    Default By pass plug {suntec pump}

    I want to add the two pipe system to my oil burner, bought the by pass plug,1/16 for a A pump,should it have a 1/16 hole ?

  2. #2
    DIY Member
    Join Date
    May 2012
    Location
    Brooklyn, New York, United States
    Posts
    46

    Default

    to convert to 2 pipe system, remove return port plug and install by pass plug, then connect return line, shut off valve on return line must not be installed.