    I am looking to use a well that is across the street from my house and I would like to know if the existing pump is the right size and if so what size pipe to run.

    The existing pump is a 1hp.
    Not sure of the GPM and the depth is a question mark also.This well was already put in when the land was purchased.
    it is a submersible pump though.
    I would like to run from this well to approximatly 600 feet to my house. The grade change is down hill from the well to the house at about a 4 ft. drop.
    I would like to have the pressure at my house to be what it is set at now (40-60 psi).

    I was going to run 1-1/4" at least half way and then change over to 1". (any ideas)?
    To check the output of the well we ran the pump for about 4 hours so the capacity seems to be alright.
    I assume the pump GPM to be around 10 (that is pretty typical right?)

    anyhelp on the sizing of the pump and pipe size to my house would be great! I know the well pump depth and water level are mysteries but if we could use worse case averages I think it will be okay.

  2. #2
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    A 1 HP, 10 GPM should build plenty of pressure. But the depth of the well or at least the water level is important. I would just stay with 1 ” all the way. A long distance of small pipe is a pressure killer.

  3. #3
    DIY Junior Member Mporter444's Avatar
    Join Date
    Jul 2013
    Location
    Georgia
    Posts
    2

    Default

    Should I run 1-1/2" about 250 feet then run 1-1/4".
    Also I assume sch. 40 pvc is okay....
    And what size chase should I under the road 2"?
    Do I need any check valves?
    Thanks.

  4. #4
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    At 15 GPM, 1" pipe loses 5.08 PSI per hundred feet. 1 1/4" loses 1.34 PSI per hundred, and 1 1/2" loses .63 PSI per hundred. So the 1 1/4" will be fine, 1 1/2" won't hurt anything, but 1" would lose 30 PSI in 600'.

Similar Threads

  1. D-W-V Pipe sizing
    By Stormrider49 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 13
    Last Post: 01-10-2010, 02:28 PM
  2. Water Source Heat Pump Deep Pump Sizing
    By Greg-VA in forum Solar and Geothermal Water Heating Forum
    Replies: 66
    Last Post: 04-20-2009, 09:33 AM
  3. Water Source Heat Pump Deep Pump Sizing
    By Greg-VA in forum Pumps and Tanks Well Forum & Blog
    Replies: 63
    Last Post: 01-21-2007, 04:49 PM
  4. Gas pipe sizing
    By skatona in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 09-12-2006, 05:51 AM
  5. gas pipe sizing
    By sulconst2 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 07-11-2005, 08:57 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •