Which Tankless To Install

Users who are viewing this thread

dtherrien

Licensed Building Contractor
Messages
15
Reaction score
0
Points
1
Location
Massachusetts
I am just about ready to replace my 20 year old State 40gal hot water heater.
I have decided on one of the two: Rannia Rc 80HPI or the Navien NPE 210A...both would be LP gas.
My house is set up for propane. In the last 10-11 years i install a Rannai room heater in the downstairs (Finished basement) and also one in the upstairs. They have run flawlessly.
I have two full baths and 5 people in the house.
Cook Stove
2 Rannai heaters
And then the new water heater.
I know with the Rannai i will have to run a new 3/4" line from the tank.
The Navien states that i can use the existing 1/2" line....but i think i will go with the larger if i decide on the Navien.
I am partial to Rannai....but i dont know much about the tankless water heaters.
Which of the two brands would you people recomend?

David
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
I think you may regret running it on propane in the long run. Electricity is getting cheaper.

I could be wrong.


Good Luck.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
The big thing about tankless systems is their temperature rise ability. In MA, you ground temperature can get quite low in the middle of the winter...I've measured 33-degrees at my upstairs tap (that's after running through a string of basements in our condo complex, then up a couple of stories!). This can stress a tankless, and you must size it according to the actual temperature rise you require and the volume you need at any one point.

In pretty much anyplace in the USA, propane will end up cheaper per BTU than using electrical, and to use electric on a whole house tankless would likely require upgrading your main panel and line back to the street! There may be a few exceptions where you have subsidized hydro-power available or in a co-op.

If you size the thing properly, they can work in any climate, but that doesn't mean they are the most economical way to do it. In some cases, you may need more than one in series to get the temperature rise and volume you want...just depends on your typical max draws, OR, if you can accommodate the quirks of the system.

You need to read the fine print on the volume available with YOUR temperature rise requirements and compare that with your actual volume will be available.
 
Last edited:

dtherrien

Licensed Building Contractor
Messages
15
Reaction score
0
Points
1
Location
Massachusetts
Propane or electric are my only options. I am not set up for fuel oil.
I was also thinking about a hybrid electric tank water heater...but not sure how much it will save me in the long run. In the summer with the a/c and the pool filter running, my electric for 3-4 months are up.
I dont think my water in the winter gets below 40. I have well water.
I also question what the temp rise will be with the tankless.
I like the compactness of the tankless.
I am trying to go with something more efficient. My hot water heater now is using the greatest share of the propane.
The cook stove doesnt use much and for most of the winter i burn wood.
A year i go through about 550 gallons of propane....thats only turning the room heaters on if we are gone for the weekend.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
FWIW, most of the advertised GPM on tankless are based on 50-degree input water, so you have to read the fine print to adjust it for your bigger delta.
 

Zl700

DIY Senior Member
Messages
257
Reaction score
4
Points
18
Location
Western NY
Both heaters you noted are high-efficiency condensing and actually the colder the inlet water the more efficient they are. Cold temps don't hurt the units but can reduce output because of desired temperature rise. All quality tankless such as these have water adjustment valves to meter the flow once the unit hits full fire to maintain desired output temp set point. That being said the energy cost to raise the water is what's looked at.
According to AHRI, the there is no higher efficient gas-fired water heater in the world, at the Navien .97 EF.

How do they make water, it's about the BTUs, and the rise required. The NPE is fired at 180,000 BTus, and the is a bigger one, the NPE240 at 199,900 BTUs.

The NPE you mention is both more efficient and higher fired than the a Rinnai mentioned so let's use that.

180,000 / 8.34 / 60 / 80 (water heated from 40 to 120) x .97 = 4.36 GPM of continuous hot water
Mixing it down to 110 for bathing, basically you have 4.75 GPM.
The bigger 240 models would give you about 5.25 GPM at 110 degrees.

One thing you never do if you need a constant flow higher than that is never never never run two or more tankless units in series, unless this is a commercial application for example and the second one is a high temp booster feeding a dishwasher for example.

Tankless water heaters have serpentine piping, elbows, valving, screens flow sensors and more. Installing a condensing tankless inline with existing piping is like adding 50' of 1/2" water line in the middle. Imagine the pressure drop and reduced flow of two units in series, with a equivalent of 100' or more of piping. Check the manufactures, they are always installed in parallel, and commonly cascaded based on load with cables or panels that the manufacture requires.

The nicest thing about the Navien is multiple units are cascaded with a inexpensive cable between controls, and then the venting can be done in a common pipe.

The Navien A model you mentioned is the premium tankless with a on-board circulator included that allows external circulation or internal circulation to solve cold water sandwiches and hot water delays.

You just need to decide is 5GPM or so max enough, to meet your needs? Bear in mind that's 2 standard showers, how hard is it to start the wash after bathing? Remember its endless hot water but at a controlled flow rate depending on rise, BTU and number of tankless.
 
Last edited:

Zl700

DIY Senior Member
Messages
257
Reaction score
4
Points
18
Location
Western NY
One more thing
Navien states it allows 1/2" gas line because it allows inlet pressures as low as 3.5" WC. This allows for higher distribution piping pressure drops but does not allow the installer to undersize and undercut all the other appliances that need higher inlet pressures. On LP this would include proper tank size to allow needed BTU LP evaporation, regulators to carry full loads and piping of course
 

dtherrien

Licensed Building Contractor
Messages
15
Reaction score
0
Points
1
Location
Massachusetts
zl700...yes both models are condensing units. I dont think i would be drawing more than the 4.5-5 gpm.
I am going to replace the gas line with 3/4" from the tank into the house. I have a 250 gallon tank (@ 80% full) a regulator at the tank and one at the house.
With the current models available, is the Navien a better choice?
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
At the recent 5 year propane pricing in MA a bigger Stiebel Eltron or AirTap heat pump water heater would make more financial sense. (A GE Geospring might cut it if you're a showering rather than a tub-bathing family, and install a drainwater heat exchanger.) During the summer it would be lowering your cooling load and dehumidifying the basement, and during the winter it would cost no more than (and probably less than) running a condensing propane tankless. The only issue is capacity, and space. The installation is much easier and cheaper than a tankless, even if the hardware cost for an 80 gallon unit is more expensive.

If you're going with tankless despite my brilliant advice ( ;-) ) Rinnai is the worlds largest manufacturer of gas-burning appliances with a very good rep. Navien (Kyong Dong Boiler Company) makes some good stuff at attractive price/performance points, but the quality control and field support in the US isn't nearly that of Rinnai. If Navien, make sure to only use factory certified techs who is willing to support both the product & installation.

With expensive fuels like propane the payback on ~50% efficiency or higher drainwater heat exchangers is pretty quick for showering families,(that would be a 4" x 48" or a 3" x 60" or bigger.) It roughly doubles the apparent-capacity of tank HW heaters, and doubles the efficiency during simultateous drain + HW flows.

july17-p3.jpg
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Nice Post Dana.

Propane is a great backup fuel. If you like to waste energy, and can afford to use it as a primary fuel that is great.

I would try to use a electrical means of heating. Not a tankless water heater tho. And a propane unit will not work in a power outage.

Using a propane electric generator as a backup, to power essentials makes a bit of sense.


That is just me, in this day and age.
 
Last edited:

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
DonL: The residential retail rates for electricity in MA can range as high as 22 cents/kwh, nearly 2x the TX average. Other locations on municipal utilites can sometimes be as low as 12 cents. Exactly which utility he is on makes a difference. The delivered propane price/gallon history isn't too promising either, averaging over $3/gallon over the past 5 years.

A condensing propane tankless that scored in the high 90s on an EF test is only about 0.85 in real-world use (short-cycling losses eat up much of the condensing efficiency.) At 91,600 BTU/gallon at 0.85 effciency you're getting 77,860 BTU gallon into the water. tThat's 12.84 gallons/MMBU, so at a cost of $3/gallon you're paying ~$38.50/MMBTU for heating water.

A cheap EF 0.90 electric tank delivers 0.9 x 3412= 3071 BTU/ kwh into the water, which is 325 kwh/MMBTU. If he's paying the state average of 15 cents/kwh that's ($0.15 x 325=) $48.84/MMBTU for heating water- a tad-bit more expensive than condensing propane.

But with an EF 2.2 heat pump water heater the cost during non-heating season periods would be (0.9/2.2 x $48,84=) $20/MMBTU, or about half what it costs with condensing propane.

During the heating season the ~60% of the non-electric portion of the heat going into the water comes mostly from the heating system, at whatever efficiency & cost that is. Cooling off the basement a degree or two with the water heater also lowers the heat loss from the building slightly, so there are significant secondary factors making the model not-so-simple, but the annualized net cost will be much lower than heating the water with either electricity OR a propane tankless. It'll likely average between 65-75% of the cost of doing it with a condensing tankless.

If you then add a decent sized drainwater heat recovery heat exchanger the water heating costs come down by another 20-35%- depending a on what fraction of your total hot water use is from simultaneous flows like showers.

At recent average MA propane & electricity prices the Rinnai space heaters are substantially more expensive to heat with than using mini-split heat pumps too. Over the course of a heating season a pretty good mini-split delivers ~10,000 BTU/kwh in this climate (better than heat pump water heater efficiency). At 15 cents/kwh that's $15/MMBTU.

The Rinnai space heaters run in the low-80s for efficiency- figure about 76,000 BTU/gallon, or 13.16 gallons /MMBTU, which at $3/gallon costs $39.50.

Even heating with the world's crummiest third-world-imitation mini-split would cost less than half what it costs to heat with propane here. If electricity & propane were my primary options, I'd be heating with mini-splits (and I know people in central MA who do.) A decent mini-split typically pays for itself in about 3 heating seasons or less for most MA locations when displacing oil or propane.
 

dtherrien

Licensed Building Contractor
Messages
15
Reaction score
0
Points
1
Location
Massachusetts
Dana...Where can i find more info on the mini-splits that you are talking about?
Yes i am in central Ma. and electric and propane are high. I am paying about $4.50 gallon for propane....company says i am not using enough to get the heat rate. I am thinking about getting my own tank and get delivery from who ever has the best price.What is that setup in the picture above? I understand the drain water part...but what brand is that heater and does it heat both the domestic hot water and water for home heating?
 

Guy48065

Member
Messages
191
Reaction score
5
Points
18
Location
SE and north MI
Anybody,
Having just researched tankless condensing HWH myself I've been wondering why Rinnai stands alone in not offering any models that use PVC venting. Have I missed something bad about plastic vent vs. concentric steel?
 

Reach4

Well-Known Member
Messages
38,795
Reaction score
4,413
Points
113
Location
IL
Anybody,
Having just researched tankless condensing HWH myself I've been wondering why Rinnai stands alone in not offering any models that use PVC venting. Have I missed something bad about plastic vent vs. concentric steel?
I would think that concentric steel would have the advantage of pre-heating the incoming air from the exhaust heat. It would also leave one hole in the house instead of two.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
The metal flue can obviously handle higher temperatures in the exhaust. Doesn't mean that it may not be condensing at least some of the time, though. Metal is (from what I read) usually necessary when the average efficiency is below 90%.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Dana...Where can i find more info on the mini-splits that you are talking about?
Yes i am in central Ma. and electric and propane are high. I am paying about $4.50 gallon for propane....company says i am not using enough to get the heat rate. I am thinking about getting my own tank and get delivery from who ever has the best price.What is that setup in the picture above? I understand the drain water part...but what brand is that heater and does it heat both the domestic hot water and water for home heating?

There are literally dozens of mini-split contractors in central MA, some more competent than others. It's been my own m.o. to calculate the heating load myself, narrow down to 2-3 models that fill the bill, then solicit bids. I'm also pretty picky about telling them where/how to install the compressors. Since the tools & skill sets are mostly air-conditioning (they are heat pumps after all), many contractors don't consider aspects like snow-depth, snow drift or ice-dam/roof-avalanche fall very carefully (or at all), leaving the homeowners to be out there dig up the compressors after every storm (or worse.) Mitsubishi has the lions share of total numbers of contractors & support in our area, followed by Fujitsu, with the rest "in the statisitical noise". Contractors that have a lot of experience with Mitsubishi are Chaves in Hudson, Advanced Energy Conceptsin Fitchburg, and Meacham in Charleton, all of whom are on the "quality" end of installers, but it's still best to detail where/how to mount the outdoor unit.

I'm not sure who the better Fujitsu installers are in the neighborhood, but you can find some here. Daikin makes some of the better equipment (and are one of the bigger operators worldwide), but they don't have very many certified installers in central MA. If you stick with those three you'd be in pretty good shape from an equipment performance & reliability point of view.

In our climate it's not absolutely necessary to go with the "cold weather" series, units, but there are fewer maintenance/performance issues to worry about if you do. In the Mitsubishi lineup those would be the "Hyper Heating" sometimes called "H2i" series (MUZ- FExxNA). In Fujitsu it would Halcyon XLT-H series (AOU-xxRLS2-H). A typical "pretty-good" mini-split like those would have about 15,000 BTU/hr output at +5F per "ton" of rated cooling. (So a 12,000 BTU/hr = 1-ton unit is really 15,000 BTU/hr from a space heating perspective, in our climate.)

The layout of your house makes a difference in how many heads you'd need, and what size. Make a spreadsheet (Excel, etc) for calculating an I=B=R method heat load calculation on a room-by-room basis. You'll have to come up with U-factors (heat loss per square foot per degree) for your wall construction, windows, doors, attic, foundation (above grade only), etc. and the appropriate indoor/outdoor design temps. (Use the 99% outdoor design temp for your area if listed, or interpolate for the nearby listed locations. In Worcester the 99% design temp is +5F, and yes, it drops to -5F every few years, but it doesn't dwell at those temps long enough to really matter from a heating system point of view.) The basic formula for calculating the heat load is:

U-factor x area x temperature difference. So for each room you would have separate U-factors and areas for wall, window, ceiling to be calculated separately, then summed.

With a room-by-room heat load and a whole-house load I can steer you toward potential solutions.

Open common areas and adjacent rooms that open up directly onto it are usually candidates for running as one "zone", with a single head. A big doored-off room with lots of windows down at the end of the hall not so much. If a room doesn't have a heat load of at least 6-7000BTU/hr it's not a candidate for having it's own head, but there are "mini-duct" cassettes where you can split output between two nearby rooms with very short duct runs. Like space heaters and wood-stoves it's point-source heating, but it's not bad. Since they modulate rather than cycle on/off you get very stable room temps, and most of the time they're quieter than your refrigerator.

Since you have a heating fuel history on the place you can get a pretty good handle on the whole-house load by using propane-use against heating degree days. To do that we would need a zip code (to find a degreedays.net weatherstation nearest you), the # of gallons of a late-winter fill-up and the exact dates between that fill-up and the prior one, and the nameplate efficiency on your Rinnai heaters.

The picture of the drainwater heat exchanger (a 4" x 48" PowerPipe) is clipped from a Natural Resources Canada website. It looks like a Rinnai RL75i or similar, probably not set up for space heating, only hot water (since it would violate the Rinnai warranty to use it as a hydronic boiler.)
 

Guy48065

Member
Messages
191
Reaction score
5
Points
18
Location
SE and north MI
hmmm...is combustion air temperature factored into efficiency? Concentric is pricey--if it won't pay for itself I don't see any reason to choose it. Still wonder why Rinnai does...

I may end up with 40 feet of vent so cost is a factor. The price difference between concentric & PVC can cover the extra cost of a condensing unit.

Edit--oops I didn't notice we're on page 2. My reply is to post 15.
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
The more heat the unit extracts from the burner (the less goes out the flue), the more efficient it is...the more efficient units can use plastic pipes solely because they extract more heat and the flue temps are lower.
 

dtherrien

Licensed Building Contractor
Messages
15
Reaction score
0
Points
1
Location
Massachusetts
I will have to do some more research on the mini-split systems....seems more complicated than i anticipated.
I live a couple of towns away from Charleton so might contact Meacham. I will also ask two other plumbing/heating subs that i use.
One thing about my house is....there is no type of central heating system. I bought this house in 1996 and it had only a propane fired heater upstairs and downstairs. I replaced them with the Rinnia heaters. I dont know if that works for me or against me...but have the option to do almost anything. Kinda looking for something that i would be able to do myself.
 