Outlet Connections

Users who are viewing this thread

ActionDave

Electrician
Messages
418
Reaction score
9
Points
18
Location
Colorado
The code DEMANDS that a three way switch be fitted at the top and bottom of a stairway in a house, and that it control a light that will illuminate the stairs sufficiently that most people will be able to get up and down those stairs safely. And breakers ain't got not'in to do with it.
The code only demands that there be a switch to control a light at each level, one at the top and one at the bottom each controlled by a SP switch would meet the requirement.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Ah. Crazy me, I was speaking of residential requirements, and not commercial or industrial. Indeed it is permissible to shut off a "branch circuit" with only the breaker and no other device in commercial and industrial applications. I am FAIRLY confident that the OP was writing of a residential application, yes?
210.70 Lighting Outlets Required.
Lighting outlets shall be installed where specified in 210.70(A), (B), and (C).
(A) Dwelling Units. In dwelling units, lighting outlets shall be installed in accordance with 210.70(A)(1), (A)(2), and (A)(3).
(1) Habitable Rooms. At least one wall switch–controlled lighting outlet shall be installed in every habitable room and bathroom.
Exception No. 1: In other than kitchens and bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.
Exception No. 2: Lighting outlets shall be permitted to be controlled by occupancy sensors that are (1) in addition to wall switches or (2) located at a customary wall switch location and equipped with a manual override that will allow the sensor to function as a wall switch.
So where does it say it must be beside the door?


As for "Planning departments and inspectors could care less where the switch is located all they are interested in is compliance." I can only say we know different inspectors. If there are no switches at the entrance for that bedroom you described, I can only say woopdie do. You out-smarted the local authorities.
I am not sure about the inspectors that you know but here is a couple of links that will give you some idea of the inspectors I know. The first link is to my work, it is the classes that I teach.
http://www.randolph.edu/continuinged/programs/building_trades/electrical.php
This one is to how I spend my free time
http://www.nciaei.org/
Check out officers and committees especially the education committee. I am no dummy when it comes to the NEC. No it is not a matter of out smarting any inspector but instead it is a matter of knowing what I am talking about.

The code DEMANDS that a three way switch be fitted at the top and bottom of a stairway in a house, and that it control a light that will illuminate the stairs sufficiently that most people will be able to get up and down those stairs safely. And breakers ain't got not'in to do with it.
Once again this is a simple case of knowing the code and not thinking one knows something they want to know. The code does not demand a switch at the top and bottom of a stairwell, read the exception to this section.
(2) Additional Locations. Additional lighting outlets shall be installed in accordance with (A)(2)(a), (A)(2)(b), and (A)(2)(c).
(a) At least one wall switch–controlled lighting outlet shall be installed in hallways, stairways, attached garages, and detached garages with electric power.
(b) For dwelling units, attached garages, and detached garages with electric power, at least one wall switch–controlled lighting outlet shall be installed to provide illumination on the exterior side of outdoor entrances or exits with grade level access. A vehicle door in a garage shall not be considered as an outdoor entrance or exit.
(c) Where one or more lighting outlet(s) are installed for interior stairways, there shall be a wall switch at each floor level, and landing level that includes an entryway, to control the lighting outlet(s) where the stairway between floor levels has six risers or more.

Exception to (A)(2)(a), (A)(2)(b), and (A)(2)(c): In hallways, in stairways, and at outdoor entrances, remote, central, or automatic control of lighting shall be permitted.
 
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
JW.

This is a pointless debate.

I wish you luck installing the light switch, which you acknowledge is REQUIRED (and breakers do not serve the requirement, so I have no clue as to why you brought it up earlier), all the way across the room from the entrance.

What is the point of this pedantic posturing?

So what if the code, when read with a fine tooth comb, permits you to do so? It is STILL the wrong way to do a thing.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
240.83 (D) Used as Switches. Circuit breakers used as switches in 120-volt and 277-volt fluorescent lighting circuits shall be listed and shall be marked SWD or HID. Circuit breakers used as switches in high-intensity discharge lighting circuits shall be listed and shall be marked as HID.

404.11 Circuit Breakers as Switches.
A hand-operable circuit breaker equipped with a lever or handle, or a power-operated circuit breaker capable of being opened by hand in the event of a power failure, shall be permitted to serve as a switch if it has the required number of poles.

What we think of as being a bad design in no way constitutes a code violation. If you feel that the switch should be beside the door then by all means put the switch there but should you ever enter an old house you might find the switch at the fixture and a string as the means of turning on and off the light. What you won’t be able to find is a code requirement mandating that the switch go beside the door.

90.1 (C) Intention. This Code is not intended as a design specification or an instruction manual for untrained persons.

I have on several occasions installed switches outside the room where the light was located. Ever seen a room addition on a mobile home? The switch that was for the outside door is now the switch for that room, yes? Ever done an all glass sunroom? Where did you put the switch?

To say a switch anywhere other than beside the door when entering the room is wrong is to say that one has never seen some of those items outlined above. No it isn’t wrong to put a switch anywhere one wants to put the switch other than beside the door.

When teaching or even answering post such as this one giving the correct answer is neither pedantic nor posturing, but, trying to sell someone that your idea is the only correct idea is. I always back my comments with verbiage found in the codes not from a standard of practice.

Edited to add

On a side note I am not trying to make you look bad but just trying to clear up the comment you made that the switch MUST be located beside the door.
Code requires that each room have a light or outlet that can be controlled from the door as a person enters....
 
Last edited:
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
Regarding switches outside the door of the room served: I did just that for my master bath, as putting the switch on the other side, classically on the strike side of the door, put it over the tub, and I don't like that from a shock hazard point.

The switch is just at the entrance to the bath. That is the point. The light is not controlled by a circuit breaker out on the side of the house, either.

Try this:

"it would be more correct to say is that it is well established custom to do so, but the fact is that code is less than absolute on the point" and then if you must, cite the code.

And yes, I know that in the dark ages rooms might have been lit by sconces with switches on the sconces and not at the door.

And the room might only have one receptacle. I did a walk-thru just today on an 1928 house that is like that.

Is that current practice?
 
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
Regarding switches outside the door of the room served: I did just that for my master bath, as putting the switch on the other side, classically on the strike side of the door, put it over the tub, and I don't like that from a shock hazard point.

The switch is just at the entrance to the bath. That is the point. The light is not controlled by a circuit breaker out on the side of the house, either.

Try this:

"it would be more correct to say is that it is well established custom to do so, but the fact is that code is less than absolute on the point" and then if you must, cite the code.

And yes, I know that in the dark ages rooms might have been lit by sconces with switches on the sconces and not at the door.

And the room might only have one receptacle. I did a walk-thru just today on an 1928 house that is like that.

Is that current practice?
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Even today as we nestle in bed we reach up and turn out the lamp beside our bed. Old habits are hard to break.
I always tell myself that I am turning off the engine to rest for an hour or so before the bathroom starts calling my name.

A Hillbilly uses a pull chain with two eye hooks just above each door or the bed with a string for a three way. My first home had a set of three ways with a four way in the master bedroom but by the time we sold that place I had figured out that the key of the lamp was used more than either of the switches. Only time the switch was used was while cleaning or making the bed and the switches beside the bed was hardly ever used.

Another little trick us hill boys are famous for is the three wire circuit to an our building we keep a freezer for the deer meat and have the light three way from house to building.
Once the black and white wire is connected to the receptacle in the building so the receptacle stays hot all the time we install a light with one wire to the common of the three way at both the building and house. Now connect the neutral to one of the traveler screws keeping continuity for the receptacle and do the same with the hot wire to the receptacle. Draw it out and see that it works.

Yes this is a violation of the polarity of the light fixture but it does work which edifies my statement that just because something will work in no way means that it is compliant and/or safe.
Once used a fan motor off the back of a refrigerator connected in series with a light bulb as a dimmer. I even once made a string of Christmas tree using festoon lights connected in series through an ice cube timer and thought about applying for a patent.

This stroll down memory lane has me remembering the Christmas I got my very own chamber pot. It was one that had a handle on it that reached all the way to the bottom. It was great for milking the old Jersey we had. I remember emptying that thing first thing in the morning and getting a bucket of water to wash her utter and letting her get a drink. She would always fill that pot to the brim which I would take back to the house and strain it into a 15 gallon can. Then back to the spring for another bucket of water that grandma would use to make a fresh cup of coffee for us all.
Well the first day after Christmas Grandpa complained about how awful the coffee tasted but I did learn a lesson. Never wash your chamber pot upstream from where you are going to drink. Us young ones drank milk for breakfast. That was the last time I have taken a drink of milk, some memories never die.
 