    Default How does my planned layout look

    Hi everyone. First I would like to say this forum has been so much help. I have been working on a bathroom remodel for some time now. I finally got all the demo work finished. I am now at the point the plumbing needs to be relocated.
    Here is the goal of the remodel. I am putting a bigger tub in place of existing tub. I will be moving the toilet and sink across to the opposite wall. I will then add a stand up shower in reclaimed closet space.
    I will put up my crude drawings of the existing layout and my plan for the new layout.
    Right now the sink has a 2" drain line with a 2"vent to roof. The sink line drops down and turns a 90 running directly under the interior wall. It connects to the toilet line that runs over to the main line of house. The bathtub drain connects in at the toilet/sink junction. Hope that makes sense. Maybe the drawing will help you see it.

    The new plain is to run the new shower in at the spot the sink line is currently and keep the 2" vent in place. This should serve as the vent for shower and still serve the tub????? The toilet line will be extended about 3 foot to the other wall. The sink will be moved over as well. The sink line will be 2" with a vent to roof . The sink drain will run over to the toilet line and connect in with a 3x3x2 wye or combo. This should vent the sink and the new toilet location???

    I should add that our house is built on a slab. The main line runs about 8 inches behind the interior wall off bath. I am getting all permits and will have it inspected. I just don't want to have do waste time doing it wrong. I want it to not only work but be done right as well. The new lines are shown in green.
    Thank to anyone that looks at this.
    BillyName:  existingbath.jpg
Views: 57
Size:  32.8 KBName:  newlayout1.jpg
Views: 60
Size:  36.7 KB

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,679

    Default

    The drawing looks good, but what really counts is HOW you install the piping. I have seen many "pretty drawings" but when the piping was installed it was a disaster which had to be completely gutted and redone.
    Licensed residential and commercial plumber

  3. #3
    DIY Junior Member itmyfault's Avatar
    Join Date
    Dec 2012
    Location
    Arkansas
    Posts
    16

    Default

    Thanks for responding. My plan was to connect new lav line to extended toilet line using a 3x3x2 wye. Does this fitting have to be installed at 45 or simply connect together maintaining the 1/4 drop?
    The shower branch I was going to connect to the old lav line using a 2x combo or wye pointing upward and connecting to the existing vent line.

    I have also been debating connecting the new 2" vent to the existing 2" in attic. That way I eliminate making a new hole in the roof.

    Thank you for again for taking time to check my plans out. I am one of those that builds things in my head a hundred times before I actually do it. I also like doing things right the first time. Nothing worse than taking work apart due to mistakes or miscalculations.

    I had two plumbers actually look at what I was planning and suggest using an AAV under the sink instead of running a vent. They said it would save some time and work. I just didn't like that idea. I would rather take the time and run the actual vent. Needless to say I didn't trust their advice.

    This is the reason I posted on here.
    Last edited by itmyfault; 10-17-2013 at 12:23 PM.

Similar Threads

  1. Confirmation on bathroom layout (detailed layout provided)
    By dantheboatman in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 08-27-2013, 12:12 PM
  2. DWV Layout Basement Bathroom - layout review
    By great white in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-13-2012, 05:28 PM
  3. Doorless outdoor urinals planned for Australian city
    By commentking in forum Toilet Forum discussions
    Replies: 0
    Last Post: 09-29-2010, 09:18 AM
  4. Can't find drain under tile for a planned bathroom
    By Do it yourself Dave in forum Shower & bathtub Forum & Blog
    Replies: 4
    Last Post: 12-05-2008, 04:34 AM
  5. New house planned: What's the best plumbing designs in the world?
    By dereks in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 14
    Last Post: 09-07-2007, 06:59 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •