Thread: Can three #8 and one #10 wires be in ½” metal conduit?

  1. #16
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Wet_Boots View Post
    By the way, did the tables change when large appliances went from 3-blade plugs to 4-blade plugs? Way back when, there wouldn't have been anything in a range outlet, for instance, for a fourth wire to connect to, so it wasn't going to be in the cable with the two hots, right?
    The use of old rubber insulation on conductors would only allow two #8 conductors in a ½ inch flexible conduit, reference the 1940 edition of the NEC

    I didn’t know that three conductor was ever allowed for ranges and dryers since the requirement for an EGC. In 4237 of the 1940 edition ranges were required to be grounded.

  2. #17
    DIY Member electrotuko's Avatar
    Join Date
    May 2007
    Location
    Chicago, IL
    Posts
    46

    Default

    Wet_Boots, thanks for pointing to online Conduit Fill calculator.
    I used this place to find ODiameters for THHN 90C wires:
    http://www.bestelectricsales.com/dat...eWire-THHN.pdf
    For 8 AWG shows 0.212", for 10 AWG is 0.160".
    Running online calculations for three 8 AWG and one 10 AWG results in:
    The conduit fill is: 39.79%

    Still not clear can I run more than three 8 AWG wires inside ½” conduit?
    Or even your idea to run bare 8 gauge wire, can this be OK?
    I just do not have room in my box to install ¾” metal flex cable, no open knockout available for this size.

  3. #18
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,673

    Default

    quote; no open knockout available for this size.

    Then you make one that size.
    Licensed residential and commercial plumber

  4. #19
    DIY Member electrotuko's Avatar
    Join Date
    May 2007
    Location
    Chicago, IL
    Posts
    46

    Default

    Still confusing regarding NEC specs for conduit fill.
    I seen in the store already made metal flex cable with three 10 gauge wires inside, this looks even smaller diameter than regular 3/8" metal flex.
    Running online calculator for three 10 gauge wires shows:
    The conduit fill is: 52.08%
    And ofcourse a warning:
    Warning: Conduit Fill of 40.0% has been exceeded

    How you would comment this case?

  5. #20
    DIY Member electrotuko's Avatar
    Join Date
    May 2007
    Location
    Chicago, IL
    Posts
    46

    Default

    OK OK, just got 3/4" metalf flex, this time will comply with NEC Code, even it does not make sense to me in this case.

  6. #21
    Sprinkler Guy Wet_Boots's Avatar
    Join Date
    Mar 2007
    Location
    Metro NYC
    Posts
    798

    Default

    It's usually easier to just oversize things and skip the calculations. I have some interest in shoehorning (within the confines of the rules) conductors and grounds into 1/2 and even 3/8 steel flex, in order to make some new wiring look like older wiring that's been there for awhile. That has me running the fill calculator, with both solid and stranded THHN, and scratching my head over what is or isn't considered a full-load conductor.

Similar Threads

  1. Aluminum wire and plastic conduit or copper and metal?
    By leejosepho in forum Electrical Forum discussion & Blog
    Replies: 25
    Last Post: 03-10-2013, 03:34 PM
  2. Running Wires in Conduit inside a wall
    By Andi.M in forum Electrical Forum discussion & Blog
    Replies: 13
    Last Post: 02-06-2013, 07:39 AM
  3. Pulling low voltage wires through metal studs
    By Ian Gills in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 08-31-2009, 03:54 PM
  4. flexible metal conduit/greenfield
    By solutions in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 03-22-2008, 05:14 AM
  5. Conduit size vs. number of wires
    By brosnt1 in forum Electrical Forum discussion & Blog
    Replies: 1
    Last Post: 09-06-2007, 06:31 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •