    Default boiler pressure at 30 PSI

    Our boiler valve goes over 30 PSI - happened with our old one so we had it replaced. Have this one not even 3 years and doing the same thing. Any idea why the same thing would be happening again? Could the tank be bad in less than 3 years?

  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,935

    Default

    Bad or unpressurized expansion tank
    Auto fill valve improperly set or bad
    High limit set too high
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    There are several possibilities, but none that we could diagnose without doing our own tests on the boiler.
    Licensed residential and commercial plumber

  4. #4
    TROJAN WORLDWIDE SALES RP MACPLUMB 777's Avatar
    Join Date
    Aug 2007
    Location
    Houston, Texas, United States
    Posts
    631
    Blog Entries
    1

    Default

    Go to this website for answers http://www.heatinghelp.com/

    MACPLUMB 777

    E-MAIL
    JERRYMAC@TROJANWORLDWIDE.COM


    35 YEAR MASTER PLUMBER, HEATING, ELECTRIC, DRAINS, FIRE SPRINKLERS, WATER HEATER
    AND BOILERS SINCE JAN, 1989

    281-706-1631 7 DYS A WEEK SALES AND TECH. SUPPORT
    Trojan Worldwide Web Site


     



  5. #5
    DIY Junior Member suelue's Avatar
    Join Date
    Sep 2013
    Location
    mukwonago, wisconsin
    Posts
    2

    Default

    This can be the problem even though it is all new?

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    If the expansion tank isn't sized properly or precharged to the needed level, it could allow the pressure to rise more than desired. But, it's more likely that the autofill valve is potentially leaking or incorrectly set. FWIW, an autofill valve can mask system problems, and you may want to just readjust the pressure to design, then (hopefully you have one) shut the water off to the autofill valve. If you have a leak, having it open can mask that to you. Constantly adding fresh water to a boiler is problematic, and you really want to know about it. IF you don't have any leaks, shutting the autofill valve will have no effect on the system operation. If you do have a leak, instead of creeping up, it will gradually drop as water leaks out, eventually tripping the boiler's low-limit safety device interlock.

    If it's something else, it's still a good idea to shut the autofill valve and you'd have eliminated one of the possibilities.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. Boiler Pressure
    By Engine1 in forum Boiler Forum
    Replies: 14
    Last Post: 02-19-2012, 11:12 AM
  2. Boiler Pressure
    By tombstone in forum Boiler Forum
    Replies: 1
    Last Post: 12-12-2011, 08:47 AM
  3. Boiler pressure
    By my88r in forum Boiler Forum
    Replies: 3
    Last Post: 04-18-2011, 07:37 AM
  4. boiler pressure
    By frank in ohio in forum Boiler Forum
    Replies: 5
    Last Post: 11-24-2009, 09:57 PM
  5. Boiler pressure
    By swcooper in forum HVAC Heating & Cooling
    Replies: 6
    Last Post: 03-31-2007, 10:29 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •