Very nice installation! The only thing I would have done differently was the plumbing connectors. Fleck makes Sweat connectors to replace the plastic threaded connectors. It will not affect anything, I just prefer to do them that way.
Just a note, check you air gaps in the floor sink. Confirm your code allows them to be below the level. Most codes require that there is an air gap of twice the diameter of the pipe, but not less than 1". Also, electrical grounding, check that you did not interupt the grounding with the break in the copper plumbing at the softener. A simple jumper can correct that.
Just a note, check you air gaps in the floor sink. Confirm your code allows them to be below the level. Most codes require that there is an air gap of twice the diameter of the pipe, but not less than 1". Also, electrical grounding, check that you did not interupt the grounding with the break in the copper plumbing at the softener. A simple jumper can correct that.