    Default Powerflex direct vent wont stay lit

    Hi all, I have a 4 year old powerflex direct vent water heater that wont stay lit. All the lights blink on the gas control valve and there is a continuous clicking from it. The only way to get it to light is to blow in the black tube on the blower connected to the diaphragm and then I hear the diaphragm click and it lights. I thought the diaphragm was the problem so I changed that. I need help please.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    By blowing through the black tube, you proved that the diaphragm switch was GOOD, not bad. It's doing its job as a safety interlock. There's a problem either with the fan, or exhaust venting - it's not moving the air properly, and creating enough pressure/vacuum to close the switch to keep it running. Could be a bird's nest, mouse, a separation in the exhaust venting, inoperative fan, crack in the tubing, etc.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member cannedham1's Avatar
    Join Date
    Aug 2013
    Location
    NY
    Posts
    2

    Default

    Thank you jadnashua. I read the manual and it says that the error code for all the lights being lit it is the gas control valve. Im going to make sure there isnt anything obstructing the vent.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    The gas valve and the diaphragm switch are related, but not the same. That switch is in the interlock, safety circuit, and must be closed for things to work. Now, if it does close, and the gas valve doesn't open or the igniter fails to operate, that's a different issue. Could also be a flame sensor.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. nwater pump wont stay on
    By chasidyndavid in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 05-06-2013, 09:53 AM
  2. Empire Heater Propane RH65, pilot wont stay lit
    By Its.me.again in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 01-03-2013, 02:18 PM
  3. Replies: 2
    Last Post: 07-10-2012, 04:19 AM
  4. Propane furnace pilot wont stay lit
    By davewest in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 11-19-2009, 08:34 PM
  5. pilot light wont stay light on furnace
    By possum in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 10-07-2008, 12:48 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •