    Default Got a question about using a 3x3x2 wye horizontally

    Hello all,

    I am certainly no plummer just a homeowner trying to tie in his sewage ejector pump to his main drain line so forgive me if I get some of the terminology wrong.

    I am coming up one wall and across the ceiling with the 2" pipe. I have the right grade and am tying it into the main 3" drain line horizontally with a 45 wye with a 60 degree elbow.

    The inspector came out today and said I needed to tilt the wye so the 3" pipe was not "cut in half" from the 2" opening of the wye so I had to rotate so the opening of the 2" portion was above the halfway point of the 3" pipe.

    Does this make sense? all the other 3x3x3 wyes that are in my house that I can see are all lying lat on their side(is that the right terminology?). Is it a different story when dropping size on the horizontal plane? I thought i had this done up pretty good.

    Here is a picture of the entire run.
    Name:  20131003_231848-.jpg
Views: 152
Size:  70.0 KB

    Here is one from directly below
    Name:  20131003_232410.jpg
Views: 146
Size:  37.2 KB

    And here is one from eye level
    Name:  20131003_231658.jpg
Views: 159
Size:  51.0 KB
    Attached Images Attached Images  

  2. #2
    DIY Junior Member Cajunhiker's Avatar
    Join Date
    Oct 2013
    Location
    Lafayette, LA
    Posts
    2

    Default

    You gotta turn that wye up at least 15 degrees so the waste will dump into the 3 inch pipe. As is, a blockage in the 3" pipe will back up into the 2" pipe.

  3. #3
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    Being that you are tying in a sewage ejector, that changes things. In Seattle, they like those to go into 4" waste lines, not 3"

    Go ahead an tilt the 3x2 wye so that the pumped 2" enters higher than the flow line of the 3".
    Don't feel bad, you've done well. Now you're gonna do weller.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    quote; In Seattle, they like those to go into 4" waste lines, not 3"

    What do you do when the entire system connects to a 3" sewer?

    You had an "anally retentive" inspector. There is no reason an "active drain" such as a pump discharge would have to enter the main line at a higher elevation. (That is a requirement for a vent so it does not get "backup" during normal usage.) It would be no different than if it were the drain from a shower or tub which CAN enter on the same plane, assuming you have proper pitch on the drain line. IF he had any issues with the installation, he should have rejected those two Mission couplings which are not approved for where, and how, you installed them.
    Last edited by hj; 10-04-2013 at 07:27 AM.
    Licensed residential and commercial plumber

  5. #5
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    What do you do when the entire system connects to a 3" sewer?
    Seattle doesn't have 3" sewers.

    But like the above problem, The wye should have been okay where it was,
    Dumping into a 3" line should have been fine in Seattle,
    The rubber Ferncos are "not" good anywhere that I know of except in the ground where they can be supported.
    But then, that's inspectors soemtimes.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    Almost ALL houses in Arizona, unless they have 4 or more toilets HAVE a 3" main line all the way to the city connection at the property line.
    Licensed residential and commercial plumber

  7. #7
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    Almost ALL houses in Arizona, unless they have 4 or more toilets HAVE a 3" main line all the way to the city connection at the property line.
    Here in Washington, we can stub out 3" if we have three toilets or less. The 4" sewer starts within 24" of the outside foundation.
    I never saw any reason why the 2" output from a sewage ejector couldn't dump into a 3" line though. I'm not an inspector though. I've also put them in 3" lines on the Eastside. It's really only the very old Seattle homes that were run with 4" cast that even have that option.

  8. #8
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    We dump them into 3" lines all the time. Very few houses here have a 4" main. Only the pipe through the foundation is required to be 4"
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    quote; Only the pipe through the foundation is required to be 4"

    We do not even have that restriction. Ours go 3" all the way to the city's connection.
    Licensed residential and commercial plumber

  10. #10
    DIY Junior Member DemoDick's Avatar
    Join Date
    Oct 2013
    Location
    Atlanta
    Posts
    7

    Default

    Quote Originally Posted by hj View Post
    IF he had any issues with the installation, he should have rejected those two Mission couplings which are not approved for where, and how, you installed them.


    I am assuming if they are not allowed there is a reason. What is that reason and what should I do there instead?

    Thanks all for the feedback.

  11. #11
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default



    We use a shielded coupling there to prevent the pipes from shifting. When you come back in a few years, those rubber ferncos will have sagged quite a bit.
    They're just made of rubber. I've seen some that have become very deformed.

  12. #12
    DIY Junior Member DemoDick's Avatar
    Join Date
    Oct 2013
    Location
    Atlanta
    Posts
    7

    Default

    Quote Originally Posted by Terry View Post
    [/IMG]

    We use a shielded coupling there to prevent the pipes from shifting. When you come back in a few years, those rubber ferncos will have sagged quite a bit.
    They're just made of rubber. I've seen some that have become very deformed.
    Thanks man!

    I have it supported 3 times over the sub 4 foot span but that said.

    The box store has the "Fernco 3 in. No-Hub Cast Iron x 3 in. Sch 40 PVC, Steel and Extra Heavy Cast Iron Neoprene Rubber Shielded Coupling" in stock. For 8 bucks each I will go back and switch them out. Not going to be here long term but I have always hated the thought that someone that buys my house someday would be sitting in a puddle of you know what cursing my name as his wife screams that she cannot give their 6 month old kid a bath while he fixes it.

  13. #13
    DIY Junior Member DemoDick's Avatar
    Join Date
    Oct 2013
    Location
    Atlanta
    Posts
    7

    Default

    All that said I have a 4" drop over a 10' span so I have the pitch plus some to spare. My entire house is only 3" main drain line until it gets to the foundation then it is 4" newer house built in 08.

    Tilting that wye up is going to be no fun as I am going to have to play geometry man but I am thinking I am not going to win an argument whit an inspector as I have stated I am not a licensed plummer. Heck I should probably be committed.

  14. #14
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    Heck I should probably be committed.
    Welcome to the plumbing fraternity!
    Being committed is part of the process.
    Dooh!

  15. #15
    DIY Junior Member DemoDick's Avatar
    Join Date
    Oct 2013
    Location
    Atlanta
    Posts
    7

    Default

    OK so the way it is laid out I think it is just going to be better for me to run things a bit differently. I failed to mention this earlier but this work was actually first done by a licensed plummer. After some issues with him showing up when he said he would and then cracking my tub I decided to take it on myself and when I did I found there was no trap under the tub. He was recommended by a friend and was not even the lowest bidder so I thought he would be the guy. Guess not.....anyway....

    If I am going to go run the same vertical on the left hand of the room in the picture above but I am going to run some hole in the rafters and run it through then rather than under them to get some extra height so I can come straight down into the top of the 3x3x2 wye.

    If I do so is it best to use long sweep 90s to make the transitions from vertical to horizontal? Any advantage over a normal 90?

    Again any advantage to a long sweep 90 if I am changing horizontal direction(making right and left turns)? TO me they look like they would flow better but II am normally wrong about stuff.

    Is it OK to put the 3x3x2 on its back with a 45 street elbow to make that 90? My inspector said it did not have to be a 90 degree direction change but is that better?



    p.s. I have all the specs on the engineered beams and know where I can and cannot cut holes and I am good there and I will then have the min 1/4 per foot pitch all the way into the wye.


    Thanks again guys!

Similar Threads

  1. Venting a WC waste line horizontally II
    By Jhall in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 09-10-2009, 06:42 AM
  2. Venting a WC waste line horizontally
    By Jhall in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 08-27-2009, 01:07 PM
  3. Combining 3x3x2 wye + 1/8 turn
    By summilux in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 05-21-2008, 10:07 AM
  4. 3x3x2 wye and 90 ell
    By frank19991999 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 02-17-2006, 08:18 PM
  5. How far can a main vent pipe run horizontally
    By snuffysmith1978 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 03-23-2005, 05:28 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •