    Default Drain lines for bathroom renovation

    I am renovating a 1st floor bathroom and I am moving the location of the toilet and tub. Referencing the drawing the "(Vent) new sink" vertical section has always been there. It is a vertical vent that goes up through the 2nd floor and out through the roof. The sink in this 1st floor bathroom connects to this vent with a Sanitary T. The tub trap used to be closer to this vertical vent/sink line and connected directly in to it, then it ran over to the toilet which was pretty much above the 3" line going off to the bottom left of the diagram. The upstairs tub, upstairs toilet, washer, and 3" line going off to the bottom left have always been there. I was wondering if you guys would give some helpful criticism of what I have planned. I know don't have lengths on there, but the line from the tub trap to the vent doesn't not exceed the max of (I think) 6'. Thanks for any help.

    Name:  plumbing.jpg
Views: 129
Size:  100.2 KB
    Last edited by lemmy; 10-10-2013 at 08:25 AM.

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,151

    Default

    All of the pipe downstream of the toilets will need to be 3". The laundry will need a vent.

  3. #3
    DIY Member lemmy's Avatar
    Join Date
    Aug 2013
    Location
    knoxville, tn
    Posts
    31

    Default

    The laundry does have a vent back closer to the trap but it isn't shown on the drawing. The only part I wasn't sure about is where the tub drain goes through the trap and then over to the horizontal run from the vent over to the toilet. Is it ok to have the line from the tub come in to this horizontal section for the vent or should I try to bring it in to the vertical section of the vent line? Thanks.

  4. #4
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,151

    Default

    As long as you are within the maximum distance your plumbing code allows for distance between the trap and vent, the tub and water closet are being wet vented through the lavatory, which is allowed in most places.

  5. #5
    DIY Member lemmy's Avatar
    Join Date
    Aug 2013
    Location
    knoxville, tn
    Posts
    31

    Default

    Thank you very much! That was the confirmation I was hoping for.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    The way you have it drawn, it looks like the tub trap WILL be too far from the vent, and connecting to the vertical pipe would be the ideal way.
    Licensed residential and commercial plumber

Similar Threads

  1. Questions about bathroom renovation
    By lucgallant in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 17
    Last Post: 01-23-2011, 01:39 PM
  2. heights for supply and drain lines for bathroom sink
    By Steve_P in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 09-21-2010, 01:27 PM
  3. Proposed layout for bathroom drain lines
    By pghsebring in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 10-01-2009, 01:22 PM
  4. Bathroom renovation
    By Clive in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 05-28-2007, 01:53 PM
  5. Bathroom Remodel - Toilet Drain Lines
    By ptl_10 in forum Remodel Forum & Blog
    Replies: 13
    Last Post: 08-11-2005, 05:57 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •