Thread: Leakage from T/P valve...still

  1. #1
    DIY Junior Member jonredraider's Avatar
    Join Date
    Jun 2013
    Location
    San Antonio
    Posts
    1

    Default Leakage from T/P valve...still

    Hi,

    We have two tank gas water heater each with expansion tanks. Recently we noticed that the T/P was leaking on our porch. Thinking I had isolated it to one tank, I replaced the valve with one from Lowe's. I then noticed that the other one was still leaking, so I replaced the other. Still leaked.

    Did some research and found that whole house water pressure could be the cause and remembered hearing that my neighborhood had very high pressure though I do have a PRV. Had the utility come out and they measured 150 at the meater and 80 at the house with low volume. They concluded the PRV was bad or needed adjustment.

    Had a plumber out today and they tested house pressure at an outdoor spigot and it was at 150. So they dug up and replaced the PRV and left saying the house was at 75. I also had them check the pressure in the hot water heater expansion tanks and they said they did and added some air.

    As they left we noticed the T/P still leaking. He exercised the valves and it was still leaking. He took apart the T/P outlet pipe at the tanks and we saw no dripping at the valve. He then blew the residual water out of the pipe by mouth. They left hoping that all was good.

    Well, they have been gone for a couple of hours and the hot water T/P is still leaking. I don't know what else this could be! Any thoughts are appreciated.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    FWIW, a T&P valve leaks for one of three reasons, two are safety, one is that it is defective (or gummed up, effectively defective). The two safety factors are excessive temperature OR pressure. If I had to guess, I'd guess one of your expansion tanks is shot and your pressure is still spiking after hot water use then during the recovery. If you knock on them, each should be nearly empty and sort of ring rather than thud. Also, the only way to check the pressure on these is if you've shut the water supply off, then opened a hot faucet until the water stops running - then, while the faucet is still open, you can check and adjust the air pressure. That part is easy - a tire pressure gauge and a bicycle tire pump. If you get water out of the air valve, the tank is shot. The pressure should be the same as what your PRV is set to. The shaft and or seals on a T&P valve can get debris caught on or in them, and that can cause them to leak. At that point, you need to replace them.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. Valve orientation + leakage problem
    By miamicanes in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 03-15-2010, 05:32 PM
  2. Problem with Tilt Valve not sealing and allowing continuous leakage
    By Jkeyler in forum Toilet Forum discussions
    Replies: 8
    Last Post: 02-23-2010, 03:00 PM
  3. sprinkler valve air leakage...
    By sclancy in forum Irrigation / Sprinkler Forum
    Replies: 1
    Last Post: 09-17-2008, 08:16 AM
  4. Valve leakage @ Low Pressure
    By kinderlind in forum Irrigation / Sprinkler Forum
    Replies: 2
    Last Post: 07-04-2008, 10:05 AM
  5. Sign of Leakage?
    By eliddon in forum Toilet Forum discussions
    Replies: 3
    Last Post: 07-04-2007, 04:34 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •