    Hi,
    In my maintenance job I came across a small B&G circulating pump installed on a hot water loop in a 60+ room Motel. It isn't very old, less than a year. I found the box that it came in indicating it is an iron cast not brass. What problems should I be aware of to report to the owner? I'm sure the cost difference was
    the reason this happened.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,408

    Default

    Code requires it to be SS or bronze as I understand it. Because potable water has lots of dissolved oxygen, it will eat itself up fairly quickly, not counting the iron it adds to the water for potential stains on the sinks and showers. An iron pump is only okay in heating situations where it is a closed system - there, the oxygen gets purged fairly quickly and the water becomes somewhat inert.
    Last edited by jadnashua; 07-31-2013 at 06:47 AM. Reason: changed brass to bronze
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member dwi's Avatar
    Join Date
    Jul 2013
    Location
    south west MO.
    Posts
    3

    Default

    Quote Originally Posted by jadnashua View Post
    Code requires it to be SS or brass as I understand it. Because potable water has lots of dissolved oxygen, it will eat itself up fairly quickly, not counting the iron it adds to the water for potential stains on the sinks and showers. An iron pump is only okay in heating situations where it is a closed system - there, the oxygen gets purged fairly quickly and the water becomes somewhat inert.
    Are there any potential health problems connected with this sort of thing? Wouldn't the rust build up in the water heaters over time?

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    There aren't any "health problems" unless someone starts drinking the hot water. The pump will rust and deteriorate fairly rapidly because of the oxygen in fresh water. Cost and lack of knowledge, are the two most common reasons. the "rust" will occur ON the pump and will stay there until the pump fails.
    Licensed residential and commercial plumber

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,408

    Default

    The rust particles could flow through the pipes and clog faucets and/or showerheads. Because it is being distributed to lots of places, the amount would be small at any one place, and it may not be noticeable. The 'proper' pump costs more, but maybe not when you consider that the iron one will need to be replaced sooner and could create some other issues along the way.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    If the particles detach from the pump, and they usually do not, they will go into the storage tank and fall to the bottom. The quantity would be very small so they would not "fill up" anything, nor would they gravitate to the faucets.
    Licensed residential and commercial plumber

  7. #7
    DIY Junior Member dwi's Avatar
    Join Date
    Jul 2013
    Location
    south west MO.
    Posts
    3

    Default

    Thank you both for your help. I may not get them to change it right now but they may just change it soon enough.

    dwi

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    Let it run until it freezes up or deteriorates to the point it no longer circulates.
    Licensed residential and commercial plumber

Similar Threads

  1. Hot water Reciculating loop vs integrated loop question...which?
    By danrudy in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 01-31-2013, 10:43 AM
  2. Replies: 3
    Last Post: 01-03-2011, 01:29 PM
  3. Re-piping the main loop of a cast-iron radiator system
    By jmk823 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 10-02-2009, 12:17 PM
  4. Hard Water Compatibility Open Loop Heat Pump
    By type@uwm.edu in forum Solar and Geothermal Water Heating Forum
    Replies: 7
    Last Post: 05-13-2008, 07:12 AM
  5. Hard Water Compatibility Open Loop Heat Pump
    By type@uwm.edu in forum Pumps and Tanks Well Forum & Blog
    Replies: 7
    Last Post: 05-13-2008, 07:12 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •