What is this?

Users who are viewing this thread

Carrud

DIY'er
Messages
20
Reaction score
0
Points
1
Location
Los Angeles area
House in So. California, built around 1965. Doing a master bath remodel. Did demo of the stall shower and found this in the plumbing wall. I'm sure this is vent pipes, but I don't know why the cleanout opening (if that's what it is called?) that was in the wall.

What is this for? I will be replacing the shower drain and trap, and if I were to replace this pictured area (not sure yet) with ABS what is best to do here?

NOTE: I definitely need to do something about this area because that cleanout piece sticks proud of the wall stud. It didn't bother the previous fiberglass shower but bothers me now with where I'm headed.

Many Thanks, Clark

(PS, sent here by the great folks at the John Bridge Forum)

2013-07-04 Master Bath Vent Pipe 1.jpg2013-07-04 Master Bath Vent Pipe 2.jpg
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
Most of us would call it "using what we have in the truck". The same thing could be accomplished with a vent bent, minus the cleanout.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
It's probably what they call a revent. IF that's the case, it's a little low - code today wants it 42" above the floor or 6" above the highest flood plane that vent serves, whichever is higher. They may have used the T because they didn't have an elbow. At that point, the vent shouldn't need to be snaked.
 

JohnjH2o1

Plumbing Contractor for 49 years
Messages
1,188
Reaction score
13
Points
38
Location
Florida
6" above the flood rim of the fixture it's serving is correct. Seeing as they're nothing connected to it above the floor I would say it's serving a tub or shower. In which case it would be 6" above the flood rim and perfectly legal.

John
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; In which case it would be 6" above the flood rim and perfectly legal.
The code reads 6" above the floor rim OR 42" above the floor, whichever is HIGHER, so it is NOT "perfectly legal".
 

Carrud

DIY'er
Messages
20
Reaction score
0
Points
1
Location
Los Angeles area
Based on the info provided above I traced these drains. I see the one on the left goes down to the first floor sink and vents to the roof. The one on the right is for this second floor shower connection only and vents to the left side pipe. So it seems this would in it's present form be legit from the 6"/42" standpoint. ??

Sorry I did not provide the info about this being on the 2nd floor, which perhaps may have been good info for your replies.


Many Thanks, Clark

Many Thanks, Clark
 