    Default 50 amp breaker for kitchen appliances

    I have a rental property that has a 50 amp 220 VAC circuit that supplies power for both an electric cooktop and wall oven. I would like to replace both appliances with new ones. The cooktop I have in mind requires a 30 amp breaker per the specs. For the wall oven, I would like to install an electric oven/microwave combo unit, and it requires a 30 amp breaker per the specs. Doing just a simple addition, it would seem I need a 60 amp breaker. Which is, of course, problematic, since I only have a 50 amp breaker. But, I started to wonder, in a situation like this, is there any sort of "derating" (I think that's the proper term) factor that can be applied to this arrangement, such that 50 amps would be considered adequate? After all, it would be rare to have all 4 cooktop burners, the oven and microwave all going full bore at the same time. I looked briefly in some electrical references I have, but haven't come across anything that addresses this.

    Even if no such allowance is allowed per the code, is it really a bad, unsafe idea to put both of these appliances on a 50 amp circuit? Would there be problems, other than tripping the breaker once in a while?

    I guess if worse comes to worse, I could just go with a separate wall oven and microwave, and put the microwave on its own 120 VAC circuit.

    Thanks in advance for all your help.

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    There should be a VA rating on each unit that would help.

    Using the 30 amps of each unit we can come up with something general.

    30 times 240 equal 7200. 7200 times 2 equals 14,400

    14,400 subtract 12,000 equals 2,400
    Now increase the demand found in column “C” by 5% for each KW or fraction thereof
    8,000 times 115% equals 9,200 divided by 240 equals 38.33

    210.19 says that a fifty amp circuit can be tapped as you propose so it looks as though what you propose would be code compliant. Always remember that anything less than code compliant is not safe.

  3. #3
    DIY Member thebeave's Avatar
    Join Date
    Oct 2008
    Location
    California
    Posts
    35

    Default

    Quote Originally Posted by jwelectric View Post
    There should be a VA rating on each unit that would help.

    Using the 30 amps of each unit we can come up with something general.

    30 times 240 equal 7200. 7200 times 2 equals 14,400

    14,400 subtract 12,000 equals 2,400
    Now increase the demand found in column C by 5% for each KW or fraction thereof
    8,000 times 115% equals 9,200 divided by 240 equals 38.33

    210.19 says that a fifty amp circuit can be tapped as you propose so it looks as though what you propose would be code compliant. Always remember that anything less than code compliant is not safe.
    Thanks! I will look up the VA rating myself on the appliances. I would like to do the calculations like you just did for the appliances I'm considering. Can you refer me to this table online so I can understand the theory behind what you just did? Much appreciated!

  4. #4
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,639

    Default

    I would not change the breaker size, and just replace the appliances.

    Then test the load for "Normal Use"

    Chances are you will be OK.

    If you need more power, then another breaker and wire run will be required. For safety.


    When putting in new appliances a person should be decreasing power usage, Not Increasing it.


    Have Fun.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  5. #5
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    Let me see if I got this straight. You have two appliances that each require 30 amp breakers but you want to use only one 50 amp to protect both? If either of the appliances malfunctioned and drew more than 30 amps, the current would be greater than what it was designed for since the single breaker would allow 50 amps. I would think that each appliance would need its own 30 amp breaker.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,615

    Default

    Since the breaker is to protect the wire from overload, and your appliances will not likely require the full amperage at any one time, just as the breakers in a panel can exceed the rating for the main breaker, you will be okay. IF you should exceed the amperage, which is unlikely, the breaker will trip and terminate the overload. To avoid the problem of a 50 amp breaker protecting a 30 amp device, you could install a subpanel fed by the 50 amp breaker with two 30 amp breakers in it.
    Licensed residential and commercial plumber

  7. #7
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    The wires of the individual appliances may be sized only for 30 amps since the specs call for a 30 amp breaker.

  8. #8
    Sprinkler Guy Wet_Boots's Avatar
    Join Date
    Mar 2007
    Location
    Metro NYC
    Posts
    798

    Default

    There might be some additional factors applied, for an electric oven and cooktop, as they are constant resistive loads not unlike my baseboard electric heaters, which are only allowed to draw 80 percent of the branch circuit capacity.

  9. #9
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by LLigetfa View Post
    The wires of the individual appliances may be sized only for 30 amps since the specs call for a 30 amp breaker.
    ...and for a 30A outlet. There is nothing wrong with connecting a 30A load (or even a potential 60A load) to a 50A circuit, but connecting two outlets of 30A each (or even of whatever size) at the end of a circuit intended for one does not sound right to me.
    Last edited by leejosepho; 08-02-2013 at 10:45 AM.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  10. #10
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by thebeave View Post
    I would like to do the calculations like you just did for the appliances I'm considering. Can you refer me to this table online so I can understand the theory behind what you just did? Much appreciated!
    See the NEC at 220.55 and table 220.55 including notes

  11. #11
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Come on now people let’s think a little. We install multiple 15 amp receptacles on 15 and 20 amp circuits so what is the problem with installing a cooktop and oven as outlined in the NEC?

    210.19 allows a #12 or larger tap for a cooktop or oven to a 50 amp circuit or you can pull individual circuits which ever you choose. What that is included in the manual does not count for much unless it is included in the listing and labeling of the appliance and no it does not void a warranty. The instructions included in the listing and labeling of an appliance can be found in the UL Guides and Whitebook

  12. #12
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by jwelectric View Post
    210.19 allows a #12 or larger tap for a cooktop or oven to a 50 amp circuit or you can pull individual circuits which ever you choose.
    So then, I could put a 30A welder outlet in the tool closet in my carport and directly behind the 50A receptacle for our oven (with gas top) in the kitchen? I know that would work, but I did not know it is legal!
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  13. #13
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by leejosepho View Post
    So then, I could put a 30A welder outlet in the tool closet in my carport and directly behind the 50A receptacle for our oven (with gas top) in the kitchen? I know that would work, but I did not know it is legal!
    no that would not be legal but wiring a cooktop and oven to a 50 amp circuit is legal


    210.19 Conductors — Minimum Ampacity and Size.
    (A) Branch Circuits Not More Than 600 Volts.

    (3) Household Ranges and Cooking Appliances. Branch-circuit conductors supplying household ranges, wall-mounted ovens, counter-mounted cooking units, and other household cooking appliances shall have an ampacity not less than the rating of the branch circuit and not less than the maximum load to be served. For ranges of 8 kW or more rating, the minimum branch-circuit rating shall be 40 amperes.

    Exception No. 1: Conductors tapped from a 50-ampere branch circuit supplying electric ranges, wall-mounted electric ovens, and counter-mounted electric cooking units shall have an ampacity of not less than 20 amperes and shall be sufficient for the load to be served. These tap conductors include any conductors that are a part of the leads supplied with the appliance that are smaller than the branch-circuit conductors. The taps shall not be longer than necessary for servicing the appliance.


    Table 220.55
    Note 4. Branch-Circuit Load. It shall be permissible to calculate the branch-circuit load for one range in accordance with Table 220.55. The branch-circuit
    load for one wall-mounted oven or one counter-mounted cooking unit shall be the nameplate rating of the appliance. The branch-circuit load for a
    counter-mounted cooking unit and not more than two wall-mounted ovens, all supplied from a single branch circuit and located in the same room,
    shall be calculated by adding the nameplate rating of the individual appliances and treating this total as equivalent to one range.

  14. #14
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by jwelectric View Post
    no that would not be legal but wiring a cooktop and oven to a 50 amp circuit is legal
    Okay, clarified.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  15. #15
    DIY Member thebeave's Avatar
    Join Date
    Oct 2008
    Location
    California
    Posts
    35

    Default

    Quote Originally Posted by thebeave View Post
    Thanks! I will look up the VA rating myself on the appliances. I would like to do the calculations like you just did for the appliances I'm considering. Can you refer me to this table online so I can understand the theory behind what you just did? Much appreciated!
    The cooktop VA rating is 7200, and the oven/microwave combo VA rating is 6400. So, I'm a bit better off than you calculated. Thanks again, everyone for all the input. Learned something new!

Similar Threads

  1. Appliances - Dry Rot?
    By MB1 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 08-02-2013, 08:39 AM
  2. Possible "broken breaker" miswiring kitchen splits
    By khedrei in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 09-29-2011, 09:35 PM
  3. Sizing Kitchen Range Breaker Size & Wire Gauge
    By chuck b in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 04-27-2011, 05:05 AM
  4. bad smell from gas appliances
    By storms in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 12-15-2010, 10:35 AM
  5. kitchen appliances
    By chaoster in forum Remodel Forum & Blog
    Replies: 3
    Last Post: 03-15-2009, 04:04 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •