
    Posts
    487

    Default

    What is your submersible? Brand/Horsepower?

  15. #15
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,632

    Default

    Quote Originally Posted by guy48065 View Post
    Not always. I bought a Champion 3500/4000W genny, chosen because it far exceeded the ratings for my submersible. I connected to my panel with everything shut off and when I threw the breaker for the well the generator stalled like I had shoved a crowbar in it. My guess is the rotating mass of these cheap & light Chinese generators is insufficient to push through the startup current of a submerged pump.

    It's probably best to do the math and make the best selection rather than buy on price or convenience.


    The Champion 3500/4000W is a 6.5 HP gen.

    The 8 HP Briggs with the cast iron flywheel will keep you operating at 60HZ.

    A lot of the newer BS has a aluminum flywheel and depend on the flywheel affect to happen in the generator, When you really need the weight on both ends of the Crankshaft.


    Inverter Generators can work good IF you have batteries connected.


    Have Fun.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

Similar Threads

  1. Need advise on submersible pump & generator
    By Let it rain in forum Pumps and Tanks Well Forum & Blog
    Replies: 6
    Last Post: 09-01-2011, 02:26 PM
  2. Submersible Pump Size
    By lray882 in forum Pumps and Tanks Well Forum & Blog
    Replies: 9
    Last Post: 04-15-2011, 08:08 AM
  3. Need advice on submersible pump size. Pleeeease.......
    By Raggare in forum Pumps and Tanks Well Forum & Blog
    Replies: 13
    Last Post: 02-28-2011, 12:15 PM
  4. Generator sizing for submersible pump
    By JAR8832 in forum Electrical Forum discussion & Blog
    Replies: 10
    Last Post: 01-06-2010, 12:56 PM
  5. Running a submersible pump off generator
    By tickridgescott in forum Pumps and Tanks Well Forum & Blog
    Replies: 9
    Last Post: 06-22-2006, 09:44 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •