    Default Main Floor Washer/Sink plumbing setup question

    I came across this setup while searching through this site. It looks like it will work for me although I don't have quite the same distance between the washing machine and my drop in sink (not a normal washing tub) as they are both side by each. I have a new LG front load and a single stainless sink to instal. The old top loader drained to a simple 45 pipe that was tied into my laundry tub. The room itself is at the front of the two story house while my air stack is closer to the back of the house.
    I will be using a washing machine outlet box like the one in the photo. I will be recessing the pipes into the wall (inside wall) once I have torn the drywall out.
    Just wondering if I can go ahead and use this same setup for my own? the original thread was here and the photo (if it doesn't show here is the one at the bottom of the page as offered by Hammerlane.

    Name:  laundry.jpg
Views: 616
Size:  52.7 KB

  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,936

    Default

    Sure you can.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    DIY Senior Member asktom's Avatar
    Join Date
    Nov 2009
    Location
    Victor, MT
    Posts
    459

    Default

    The combination below the cleanout could be a sanitary tee.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    Unless your installation is LIKE that one, and you indicate that it might not be, then this might not be the easiest, or best, piping arrangement for your purposes.
    Licensed residential and commercial plumber

  5. #5
    DIY Member closer's Avatar
    Join Date
    Nov 2006
    Location
    Ontario
    Posts
    53

    Default

    Quote Originally Posted by hj View Post
    Unless your installation is LIKE that one, and you indicate that it might not be, then this might not be the easiest, or best, piping arrangement for your purposes.
    It looks pretty much identical... With the washing machine on the left and a sink on the right side. Once we have the drywall off we will have a better view of what is behind but I'm thinking it will be close if not the same. Hoping to tear the drywall off this weekend so will post back then.

    I'm interested to know though why you think it may not be the best arrangement for my purposes.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    In many cases it is going to be more complicated than you really need, but it depends on WHERE the vertical pipe is in the wall and in relation to the washer/sink locations.
    Licensed residential and commercial plumber

  7. #7
    DIY Member closer's Avatar
    Join Date
    Nov 2006
    Location
    Ontario
    Posts
    53

    Default

    I've got a few spots opened up to see what's in behind... also to show the proximity of the washer to the sink...
    One image shows the unit locations... the other the existing plumbing
    Name:  photo-2.jpg
Views: 223
Size:  32.3 KB
    Attached Images Attached Images  

  8. #8
    DIY Member closer's Avatar
    Join Date
    Nov 2006
    Location
    Ontario
    Posts
    53

    Default

    there is an electrical outlet from an adjoining room within inches of the plumbing (slightly visible in photo behind the cold water supply line)... no doubt not to any code... and I will be relocating it before proceeding with any plumbing. I also have to move the PTrap higher as there will be a cabinet slid into the area where the laundry tub is now... so... do you still think I have room to do the setup as it appears in the first photo? I have standard 16" studs in the wall to work with and it looks like only one set to slide everything through to make it work... not nearly as many as appear in the setup example.

  9. #9
    DIY Senior Member dj2's Avatar
    Join Date
    Aug 2013
    Location
    California
    Posts
    314

    Default

    The plan in the first photo has flaws.

    1. Washing machine standpipe must be 36" to 42" tall: lower the trap and raise the box.
    2. Electrical outlet must be GFI/GFCI.
    3. I would relocate the vent for the washing machine:

  10. #10
    DIY Senior Member asktom's Avatar
    Join Date
    Nov 2009
    Location
    Victor, MT
    Posts
    459

    Default

    UPC specifies the trap to be 6" to 18" above the floor and the standpipe 18" to 30" tall. I would put the trap at 12" and use a 30" standpipe.

  11. #11
    DIY Member rosem637's Avatar
    Join Date
    Jan 2013
    Location
    Michigan
    Posts
    38

    Default

    Quote Originally Posted by dj2 View Post
    The plan in the first photo has flaws.

    1. Washing machine standpipe must be 36" to 42" tall: lower the trap and raise the box.
    2. Electrical outlet must be GFI/GFCI.
    3. I would relocate the vent for the washing machine:
    #2 and #3 have no merit.

    Im going to say Outlet has GFI breaker.
    No functional reason to relocate vent for standpipe just because you say you would.
    Last edited by rosem637; 08-14-2013 at 02:11 AM.

  12. #12
    DIY Member closer's Avatar
    Join Date
    Nov 2006
    Location
    Ontario
    Posts
    53

    Default

    I have everything in place from the wet side... But have a very tiny leak at the copper brass threaded connection entering the Oakey box. It's on the hot side and seems to be leaking at the threads. I connected the two with plumbers dope as I was told this was better than Teflon etc for anther job and in fact it cured a previous thread leak on a washroom instal. The problems have now is that all the copper has been set in place and while I've turned the copper brass connection tighter (less than 1/4 turn) I'm afraid any more and two things will happen... 1 I will not be able to connect the hot water hose coming from the washing machine and 2 it will put undue stress on the copper joins which so far are showing signs that my soldering techniques are improving!
    What should I do about this leak as it will eventually be buried behind drywall?

  13. #13
    DIY Member closer's Avatar
    Join Date
    Nov 2006
    Location
    Ontario
    Posts
    53

    Default

    Here's the photo of where it's at now... with the leaky joint being the one with the old sock around it... I'm not sure why I ever used this box cuz it appears that there is no way to make adjustments to the joint without twisting and warping everything else in place. When I installed it I had it in place, soldered the down pipe to the copper threaded part, let it cool and then applied the plumber's dope to the threads and tightened it... same with the cold side that does not leak... both were tightened to about the same tautness but not overtightened... ... later I soldered the other joints then soldered that unit to the downpipe... this morning I found the drip and the rest is (bad) history

    guess my next question is... what do I do next to get out of this mess...
    a) unsolder the joint at the base of the 9" downpipe, clean it up, secure the threaded joint then resolder the joint again then hope for the best... my skills may not allow this
    b) unscrew the hot water valve (which does not presently leak!), tighten the copper brass connection, reattach the hot water valve with "x" number of wraps of teflon so that it faces the front again...
    c) find some other solution for below the water outlet box... ie... a flexible hose... but that may not either be code (inside wall) or advisable as it then brings two threaded connections into the mix
    d) do the laundry at the the local laundromat this weekend
    Name:  pipes.jpg
Views: 189
Size:  40.6 KB
    Last edited by closer; 08-16-2013 at 03:24 PM. Reason: added more info

  14. #14
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    Those threads are not tapered. They are meant to have a pipe inserted inside the end and soldered. No female fitting should be used there.
    It took us plumbers a while to figure that one out too.

    Just unthread and remove. Put it together with a section of pipe soldered on. Drop it back down into the box, and then using a coupling, solder it back up.
    you're almost there

  15. #15
    DIY Member closer's Avatar
    Join Date
    Nov 2006
    Location
    Ontario
    Posts
    53

    Default

    Holy Shmoly!!! I'd have never in a million figured that one out... Thanks Terry...

    Now i have another question... when i soldered the 9" copper with (unnecessary) fitting to the brass one (like I shouldn't have) i left the valve open and had a wet (not soaking) rag around the top of the pipe to make sure that it didn't melt the plastic... but will I be able to unthread it ok without twisting the existing setup?... I'll check before doing anything drastic... anyway... else I'll have to cut the 9" section or lower to keep the heat further away from the plastic box and valve (left it on first time cuz I couldn't unfasten it! (probably just weak and afraid of cranking it!)...

    Any special tips for soldering copper pipe to a brass fitting?

Similar Threads

  1. Wye Setup for Laundry Sink and Possible Standpipe - Renewing 90 YO CI Plumbing
    By JHZR2 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 07-27-2013, 07:26 AM
  2. Need washer & sink plumbing setup advice.
    By AnthonyC in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 07-07-2013, 06:02 AM
  3. Washer box & sink question
    By builder59 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 05-10-2007, 06:02 AM
  4. Leaky Utility Sink / Odd Setup for Washer
    By sirih in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 02-10-2007, 10:51 AM
  5. Moving washer and sink... DWV question
    By AMP in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 05-03-2006, 06:04 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •