    Default carrier question for wall hung toilet

    I'm remodeling the basement powder room to add a shower. I figured I would replace the old blue wall hung toilet with a new one, either the AS or the Gerber mentioned here (still undecided which). I wish there were nicer looking wall hung with exposed tanks (just don't trust a tank I can't look into, that's why the high tank toilet in the main floor powder is getting replaced too.) Use the old carrier, attach new toilet, no problem, right? Well the plumber I had out here over the weekend says the old toilet is not vented, so the old cast iron on the other side of the wall will have to have a chunk cut out, and tied in to a vent (luckily all is above the concrete floor in the utility room). He said the new plumbing put in will be pvc, which will not connect to the old carrier, so I won't be able to reuse the carrier. If this is so, then what carrier do I get for either of the two toilets I mentioned? I've looked on the spec sheets, and neither one says anything about it. Or is there a way to use the old cast iron connection with the carrier with the pvc he puts in?

    Thanks for any input.

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    A wall hung toilet can be vented within six feet.
    How is he sure that the vent isn't downline of the fixture and in a different wall?

    Do you have a picture of your current setup?
    Going from cast to PVC isn't a big deal.

  3. #3
    DIY Junior Member diymomma's Avatar
    Join Date
    Apr 2012
    Location
    Waterloo Ontario
    Posts
    8

    Default

    The wall is completely open on the other side- right next to the furnace, etc. for all to see. He said the powder room sink is vented though, so plans are to tie in to that vent stack I think. My contractor and plumber seemed to agree that the carrier needed to be changed, but I still didn't understand why. I'll get some photos in the morning and see if I can post them. I think part of it is that both seem dubious of just exchanging the toilet. They thought they don't make them like that anymore, the carrier bolts would be in the wrong place, etc. I told them what I read here, and their response was "Terry who?" Seriously now, have they never done any kind of toilet research online?
    Part of me says "just find a new plumber" and part of me says "give up on the wall hung, get a floor mount back outlet toilet" (like the Maier on Signature Hardware) maybe they won't be as afraid of that.

    I'll try to get some pics of the situation.
    thanks

  4. #4
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    I'm not surprised they don't know me, but working with wall hung toilets is a pretty simple thing. They should know that if it's a four bolt carrier, that any four bolt wall hung will work. We replace them all the time.
    It sounds like they either want a bigger job, or they are just a little clueless.
    My mother still has an American Standard Glenwall in her master from 1962. Her main bathroom has a newer pressure assist Glenwall.
    We've been selling one a month, and at the moment I have the Gerber Maxwell Wall Hung ready to go in inventory.
    http://www.terrylove.com/forums/show...rkville-review





    You may have something like this.



    Mifab Residential Carrier
    Last edited by Terry; 10-07-2013 at 03:46 PM.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    If they used a carrier "frame" like Terry shows, then there could be any kind of fitting in the wall behind it. But, if they used a carrier with integral fitting, which most plumbers would, I have NEVER seen one which did not have provision for a vent, even if the installer did not use it for some reason. How about a picture of what is in the wall. The new toilet will fit the carrier EXACTLY, and if they do not know that, then they may NOT be "plumbers".
    Licensed residential and commercial plumber

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    The new toilet will fit the carrier EXACTLY, and if they do not know that, then they may NOT be "plumbers".
    I think hj may have a point there. Have you checked to see if he is one?

  7. #7
    DIY Junior Member diymomma's Avatar
    Join Date
    Apr 2012
    Location
    Waterloo Ontario
    Posts
    8

    Default

    Quote Originally Posted by Terry View Post
    [COLOR=#333333]

    I think hj may have a point there. Have you checked to see if he is one?
    Just took my contractors word for it. He re-routed the washer drain for me, and seemed to know what he was doing there (and my washer now drains properly). I'm not sure if you can make anything out from the photos I took, but I'll post (if I can figure out how) them just in case. I'm thinking I should get a different plumber in for an estimate before I get any more work done.
    Name:  P1010047.jpg
Views: 161
Size:  43.3 KB

    Name:  P1010040.jpg
Views: 174
Size:  26.4 KB

    Name:  P1010041.jpg
Views: 167
Size:  45.2 KB
    Last edited by Terry; 10-08-2013 at 12:10 PM.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    They did use a "face plate" style carrier, but the vent is the pipe connected to the line which goes vertically, although it would be nice to see what is behind that "blue" object. I might also be concerned, since they do not seem to know much about wall mount toilets, that they may NOT install it correctly with the proper "backup nuts and washers" behind the bowl. There is more to it than just putting the toilet over the bolts and screwing the nuts on.
    Last edited by hj; 10-08-2013 at 06:32 AM.
    Licensed residential and commercial plumber

  9. #9
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    the vent is the pipe connected to the line which goes vertically
    To hj and I, that's the toilet vent.
    It looks like someone recently added a PVC wye fitting to that, perhaps someone is now using the "vent" for some other fixture now?
    Previous to that, it was a Santee behind the toilet acting as a vent. The Santee on it's back is not a waste fitting there, but had been used for vents in the past.

    So looking at that again, is he using the toilet vent for a washer drain?
    Last edited by Terry; 10-08-2013 at 12:07 PM.

  10. #10
    DIY Junior Member diymomma's Avatar
    Join Date
    Apr 2012
    Location
    Waterloo Ontario
    Posts
    8

    Default

    So looking at that again, is he using the toilet vent for a washer drain?
    Yes, he is using that for the washer drain. I think the washer was draining into it already, but in a very round about and uphill way (the washer drained into a small pipe only a foot off the floor, went several feet at a minimal pitch, through the wall, around the corner where all the other plumbing is, up hill for about 6 feet while rising abut 4 feet, then that emptied into a pipe that came back towards what you are calling the toilet vent. I think the sink drained into it too. My clothes were always wet dripping going into the dryer. I wish I had taken some before photos, I can't remember exactly how everything was tied in. The plan is for them to come back and get a pump in the ground for the new shower, rough everything in, and tie in to a vent that he has capped right now (you might be able to see it near the top right in the new photos. Sure better be a vent. They had me run water through all the plumbing upstairs, and nothing came out the pipe, so they said it is a vent they can use. I think maybe the old sink was tied into it. The blue thing is my hot water.

    It is a plumber my contractor uses. He is fairly young, and I don't think he had ever seen a wall hung with exposed tank like that before. I have a different plumber coming out to remove a 1980's repro high tank and rough in for a Toto Guinevere in the first floor powder room next week. Maybe I should have him take a look at my basement situation before allowing the other guys to do any more work? He already hooked up a Toto for me upstairs, and seemed pretty knowledgeable.

    Name:  P1010052.jpg
Views: 310
Size:  36.1 KB

    photo 1- far side of water tank.

    Name:  P1010054.jpg
Views: 223
Size:  36.7 KB

    Photo 2- washer drain from left, into the waste pipe, pipe going to right goes behind the water tank.

    Name:  P1010055.jpg
Views: 165
Size:  28.8 KB

    Photo 3-behind the water tank.

    Name:  P1010056.jpg
Views: 159
Size:  45.1 KB

    photo 4- vent? they plan on using.
    Last edited by Terry; 10-08-2013 at 02:22 PM.

  11. #11
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default



    It looks like the lav to the right was wet venting the toilet, and then the vent continued up to the vent 90 near the ceiling.
    The lav has been cut out, and now the washer is draining into the toilet vent. No plumbing code allows that, but that's what someone did.



    This standpipe with p-trap is not vented. Maybe not a big deal if that is just for furnace condensation.
    Last edited by Terry; 10-08-2013 at 02:27 PM.

  12. #12
    DIY Junior Member diymomma's Avatar
    Join Date
    Apr 2012
    Location
    Waterloo Ontario
    Posts
    8

    Default

    The plumber went ahead and removed the lav in anticipation of the remodel since neither sink or toilet was functional right now. When they put a lav back in during the remodel, and vent back up, will that be venting the toilet again? And where should the washer be draining into? When they re-routed things, it was a stop-gap measure to get the washer draining better (I didn't want to wait for 2 months until my contractor can start the full remodel, I was afraid it might kill my washer in the mean time.) The toilet has been disconnected from the water supply already.

    The standpipe is just for furnace condensation now.

    I'm glad a permit is going to be pulled for the project, so I know it has to pass inspection at the end.

  13. #13
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    quote; went several feet at a minimal pitch, through the wall, around the corner where all the other plumbing is, up hill for about 6 feet while rising abut 4 feet, then that emptied into a pipe that came back towards what you are calling the toilet vent.

    Unless they have discovered antigravity, or new laws of physics, water does NOT run uphill for 6 feet and the rise another 4 feet before connecting to a drain line.
    Licensed residential and commercial plumber

  14. #14
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    The only way that might work is if the WM hose was sealed to the drain, and then, when the pump turned off, a bunch of that water would run back down into the WM...neither situation is 'right'.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  15. #15
    DIY Junior Member diymomma's Avatar
    Join Date
    Apr 2012
    Location
    Waterloo Ontario
    Posts
    8

    Default

    Yeah, well, the hose was pushed into the drain -a somewhat snug fit atleast- and I can say that the water running back into the WM was not the cleanest. Ugh.
    What I meant was a rise of 4 feet over a run of 6 feet. Certainly not ideal. That is why I decided to have my GC get the washer and dryer moved over in anticipation of the remodel and get the WM drain sorted out right away. The remodel is supposed to happen in a month, but I didn't see any point in waiting to get my WM draining. I don't want my WM dying on me in the mean time.

Similar Threads

  1. Can one toilet carrier hold back to back wall hung toilets
    By Chaosherder in forum Toilet Forum discussions
    Replies: 3
    Last Post: 06-20-2012, 11:17 AM
  2. basement drain question for adding wall hung toilet
    By Bull in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 12-10-2011, 06:45 AM
  3. Need Wall Hung In-wall-carrier for Toto
    By Breezer in forum Toilet Forum discussions
    Replies: 1
    Last Post: 08-25-2009, 01:55 PM
  4. GroheDal in-wall toilet carrier install problems
    By wharf in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 05-10-2007, 11:21 AM
  5. recommendation for wall hung "closet carrier"?
    By Royboy in forum Toilet Forum discussions
    Replies: 6
    Last Post: 05-29-2006, 07:13 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •