    Default Baxi Luna issue

    Hey,

    Baxi Luna 310 Fi combi boiler


    I generally don't get into extensive service on gas appliances.
    Had a customer call with "no hot water at shower" but has very hot water at lav and kitchen sink. I suspected moen cartridge so I replaced it.
    After nosing into it more, there is hot water when using the shower head, but not when using tub spout, unless moentrol valve is open to allow only a small amount of flow then it gets hot.
    this tells me the boiler is not keeping up with the higher flowrate of the tubspout vs showerhead or sink faucets.
    This boiler has been in for a few years I believe and this problem only started after the original installer performed a service on it and changed a diverter inside the boiler that controls the flow for heating/domestic water load.
    There shouldn't be any control required for heat vs domestic flow as there is no call for heat, just to be sure I turned the boiler to only domestic hot water mode and the problem remains, making me suspect its not the diverter itself.
    Any ideas what else could cause this?

  2. #2
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,730

    Default

    The thing can deliver 100,000BTU/hr, which is enough for a shower flows, but pretty marginal for tub fill rates. It's possible that the heat exchanger is liming/scaling up if this is a hard-water area, but whatever the service guy hacked inside the boiler is the more likely culprit, and you may not be fully backing out whatever tweaks he made. Did changing modes make ANY difference? (Measure the water temps at the faucet in both modes, running at least 10 gallons in each mode.l)

  3. #3

    Default

    thanks for the quick reply.

    the previous guy simply removed the diverter valve assembly as a whole and replaced it with a new replacement - I wouldn't say he "hacked" anything in.

    secondly changing the mode made no difference at all.

    I got the service manual online and it doesn't show any procedure to adjust the diverter assembly.

  4. #4
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,730

    Default

    If it screwed up the DHW output, intentional or not, it was hacked. Was it really the right part? Was it installed correctly? If the change in performance was concurrent with the swap out, it's a flag. Why was it changed out?

  5. #5
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,946

    Default

    I'm betting in a limed up exchanger
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,442

    Default

    SOme of these things use a flow restrictor to help ensure you can get enough heat rise. If he changed that, allowing more flow, it will never be able to get as big of a delta-T as it did before.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7

    Default

    As far as I can tell without pulling it back out it looks to be the same assembly as he took out, it appears that everything is where it should be as far as connections to it. he is a local heating contractor that I work with often and is professional in workmanship.
    I do agree that the new problem coinciding with the part swap is not coincidental, but in fact something during the process caused this.
    I was suspecting that the filter in the flow restrictor may need cleaned and that the heat exchanger has likely never been flushed.

    thanks for all the help so far guys

  8. #8
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,442

    Default

    On one (long since replaced) boiler I had, they specified various restrictors depending on how the burner was jetted...the external appearance is pretty much the same...it may have been replaced with a larger one. The only way to tell is to look very carefully, and maybe even check part numbers. Some may be marked on the outside. Try this: at an unrestricted faucet (say the WM supply), run the hot out full force and measure the flow rate into a bucket. Compare that to what the boiler says it should have for a flow restrictor. You may need to do this for a few minutes to equalize things between the tempering valve and what may have been stored inside while the boiler comes up to full temperature (not much, but it could skew the results - you want steady state, and that takes a bit of time to achieve).
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. Drainage issue
    By Austin1983 in forum Lawn Care/Landscaping
    Replies: 2
    Last Post: 08-30-2012, 05:15 AM
  2. Thoughts on Baxi Luna HT Systems
    By ak99588 in forum Tankless Water Heater Forum
    Replies: 0
    Last Post: 03-20-2012, 07:44 PM
  3. Hot water issue
    By Dan75 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 03-13-2012, 10:58 PM
  4. Hot Water Issue
    By Scott-unlv in forum Shower & bathtub Forum & Blog
    Replies: 5
    Last Post: 03-10-2009, 11:07 AM
  5. need assistance with baxi luna operation
    By SuperSewist in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 01-10-2009, 06:02 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •