    Default Natural gas line routing

    I have a natural gas line running in the attic to feed my furnace at the other end of the house. At the furnace, it drops through the ceiling down the inside of the furnace closet to the furnace valve.
    I want to run a "T" off of that line in the attic down the inside of a wall so that I can install a gas stove top where an electric one is.

    Is this legal? I know that I can't have a union in the gas line and it has to be black pipe. Is this legal? Tips and or ideas? Thanks!

  2. #2
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    As long as the line is large enough to serve both appliances.
    John

  3. #3
    DIY Member ankhseeker's Avatar
    Join Date
    Oct 2013
    Location
    California
    Posts
    52

    Default

    So that means that there is a BTU or CFM specification for the pipe. I will also have to get the BTU specs for the furnace and stove and see if they are together less than the pipe spec? I am pretty sure that the supply is 3/4".

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,607

    Default gas

    You don't need a 1" line to feed gas to a range.
    Licensed residential and commercial plumber

  5. #5
    DIY Senior Member Hammerlane's Avatar
    Join Date
    Oct 2011
    Location
    Ohio
    Posts
    252

    Default

    Quote Originally Posted by ankhseeker View Post
    Tips and or ideas? Thanks!
    Make sure your line is sized for the furnace and stove to operate at the same time. Make sure there are no leaks.

    Here is a chart from the National Fuel Gas Code which shows the capacity of certain lengths and sizes of pipe.
    Attached Images Attached Images  

  6. #6
    DIY Senior Member Hammerlane's Avatar
    Join Date
    Oct 2011
    Location
    Ohio
    Posts
    252

    Default

    Also remember that each fitting like a tee, elbow or a 45 has an equivalent length of straight pipe that has to be taken into consideration when calculating your developed length of pipe.

    You should establish what the developed pipe length is. By that I mean the actual length may only be 40 feet but you have to add in any 90's or Tee's as its equivalent length of pipe. A 1/2" 90 is equal to 1.55 feet and a 1/2" Tee is equal to 3.10 feet.

    So if you had say 6-90's and 1- Tee, that would be an additional 12 feet of pipe to consider for calculations

    Here is part of a table. Notice how a 1/2" tee is equivalent to 3.10 feet of straight pipe.
    Attached Images Attached Images  
    Last edited by Hammerlane; 12-23-2013 at 08:40 AM.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,607

    Default

    quote; Here is a chart from the National Fuel Gas Code which shows the capacity of certain lengths and sizes of pipe.

    However, you CANNOT say, "Well, I have 30' of 1", so it has a capacity of 284 cfm, 20' of 3/4 with 188 cfm, and 10' of 1/2" which can handle 131 cfm. You have to add ALL the dimensions, including fitting equivalences, then use THAT row, (i.e., 60' for this example),a capactiy of 195 for EACH pipe size. When you do that 1" has a capacity of 195 cfm, 3/4" carries 104 cfm, and 1/2" only 50 cfm.
    Licensed residential and commercial plumber

Similar Threads

  1. New drain line routing in half bath?
    By pghsebring in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 21
    Last Post: 03-18-2011, 05:43 PM
  2. Confused on Drain Line Routing
    By wallskev in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 08-30-2009, 01:33 PM
  3. Routing pressure relief valve line
    By dabiz7 in forum Water Heater Forum, Tanks
    Replies: 5
    Last Post: 03-15-2009, 06:15 PM
  4. Re-routing a drain vent line
    By Philip in Connecticut in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 01-14-2009, 10:21 PM
  5. Re-routing a waste stack branch line
    By rrzepka in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 12-11-2004, 08:14 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •