    Default Peninsula electrical outlet?

    I am putting in an island as part of my kitchen remodel. It will be 72" long with a 10" overhang for a total of 82" on the long end, cabinets on one side and a 10" over hang on the other end for a total of 36" wide.

    I am not sure where to put the outlet. I see it is often put ont the long end but i have an over hang there as well. I am unsure of the code but are you allowed to put an outlet on a side where you have an overhang?

    I can put one on the wall where the pensula starts but the code says i need on one the *****ula as well. This is a non permit job so usability is more important then code in this respect.

    thanks
    mark

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,615

    Default outlets

    I have three outlets on my island under the overhang. YES, you can put them there.
    Licensed residential and commercial plumber

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    Kitchens have some specific rules about the max distance between receptacles. On that length you may need three. Most kitchen appliances' cords are fairly short because they often have some significant heating elements. I think the max is 4' between for a kitchen.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by marklamberti View Post
    This is a non permit job so usability is more important then code in this respect.

    thanks
    mark
    No permit no advice

  5. #5
    DIY Junior Member marklamberti's Avatar
    Join Date
    May 2013
    Location
    staten island
    Posts
    5

    Default

    yea i know the 2-4 foto rule but i also dont think your supposed to have them towards the top of the pensula if there is an overhang due to the same reasoning.

  6. #6
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Ten inch overhang???

    Get over it. Put them in.

  7. #7
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    Whether you get a permit or not, it may come back to bite you later if you don't. You can always exceed the code minimum, you definitely should not shortchange it.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  8. #8
    DIY Member Stuff's Avatar
    Join Date
    Mar 2013
    Location
    Pennsylvania
    Posts
    36

    Default

    Code says you can put the required outlet where there is an overhang of 6" or less and then not more than 12" below the counter top. NEC 210.52(C)(5) exception

    It is not usability but safety. Most kitchen appliances have short cords and won't easily reach the outlet.

    Either add 4" to your cabinets or cut 4" off the counter top length.

  9. #9
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    here is the answer you are seeking
    http://www.arnev.com/AP-FDN-300-A-W-P.html

  10. #10
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by jwelectric View Post
    here is the answer you are seeking
    http://www.arnev.com/AP-FDN-300-A-W-P.html
    What JW showed you there is a "monument". They are very common in open plan offices, were power and telecommunications need to come up out of a floor to service desks arranged without partitions or walls.

    There are many manufacturers with many designs, if that one does not suit you.

    Or just change the 10" overhang to 6".

  11. #11
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by marklamberti View Post
    ...cabinets on one side and a 10" over hang on the other end for a total of 36" wide.

    I am not sure where to put the outlet. ....

    thanks
    mark
    Hang on.

    Are the cabinets built yet?

    The cabinets face away from the side that has the overhang? They are close to the front edge of the counter on that side?

    Either have the cabinets have a 2" wide void between each of them such that you can set an outlet vertically between them, or have them have a 3" wide rail along the top such that you can install two or three outlets on their sides just under the counter top, lying on their sides.

  12. #12
    DIY Junior Member marklamberti's Avatar
    Join Date
    May 2013
    Location
    staten island
    Posts
    5

    Default

    Thanks for the ideas guys. I saw that code about when the overhang is greater then 6". I dont want to do a pop up but i like the idea of using a spacer between the cabs and putting it there.

    If i curve the end of the coutertop on the end of *****ula can i put one towards the corner?

Similar Threads

  1. Outlet inside peninsula cabinet
    By JMingrone in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 12-14-2012, 07:37 AM
  2. Electrical Outlet For Welding
    By willplunk in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 08-14-2008, 08:19 AM
  3. kitchen peninsula outlet
    By geandham in forum Electrical Forum discussion & Blog
    Replies: 11
    Last Post: 06-25-2008, 04:45 AM
  4. Electrical outlet question
    By brosnt1 in forum Electrical Forum discussion & Blog
    Replies: 32
    Last Post: 01-14-2008, 04:04 AM
  5. Electrical Work, Dryer Outlet
    By toolbeltbabe in forum Remodel Forum & Blog
    Replies: 10
    Last Post: 07-20-2006, 08:26 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •