  1. #31
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,936

    Default

    Yea, leaking, rotted returns is a very common thing. I'd estimate that we repair a dozen or so every year. Not as common on the supply piping but it does happen, especially at the radiator valve which are another source of problems because packings wear out and valves freeze in position. Then you get into radiator and main vents that haven't been changed in 50 years, radiator and main traps that quit working properly sometime in the 50's. Steam is wonderful when everything is in new condition and functioning properly but its expensive to maintain. A quick tell, is when you see the pressure-troll cranked up to 5 lbs or so trying to compensate for other problems. Most residential steam was designed to run at around 1/2lb steam.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  2. #32
    DIY Member
    Join Date
    May 2012
    Location
    Brooklyn, New York, United States
    Posts
    46

    Default

    Quote Originally Posted by BadgerBoilerMN View Post
    Viessmann does not mandate P/S and one of the reasons they are one of our favorites on steam and gravity conversions. They do like to sell hydrolic separators, something trade magazines and those who write for them are sensitive to.

    There is no logical argument for doubling electrical operated costs and the chance of a nuisance no-heat by adding a redundant circulator to any single zone hydronic system. The only thing this will accomplish, beyond the obvious wasted labor, material and operating cost, is to inevitably raise the return water temperature to the boiler. This is not progress where condensing boilers are concerned.
    these are clear guidelines for LLH
    also make a note that in viessmann opinion primary secondary arrangement does promote condensing in condensing boilers, quite different from your statement.
    Name:  2013-08-30 21.22.01.png
Views: 75
Size:  81.6 KB
    Last edited by gennady; 08-30-2013 at 06:35 PM. Reason: Grammar, English is not my native language

  3. #33
    DIY Member
    Join Date
    May 2012
    Location
    Brooklyn, New York, United States
    Posts
    46

    Default

    Quote Originally Posted by BadgerBoilerMN View Post
    The higher the water temperature delivered to the radiation, the higher the heat load
    This is not true. load is determined by space heat loss, not temperature of radiator. Also, delivering higher temperature water to radiator or manifold, allows to cut on flow, because heat load is dictated by heat loss, and using universal formula Q=dTxFlow(GPM) x500, where Q is amount of heat transferred by water flow, we see if we increase delta t we can decrease flow, and cut pumping costs and so on.
    Last edited by gennady; 08-30-2013 at 06:51 PM.

  4. #34
    DIY Member
    Join Date
    May 2012
    Location
    Brooklyn, New York, United States
    Posts
    46

    Default

    Quote Originally Posted by Tom Sawyer View Post

    but when you back that out against a 10 to 20 thousand installation cost
    It costs much more than $20.000 to do steam to hot water conversion properly
    Last edited by gennady; 09-01-2013 at 05:35 AM.

  5. #35
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,714

    Default

    Quote Originally Posted by gennady View Post
    This is not true. load is determined by space heat loss, not temperature of radiator. Also, delivering higher temperature water to radiator or manifold, allows to cut on flow, because heat load is dictated by heat loss, and using universal formula Q=dTxFlow(GPM) x500, where Q is amount of heat transferred by water flow, we see if we increase delta t we can decrease flow, and cut pumping costs and so on.
    gennady- you conveniently omit and thus misconstrue the rest of BadgerBoilerMN's statement, which was his primary point:

    "The higher the water temperature delivered to the radiation, the higher the heat load. Yes, the heat load since temperature differential between indoor air and outdoor air during design conditions is but one factor of heat loss 200F radiators next to double hung window from the horse-and-buggy days will drive more heat out of the building than the same radiator at 100F operating on ODR."

    Yes, a hotter radiator next to a high-U section of exterior (like a window) does in fact increase the heat loss of the building, in exactly the manner he states- you can't cheat the raw physics. Raising the convecting column of air next the window several 10s of degrees relative to what it would be with a low-temp system creates a higher net heat load, even at the same average room temperature.

    Similarly you somehow mis-read Viesmann's promotion of P/S plumbing at a mandate for the same, which it clearly is not. It explicitly spells out "When to use a low loss header:", leaving implicit the conditions under which is it not needed. A suggestion is not a mandate- designers who can do the math know the difference. If the design flow requirements of both the system & the boiler are in the same range there is no requirement (or any real reason) for hydraulic separation.

    When making the argument, please try to parse the words of Viessmann or BadgerBoilerMN a bit more carefully, lest it stop making sense.

  6. #36
    DIY Member
    Join Date
    May 2012
    Location
    Brooklyn, New York, United States
    Posts
    46

    Default

    Quote Originally Posted by Dana View Post
    gennady- you conveniently omit and thus misconstrue the rest of BadgerBoilerMN's statement, which was his primary point:

    "The higher the water temperature delivered to the radiation, the higher the heat load. Yes, the heat load since temperature differential between indoor air and outdoor air during design conditions is but one factor of heat loss 200F radiators next to double hung window from the horse-and-buggy days will drive more heat out of the building than the same radiator at 100F operating on ODR."

    Yes, a hotter radiator next to a high-U section of exterior (like a window) does in fact increase the heat loss of the building, in exactly the manner he states- you can't cheat the raw physics. Raising the convecting column of air next the window several 10s of degrees relative to what it would be with a low-temp system creates a higher net heat load, even at the same average room temperature.

    Similarly you somehow mis-read Viesmann's promotion of P/S plumbing at a mandate for the same, which it clearly is not. It explicitly spells out "When to use a low loss header:", leaving implicit the conditions under which is it not needed. A suggestion is not a mandate- designers who can do the math know the difference. If the design flow requirements of both the system & the boiler are in the same range there is no requirement (or any real reason) for hydraulic separation.

    When making the argument, please try to parse the words of Viessmann or BadgerBoilerMN a bit more carefully, lest it stop making sense.

    where in my post

    "these are clear guidelines for LLH
    also make a note that in viessmann opinion primary secondary arrangement does promote condensing in condensing boilers, quite different from your statement."

    you see words viessmann mandates?

    Also see all benefits listed. Why not do it right?

    And on all jobs conditions of flow in the system within parameters of boiler flow? Hard to believe. P/S guaranties trouble free performance of system and boiler. When I design systems, I do not go pennies and dimes, system must be done right, no corners cut. Eliminating P/S makes no sense whatsoever.
    I do not buy into argument that 2nd pump consumes more electricity or can break. There 2 ways of doing job, right or whatever.
    Last edited by gennady; 09-03-2013 at 08:03 PM.

  7. #37
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,936

    Default

    Around 20 large is possible with the right crew and we have the right crew. It's the labor that usually gets you.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  8. #38
    DIY Member
    Join Date
    May 2012
    Location
    Brooklyn, New York, United States
    Posts
    46

    Default

    Quote Originally Posted by Tom Sawyer View Post
    Around 20 large is possible with the right crew and we have the right crew. It's the labor that usually gets you.
    Usually $20k+ only boiler with indirect. Steam to hot water with mod con boiler and indirect for 20K is below the cost in my opinion.

  9. #39
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,714

    Default

    Quote Originally Posted by gennady View Post
    where in my post

    "these are clear guidelines for LLH
    also make a note that in viessmann opinion primary secondary arrangement does promote condensing in condensing boilers, quite different from your statement."

    you see words viessmann mandates?

    Also see all benefits listed. Why not do it right?

    And on all jobs conditions of flow in the system within parameters of boiler flow? Hard to believe. P/S guaranties trouble free performance of system and boiler. When I design systems, I do not go pennies and dimes, system must be done right, no corners cut. Eliminating P/S makes no sense whatsoever.
    I do not buy into argument that 2nd pump consumes more electricity or can break. There 2 ways of doing job, right or whatever.
    His statement was "Viessmann does not mandate P/S...". Your statement was that the Viessmann's document indicated something "quite different" from his statement. Quite different would mean that they in fact DO mandate P/S plumbing. Nothing in the the supplied document differs from BadgerBoilerMN's assertion- far from it. The document merely suggests where P/S might be beneficial.

    Nobody was making blanket statements that direct pumping is suitable "on all jobs" either, only some.

    Yet again, you bark up an empty tree, mis-stating or misconstruing the statements of others rather than parsing the actual sentences.

  10. #40
    DIY Member
    Join Date
    May 2012
    Location
    Brooklyn, New York, United States
    Posts
    46

    Default

    Quote Originally Posted by Dana View Post
    His statement was "Viessmann does not mandate P/S...". Your statement was that the Viessmann's document indicated something "quite different" from his statement. Quite different would mean that they in fact DO mandate P/S plumbing. Nothing in the the supplied document differs from BadgerBoilerMN's assertion- far from it. The document merely suggests where P/S might be beneficial.


    Quote Originally Posted by BadgerBoilerMN
    QUOTE: Viessmann does not mandate P/S and one of the reasons they are one of our favorites on steam and gravity conversions. They do like to sell hydrolic separators, something trade magazines and those who write for them are sensitive to.

    There is no logical argument for doubling electrical operated costs and the chance of a nuisance no-heat by adding a redundant circulator to any single zone hydronic system. The only thing this will accomplish, beyond the obvious wasted labor, material and operating cost, is to inevitably raise the return water temperature to the boiler. This is not progress where condensing boilers are concerned. END OF QUOTE
    ===============================
    MY RESPONSE: something quite different is indicated in viessmann document. And this difference is that P/S does promote condensing in condensing boilers

    and this is what i wrote in my post:
    These are clear guidelines for LLH
    also make a note that in viessmann opinion primary secondary arrangement does promote condensing in condensing boilers, quite different from your statement.

    Again, the difference is that BadgerBoilerMN stated primary secondary is not progress where condensing boilers are concerned, and viessmann statement is that primary secondary does promote condensing in condensing boilers. you see, this is the difference

    MY RESPONSE: P/S does promote condensing in condensing boilers according viessmann manual

    Also if you read viessmann list of benefits, you see there are benefits in P/S, and this is quite different from the statement:
    QUOTE: There is no logical argument for doubling electrical operated costs and the chance of a nuisance no-heat by adding a redundant circulator to any single zone hydronic system. END OF QUOTE

    it is not just redundant pump and doubling electrical costs.
    please read list of benefits.
    Also Dan Hologan wrote a book, named " primary secondary pumping made easy", addressing all these benefits, you can see picture of its cover few posts earlier, read it, you might like it.

  11. #41
    Master Hot Water Mpls,MN BadgerBoilerMN's Avatar
    Join Date
    Mar 2011
    Location
    Minneapolis
    Posts
    285

    Default

    Quote Originally Posted by gennady View Post
    ===============================
    MY RESPONSE: something quite different is indicated in viessmann document. And this difference is that P/S does promote condensing in condensing boilers

    and this is what i wrote in my post:
    These are clear guidelines for LLH
    also make a note that in viessmann opinion primary secondary arrangement does promote condensing in condensing boilers, quite different from your statement.

    Again, the difference is that BadgerBoilerMN stated primary secondary is not progress where condensing boilers are concerned, and viessmann statement is that primary secondary does promote condensing in condensing boilers. you see, this is the difference

    MY RESPONSE: P/S does promote condensing in condensing boilers according viessmann manual

    Also if you read viessmann list of benefits, you see there are benefits in P/S, and this is quite different from the statement:
    QUOTE: There is no logical argument for doubling electrical operated costs and the chance of a nuisance no-heat by adding a redundant circulator to any single zone hydronic system. END OF QUOTE

    it is not just redundant pump and doubling electrical costs.
    please read list of benefits.
    Also Dan Hologan wrote a book, named " primary secondary pumping made easy", addressing all these benefits, you can see picture of its cover few posts earlier, read it, you might like it.
    I have a signed copy, thank you. Fortunately I have actually installed, distributed and manufactured condensing boilers for a living since the 80's. I agree that it is best for the average plumber to use P/S, one cannot argue this point. I am speaking mainly of single zone conversions in which the flow rate thought distribution is greatly enhanced in the case of a gravity system (any flow would be an improvement) and the flow through the low-mass condensing boiler (many will suffer a 45 delta-T) is easily satisfied with the smallest of common circulators. Adding a extra pump in such a case would be wasteful and ignorant neither of which I care to be associated with. Thus we do not use Buderus, Weil McLain Ultra, SlantFin condensing for small hydronic systems where P/S can't be rationally justified, as they share your the single-minded opinion, with one intellectual advantage; in benefits them in fewer service tech calls and they don't pay for the considerable installation and operating cost of the redundant pump.

    Simply put, if the flow through the system and the boiler are adequate to both no advantage can be gained by applying P/S piping either for hydraulic separation or flow control. The design has it's applications, mostly commercial, multi-boiler and multi-temperature applications but a steam or gravity conversion most certainly is not one of them.

  12. #42
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,714

    Default

    "Promoting" a practice is a very very distant cry from "mandating". When the math proves that it's not necessary, it's simply not necessary. Presuming that P/S is the only way to "do it right" is for folks who can't or won't do the math (which is apparently the vast majority of boiler installers.)

    Since P/S piping can limit the damage from a host of design errors from the folks who can't/don't do math it's in the manufacturer's interest to promote the practice, but that doesn't mean it's always the right thing to do.

  13. #43
    DIY Member
    Join Date
    May 2012
    Location
    Brooklyn, New York, United States
    Posts
    46

    Default

    So, if you using TRVs, do you use p/s or you still using direct pumping ? Also buderus , Weil McLain and slant fin are great brand names and I feel good you some how place me in that group in regards of single minded average plumber I am.
    So still do you use TRVs with direct pumped boiler ?

  14. #44
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,936

    Default

    Two words " VFD pumps"
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  15. #45
    In the Trades LamdaPro200's Avatar
    Join Date
    May 2013
    Location
    New York
    Posts
    10

    Default

    Here is why you should/must be using a LLH with a Vitodens 200. There is no TT on the boiler. The boiler logic utilizes a down stream/LLH sensor to maintain the proper supply side water temperature the system needs based on the set ODR curve. Second, Viessmann boiler pumps are sized for 40 degree rises meaning your boiler or primary side flow rate is much lower then the system side flow rate. As an example the max flow rate for a B2HA35, 19,000-125,000 is 6.2gpm. If the system side has a need for higher flow rate you must pri/sec or use a LLH. Now can you direct pipe it. Yes you can but you will now loose some of the control logic and features in the control.

    For a direct piped system you would have to utilize the 143 plug, ie, external demand. Now you've just made a smart boiler dumb and have to tell it what to do. Generally the 143 plug is used when your either doing snowmelt or maybe a pool HX were you want a fixed set point.

    The biggest issue with condensing boilers is the boiler pump selection. We select fixed speed pumps based off the traditional 20 degree rise that promotes high boiler side flow rates that the system side cannot take away and you end up with elevated boiler return water temps and short cycling condensing boilers. You can never oversize a condensing boiler on the high end output because the boiler will never get there unless it sees the design delta-t but it sure can be oversized in the low end and that fixed speed pump is always the culprit.

    The additional benefits of air, dirt separation and protecting the HX from system debris and the utilization of the system side or LLH sensor is why Viessmann strongly recommends the LLH over pri/sec.

    What happens to your fixed speed boiler pump when piped direct? Either one or two things. You over pump the zones or you beat the living day lights out of the pump because if your not splurging on a couple of tees you sure the heck aren't buying a pressure differential bypass.
    Last edited by LamdaPro200; 09-05-2013 at 04:17 PM.
    "The bitter taste of a poor installation remains much longer than the sweet taste of the lowest price."

Similar Threads

  1. Steam heat and pressuretrol switch
    By racerc20 in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 02-02-2010, 05:16 PM
  2. pex and steam heat
    By arturofitz in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 01-18-2010, 09:24 AM
  3. steam radiator valve for hot water heat
    By chickenbrown in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 08-14-2009, 07:48 AM
  4. Clicking noises in steam heat pipes??
    By Katie Easton in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 01-30-2006, 04:57 PM
  5. Boilers, and Steam for heat
    By kerrpress@telis.org in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 11-04-2005, 07:04 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •