    Default Supply valve too close

    The supply valve on my toilet is 1" off centerline of the toilet. I am thinking of ordering a new Toto Drake CST744EG (elongated bowl), but concerned the supply valve will hit the trap at the back of the bowl.
    Name:  P1020570.jpg
Views: 108
Size:  25.8 KB

    Does anyone know the clearance from the trap at the back of the bowl to the wall. Or conversely, does someone make low profile supply valve.

    Thanks for the help and thanks for the great information in this forum.
    Last edited by Terry; 06-30-2013 at 09:47 PM.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    Dahl makes a right-angle shutoff valve, that, should you need one, would solve that issue. I'd try what you have - it may fit. But, it's not a bad idea to change the shutoff and hose when you replace a toilet, especially if the valve is a multi-turn valve verses a 1/4-turn one.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    Water supply location specs can be a bit confusing. The recommended location would place the supply directly below the toilet inlet. However, with the use of the right angle valve as Jim describes and a flexible supply line, these specs are not absolutes. If you were going to use a solid supply pipe that has to be custom bent to fit, then you might have a problem.

  4. #4
    DIY Senior Member wjcandee's Avatar
    Join Date
    Apr 2012
    Location
    New York, NY
    Posts
    1,590

    Default

    The base of the bowl of the original Drake (CST744S or SG in your case) extends just about 10.5" towards the wall from the center of the closet bolts. You get a smidge more as you get higher above the floor as there is a slight angle to the porcelain away from the wall. So if you're on a 12" rough-in, you have about 1.5" between the base and the wall. I can't tell from your photo, but it looks like you might have more than that sticking out right now.

    Here's the brochure for the Dahl valve Jim was talking about. http://www.dahlvalve.com/PDF/Skirted..._Brchre_US.pdf

    It comes in various styles and various attachment methods (i.e. compression, sweat, etc.). If that's a piece of copper pipe coming out of your wall, attaching a compression angle stop like the Dahl valve should be pretty straightforward. Depending on your skill set, you could just put a 90 on there, although the Dahl solution probably looks a little more aesthetically-pleasing.

    Good luck and let us know if we can help.

Similar Threads

  1. toilet water supply turnoff too close to floor
    By plumbing-newbrain in forum Toilet Forum discussions
    Replies: 5
    Last Post: 03-29-2012, 06:13 PM
  2. Sprinkler valve doesn't appear to close
    By Rshane in forum Irrigation / Sprinkler Forum
    Replies: 1
    Last Post: 09-10-2009, 01:20 PM
  3. Floor supply line too close?
    By stking in forum Toilet Forum discussions
    Replies: 5
    Last Post: 08-25-2008, 05:59 AM
  4. Copper Supply Pipes - how close to outside wall
    By DrummerDad in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 15
    Last Post: 07-16-2007, 04:52 AM
  5. Valve will not close
    By denver.home in forum Irrigation / Sprinkler Forum
    Replies: 2
    Last Post: 05-20-2007, 07:12 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •