Thread: Extending gas line for NG bbq

  1. #1
    DIY Junior Member minus08's Avatar
    Join Date
    Jan 2012
    Location
    PA
    Posts
    8

    Default Extending gas line for NG bbq

    My next purchase is going to be a natural gas grill. I will need to get NG out to the backyard. I will not need anything run underground as I'd like to have the quick disconnect coming out of the back of the house well above grade. In the basement I have a 1/2" line running off of a 1" line. The 1/2" is going up to the 1st floor laundry area for the location of a gas dryer. I have an electric dryer and will never get a gas dryer. Also I am really not that concerned about the needs of any future owner as far as their clothes drying preference.

    Was contemplating just taking this gas dryer line apart back to the 1" x 1/2" Tee and rerouting the 1/2" run toward the outside. The run toward the outside would be about 40' from the point of the Tee. The grill will be about 40,000 BTU. The gas piping is black iron pipe. Have no qualms about installing new run as I have worked with black pipe alot. Is 1/2" ok for that distance? Also is there anything to mount on outside of house where the gas line exits? The house is vinyl siding at the location where the gas line would exit.

  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,943

    Default

    The National Fuel Gas Code book will give you the sizing requirements.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    DIY Senior Member Hammerlane's Avatar
    Join Date
    Oct 2011
    Location
    Ohio
    Posts
    252

    Default

    Quote Originally Posted by minus08 View Post
    Was contemplating just taking this gas dryer line apart back to the 1" x 1/2" Tee and rerouting the 1/2" run toward the outside. The run toward the outside would be about 40' from the point of the Tee. The grill will be about 40,000 BTU. The gas piping is black iron pipe. Have no qualms about installing new run as I have worked with black pipe alot. Is 1/2" ok for that distance? Also is there anything to mount on outside of house where the gas line exits? The house is vinyl siding at the location where the gas line would exit.
    You say the run is about 40 feet. You will be OK with 1/2" for that length. 40' of 1/2" will deliver 63K BTU per hour at 2 psi. For reference though you should establish what the develeoped pipe length is. By that I mean the actual length may only be 40 feet but you have to add in any 90's or Tee's as its equivalent length of pipe. A 1/2" 90 is equal to 1.55 feet and a 1/2" Tee is equal to 3.10 feet.

    So if you had say 6-90's and 1- Tee, that would be an additional 12 feet of pipe to consider for calculations. But you are well within the limits according to the NFGC table 6.2(a)

  4. #4
    DIY Senior Member Hammerlane's Avatar
    Join Date
    Oct 2011
    Location
    Ohio
    Posts
    252

    Default

    Quote Originally Posted by minus08 View Post
    In the basement I have a 1/2" line running off of a 1" line. The 1/2" is going up to the 1st floor laundry area for the location of a gas dryer. I have an electric dryer and will never get a gas dryer. Also I am really not that concerned about the needs of any future owner as far as their clothes drying preference.
    I know you dont care about leaving a line for a future dryer but if you could eliminate that 1 x 1 x 1/2 Tee and replace that with a 1 x 1 x 3/4 Tee, you would be able to run 3/4 toward the grill until you need to reduce down to 1/2. Also off that 3/4 line you could add a 3/4 x 3/4 x 1/2 Tee for a future dryer and just plug it. The cost to do it this way would be maybe another $15.

    Quote Originally Posted by minus08 View Post
    Also is there anything to mount on outside of house where the gas line exits? The house is vinyl siding at the location where the gas line would exit.
    Vinyl siding mouting block can be used
    Attached Images Attached Images  
    Last edited by Hammerlane; 06-17-2013 at 09:29 AM.

  5. #5
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,943

    Default

    Quote Originally Posted by Hammerlane View Post
    You say the run is about 40 feet. You will be OK with 1/2" for that length. 40' of 1/2" will deliver 63K BTU per hour at 2 psi. For reference though you should establish what the develeoped pipe length is. By that I mean the actual length may only be 40 feet but you have to add in any 90's or Tee's as its equivalent length of pipe. A 1/2" 90 is equal to 1.55 feet and a 1/2" Tee is equal to 3.10 feet.

    So if you had say 6-90's and 1- Tee, that would be an additional 12 feet of pipe to consider for calculations. But you are well within the limits according to the NFGC table 6.2(a)
    How do you know he is running a 2lb. psi system? 2lb.psi is not too common inside the structure for Nat gas
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  6. #6
    DIY Senior Member Hammerlane's Avatar
    Join Date
    Oct 2011
    Location
    Ohio
    Posts
    252

    Default

    Quote Originally Posted by Tom Sawyer View Post
    How do you know he is running a 2lb. psi system? 2lb.psi is not too common inside the structure for Nat gas
    I made a mistake, that table is for (less than 2 psi) systems, not 2 psi exactly.

  7. #7
    DIY Senior Member bluebinky's Avatar
    Join Date
    Aug 2011
    Location
    Santa Clara, CA
    Posts
    355

    Default

    As Tom says, you need to look at the gas distribution as a whole to be 100% sure. Depending on what else is going on, 1/2 inch may or may not be OK.

    It's not hard at all. You just need to draw a simple diagram and follow the procedure of looking at tables in the book.

Similar Threads

  1. Extending a well casing
    By Schwab Electric in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 11-25-2011, 06:00 AM
  2. Extending an Existing Well
    By lzenglish in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 08-08-2009, 02:13 PM
  3. Extending Outdoor Water Line
    By MLyle in forum Irrigation / Sprinkler Forum
    Replies: 2
    Last Post: 04-23-2008, 08:23 AM
  4. Extending a Natural Gas Line to Grill
    By sbphuntington in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 04-11-2008, 02:39 AM
  5. Cutting and extending ABS
    By hans_idle in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 01-24-2008, 06:12 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •