    Question heating upstairs zone works, downstairs doesn't - New piping

    Folks,

    I just fired up my TT-110. The upstairs zone works fine. The downstairs (the one to the left) doesn't. The pipe above the valve hardly gets hot. Even when the circulator pump is on and the the second zone is closed. The Diff Bypass valve is set properly and water is not flowing back thru it. Something isn't right. I check and the zone valve is working. I even tried it manually. The flow goes up.

    I'm thinking the down stairs tee may be too close to the elbow to the left. I've see the rule of 12d. I can fix this, but do you think that's the problem. I don't want to do that work if it's not the problem. The zone valves are 4d apart.

    Any input would be greatly appreciated.

    Sorry about the photo being sideways. I tried to fix it with no luck. Up is to the left
    Attached Images Attached Images  

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    It's more common to have air in the higher level, but it doesn't take much to block flow through a loop...first thing I'd do is try to purge air from the system again.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Member philtrap's Avatar
    Join Date
    Jun 2013
    Location
    Long Island, NY
    Posts
    66

    Default

    Thanks jadnashua!! I re-purged again and one large burp and now all is fine now.

    Quote Originally Posted by jadnashua View Post
    It's more common to have air in the higher level, but it doesn't take much to block flow through a loop...first thing I'd do is try to purge air from the system again.

Similar Threads

  1. 2 zone system-no heat upstairs-Boiler doesn't fire when that zone asks for heat
    By MrBostn in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 14
    Last Post: 10-13-2012, 08:33 AM
  2. Converting a manual switch heating zone to a thermostat heating zone
    By breilly629 in forum HVAC Heating & Cooling
    Replies: 4
    Last Post: 03-12-2010, 01:04 PM
  3. Toto ADA/upstairs downstairs questions
    By notmyfield in forum Toilet Forum discussions
    Replies: 6
    Last Post: 08-26-2009, 12:00 PM
  4. Smell after upstairs shower in Downstairs bathroom????
    By harheath in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 11-28-2005, 06:34 PM
  5. Upstairs don't flush, downstairs does
    By catlind in forum Toilet Forum discussions
    Replies: 3
    Last Post: 02-24-2005, 08:40 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •