Thread: outdoor pvc pipe and saddle tee question about maximum pressure

  1. #1
    DIY Junior Member hamlet_jones's Avatar
    Join Date
    Oct 2013
    Location
    Idaho
    Posts
    11

    Default outdoor pvc pipe and saddle tee question about maximum pressure

    Hi folks,

    I have a 1-1/2 pvc supply pipe in a 1100 foot run from my well to my house. I need to tap into this near the middle section for irrigation supply to a planned orchard.

    I am contemplating using a sch40 saddle tee. I've dug up the pipe (36 inches deep). Of course, there is no lateral flex in the line, so either it's a saddle tee or
    I cut out a chunk and splice in a regular tee paired with a compression coupling.

    Thoughts?

    How much psi will a saddle tee take? My line is 65psi.

  2. #2
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    Don't use a saddle tee. They are trouble waiting to happen. You also must install a back flow prevention device where you branch off and the connections would be made with unions. You should consult with an irrigation supply company for the bests BF device. These are supposed to be re-certified annually by a licensed inspector. Idaho may not enforce these regulations, but you sure don't want contaminated water drawn back into you domestic supply.

  3. #3
    DIY Junior Member hamlet_jones's Avatar
    Join Date
    Oct 2013
    Location
    Idaho
    Posts
    11

    Default

    Okay, I'll use a Slip-Fit with a tee. I'll look for an appropriate BF.

  4. #4
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    Or you can use something like four 90's or two 90's
    Nothing says you can't jog sidewise in the ditch. Or up and down.

  5. #5
    DIY Junior Member hamlet_jones's Avatar
    Join Date
    Oct 2013
    Location
    Idaho
    Posts
    11

    Default

    Jogging sideways in a ditch? Story of my life...

    I want to avoid the downtime with glue, so I may use compression. This line also supplies a rental home, and cabin. Trying to keep everybody happy.

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    The last water service leak I worked on, I had to remove the leaking compression fitting they had used to repair a previous leak. It was a dressler coupling I removed.

    If you are using glued fittings, give it and hour and turn the water back on.
    That's what I like doing.

  7. #7
    DIY Junior Member hamlet_jones's Avatar
    Join Date
    Oct 2013
    Location
    Idaho
    Posts
    11

    Default

    Okay, thanks Terry. I'll use the primer/glue and be done with it.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    Saddles are often used on larger pipe sizes to make a connection, but are seldom used with smaller sizes. If you do use one be sure to use hose clamps on both ends plus primer and glue on the pipe and saddle. Put the saddle on BEFORE you make the hole in the pipe. I fact, with my tools, I would also install the valve, then I could drill the hole without turning off the water, then close the valve when I removed the drill.
    Licensed residential and commercial plumber

  9. #9
    DIY Junior Member hamlet_jones's Avatar
    Join Date
    Oct 2013
    Location
    Idaho
    Posts
    11

    Default

    Interesting. Will a well primed, glued, and CLAMPED saddle last? I like the part about drilling it with the valve installed! (Ball valve?) I'm sure you're using some kind of splash-shield and a cordless drill to prevent electrocution...

  10. #10
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    No, I have a "Hot tap" device that screws on to the valve and drill is inside it. No leaking.
    Licensed residential and commercial plumber

  11. #11
    DIY Junior Member hamlet_jones's Avatar
    Join Date
    Oct 2013
    Location
    Idaho
    Posts
    11

    Default

    Quote Originally Posted by hj View Post
    No, I have a "Hot tap" device that screws on to the valve and drill is inside it. No leaking.
    Sounds like a tool the NSA should have used

Similar Threads

  1. Frozen/Burst Outdoor Pipe Question
    By bh81 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 01-25-2011, 10:23 AM
  2. saddle valve on black pipe
    By Fubar411 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 05-13-2008, 08:25 AM
  3. IceGuard - Maximum length of T pipe
    By lemonhead in forum Pumps and Tanks Well Forum & Blog
    Replies: 0
    Last Post: 04-05-2008, 03:23 PM
  4. Maximum length of PE pipe in a well?
    By Raucina in forum Pumps and Tanks Well Forum & Blog
    Replies: 9
    Last Post: 09-19-2006, 09:58 AM