    Default Minimum Trap Arm Length

    Is there a minimum trap arm length for a washer stand pipe? Right now, I have the outlet from the P-trap butting tight to the sanitary tee. Is this too close? Will this create a S trap?

    Thanks for any advice!

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    I think I read two pipe diameters, but don't quote me on this...
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,644

    Default trap

    Depending on how you measure the trap arm, the two fittings may "force" it to be at least two diameters between the "pipes". IF you have a proper vent you cannot "create" an "S" trap as long as the maximum length is within the parameters for the pipe size.
    Licensed residential and commercial plumber

  4. #4
    DIY Junior Member denikar's Avatar
    Join Date
    Feb 2013
    Location
    Canton, MI
    Posts
    13

  5. #5
    DIY Senior Member wjcandee's Avatar
    Join Date
    Apr 2012
    Location
    New York, NY
    Posts
    1,590

    Default

    The third page of this pdf has a diagram and a table that may be helpful. You measure, according to it, from the interior portion of the vertical pipe on the p-trap (the weir is where it tips over to the horizontal) TO the closest portion of the vent pipe. The top right diagram on the third page of the document makes it clearer. 3" pipe has a minimum 6" trap arm.

    http://www.klickitatcounty.org/build...andout0411.pdf

  6. #6

    Default

    our code requires a minimum of 2 pipe diam to avoid crown venting

Similar Threads

  1. Minimum Length Between 3/4" Copper Fittings
    By Fraser Jim in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 03-22-2013, 01:02 PM
  2. trap tailpiece minimum length
    By stevenrobertburke in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 02-08-2011, 07:39 PM
  3. Minimum trap arm length?
    By mtbonn in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 04-19-2010, 07:45 AM
  4. Minimum Trap Arm?
    By dlarrivee in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 02-06-2010, 10:03 PM
  5. Trap arm height, minimum tail piece length
    By davefoc in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 11-18-2009, 09:20 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •