    Default 5800 SXT start up

    Hi Pro`s
    I just installed a water softener, i do not know how set this up at first time when i started it it spits lots of water thru drain pipe.
    Not sure weather it is normal so i stopped it.
    Can anybody suggest me from the start up procedure for new water softener please.
    Thanks,

  2. #2
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,712
    Blog Entries
    1

    Default

    What is the tank size? i can post a programming guide on Monday.

  3. #3
    DIY Junior Member ra's Avatar
    Join Date
    Jul 2013
    Location
    Manitoba
    Posts
    7

    Default

    it is 64000 capacity grain tank

  4. #4
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,712
    Blog Entries
    1

    Default

    Sorry, out of the office all day. I will try to post it for you in the morning.

    Congrats on the new system!

    And, what color is the injector, and the BLFC size? The BLFC should be indicated by the sticker on the injector assembly. Also confirm the DLFC button size, and what is your water temperature?

  5. #5
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,712
    Blog Entries
    1

    Default

    Here is a quick master programming guide.
    1: set time to 12:01 P.M.
    2: push “regen” button
    3: push and hold ^ v buttons to enter master program mode
    Push “regen” button between each step to get to next step
    4: DF Gal, factory set, leave as-is
    5: VT 5800
    6: RT dF1b, set to dF2b
    7: CT Fd, factory set, leave as-is
    8: C set to 48
    9: H 20, set to the actual water hardness
    10: RS Set to SF
    11: SF Set to 15
    12: DO 14 factory set, leave as-is
    13: RT 2:00 factory set, leave as-is
    14: BW Set to 5
    15: BD 60 factory set, leave as-is
    16: B2 set to 5
    16: RR Set to 5
    17: BF set to 43 for .125 BLFC, 22 for .25 BLFC


    18: FM t0.7 factory set, leave as-is

Similar Threads

  1. $5800.00 to replace the well pump and wiring
    By Jonnie Claeys in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 06-19-2012, 10:18 PM
  2. Review of the new...Fleck 5800 valve
    By Tom Sawyer in forum Water Softener Forum, problems, installation and reviews
    Replies: 3
    Last Post: 06-08-2012, 08:52 AM
  3. A/C start-up intermittent start up issue
    By jp102 in forum HVAC Heating & Cooling
    Replies: 37
    Last Post: 08-01-2011, 03:13 PM
  4. delayed start
    By jsmith6752 in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 07-27-2007, 08:19 AM
  5. where to start?
    By reve4asu in forum Remodel Forum & Blog
    Replies: 5
    Last Post: 09-20-2005, 03:01 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •