    Default Galvanized supply line question

    We just demolished a 60 year old home and are building a new house. We found that the supply pipe from the city water supply is 1.5" galvanized. It looks to be in pretty good shape, but has some evidence of internal and external corrosion. It's about a 270' run to the meter near the street and about half of this is in an easement, but under the neighbor's extensively landscaped yard. Would it be possible to use this pipe as conduit and run a pex pipe inside it? Or do you have any other suggestions? Thanks, Ed

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    The required size of the pipe and the distance it has to travel, plus how much water your house needs all go into deciding how big the pipe should be. If the pipe ends up too small, while the pressure will stay the same when nothings on, as you try to use more water than the pipe can handle, the flow can't keep up. Think soda straw verses fire hose...at a trickle, they're the same, but if you need it, you'll get LOTS more water out of the fire hose!

    Without knowing what's going to be in the new house, it's hard to say what size you need. 1.5" supply pipe is bigger than an average house, but you may not be planning an average house. Are you measuring OD or ID? If OD, that could be much more common. IOW, need more info.

    There are ways to minimize disruption to the landscaping depending on the soil, how deep the line needs to be and probably other factors. But, I doubt you can use it as a conduit for pex...it would end up being too small of a diameter for your needs.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Senior Member craigpump's Avatar
    Join Date
    Apr 2012
    Location
    ct
    Posts
    710

    Default

    Dig a trench and put a new line in. Just because the pipe looks ok where you can see it doesn't mean it's good the entire run, nor does it mean you can slide another line through it. I have a piece in my shop that was thought to be good too until it was dug up. It looks like an 1.25 galvanized flute.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    The inside of the pipe SHOULD be so fouled with rust the you would not be able to run any adequate sized tubing through it.
    Licensed residential and commercial plumber

  5. #5
    DIY Member u.s.coins's Avatar
    Join Date
    Mar 2012
    Location
    Pennsylvania
    Posts
    35

    Default

    I wouldn't even try using any of the galvanized original. just inviting nightmares. jmo

  6. #6
    DIY Junior Member esmith's Avatar
    Join Date
    Oct 2013
    Location
    Richland, WA
    Posts
    4

    Default

    Thanks for your replies. Here's a picture of a short section of the pipe.

    Name:  DSC_0004.jpg
Views: 152
Size:  42.6 KB

    It's about 1 9/16 id and 1 15/16 od (where it's not corroded.) Seems like schedule 40 size 1.5" to me. I could get a piece of 1" pex through this piece, but through 270' ???, especially if the corrosion varies as much as your experiences indicate. I don't know why the original pipe is this size. I know that they originally owned the entire acre and maybe it was irrigated with city water at some point in the last 60 years? It's currently irrigated from the river. The new house is not unusual. 3.5 bathrooms, kitchen, etc. 2 stories with a basement. Does a 1" pex line 270' long seem adequate. Static water pressure is pretty good down here. I'm only a half mile from the water treatment plant, same elevation. I haven't measured the static water pressure, but I'd guess it's 60-80 psi. My temp hydrant will about blow a short section of 5/8" garden hose out of your hand. Do you think I could ream the corrosion out the inside of the pipe with a sewer snake to allow more room to use it as conduit for a pex line? Thanks.
    Last edited by Terry; 10-22-2013 at 09:31 AM.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    Sewer snakes are no that long and do NOT remove rust from the pipes, unless you use a carbide cutter.
    Licensed residential and commercial plumber

  8. #8
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    The way the water supply pipe is sized requires knowing at least three things: distance, Water Supply Fixture Units (WSFU), and the water pressure. The goal on any supply is to still have adequate flow and pressure when you're using your water. Your town may have it's own charts to determine the supply line (and meter size), but this reference should give you a running start http://www.engineeringtoolbox.com/Wa...ts-d_1073.html and once you've added those up, go to here http://www.engineeringtoolbox.com/wf...es-d_1075.html to get an idea on the pipe. Unfortunately, their charts only go up to a max of 200', but you can interpolate from the curves on the graphs and be fairly accurate, or search for some others.

    1" pex, I don't think will cut it...note, the pipe sizes are based on (I think) copper nominal sizing, and 1" pex is closer to the flow capacity of 3/4" copper. Run the numbers, report back.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  9. #9
    DIY Senior Member dj2's Avatar
    Join Date
    Aug 2013
    Location
    California
    Posts
    314

    Default

    You are facing the inevitable - replacing the main line, the entire 270 feet.

  10. #10
    DIY Junior Member esmith's Avatar
    Join Date
    Oct 2013
    Location
    Richland, WA
    Posts
    4

    Default

    I've come up with about 34 fixture units in the new house. Extrapolating from this graph it looks like I'd need an 1 1/4" line. Name:  WSFU.jpg
Views: 112
Size:  36.4 KB The 2nd order polynomial trendline looks like a pretty good fit to the available data, but its quite an extrapolation and seems kind of conservative. Anyone have any practical experience in this sort of situation?
    Last edited by esmith; 10-22-2013 at 08:04 AM.

  11. #11
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    How many people you have in the house and how many of them could be using faucets simultaneously, (i.e. showers or bathtubs), is a better indication of "volume demand" than the WSFU, which is a theoretical number. you could have ten shower rooms, but if there are only two people living in the residence, the flow demand will be less than if there were 10 teen agers living there.
    Licensed residential and commercial plumber

  12. #12
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    For that distance, a 3.5 bath home would require a 1.25" line.

    1" PEX is more like a 3/4" line.

    Last edited by Terry; 10-22-2013 at 09:50 AM.

  13. #13
    DIY Junior Member esmith's Avatar
    Join Date
    Oct 2013
    Location
    Richland, WA
    Posts
    4

    Default

    Would you recommend PEX or HDPE or gold (I mean copper)? There's only my wife, me and a 13 year old boy who likes long, hot showers in the house full time. I measured the static pressure and it looks like 68 psi.

  14. #14
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    I concur with the other advising total line replacement. If you elect to go with copper, you should know that copper joints underground must be brazed, not soldered. Many people chose PVC to replace their old lines, others like copper. I can understand with the distance you have to cover, cost will be a consideration. Also with that distance, it would be wise to consider a professional. They could do the job and your neighbor's yard would left in good condition. You really don't have too much choice about putting in a new line, patching old galvanized is not very wise. Might get you by for awhile, but eventually it will develop leaks.

  15. #15
    DIY Senior Member craigpump's Avatar
    Join Date
    Apr 2012
    Location
    ct
    Posts
    710

    Default

    Poly would be the least expensive, plus I'm not sure how well PEX would hold up in a direct bury application.

Similar Threads

  1. Replacing old galvanized water supply line from meter to entry at house
    By k9mlxj in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 37
    Last Post: 09-26-2013, 05:03 PM
  2. PEX Supply Line Question
    By maxmitchell in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 05-12-2011, 01:07 PM
  3. Replace old galvanized supply line from well
    By Stude60 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 10-09-2010, 10:58 PM
  4. Supply Line Question
    By waxgroove in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 03-23-2009, 06:11 AM
  5. Secondary (supply) line question
    By HockeyFan in forum Electrical Forum discussion & Blog
    Replies: 14
    Last Post: 02-27-2008, 06:03 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •