Thread: Rapid Cycle Well Pump

  1. #1
    DIY Junior Member warrens's Avatar
    Join Date
    Jul 2012
    Location
    quebec
    Posts
    18

    Default Rapid Cycle Well Pump

    Hi

    (NB SUBJECT SHOULD BE RAPID CYCLE NOT RECYCLE!)

    I have had constant problems with my well pump (400 feet deep) running dry and then either frying the pump or heating the pipe up so much that it bursts and my well guy comes and pulls it out to replace the piece of pipe.

    the main reason I believe this was happening (apart from the fact that I have a very low producing well which means I have to manage water very carefully) was because my wires were the wrong gauge so the pumptech was never shutting the pump off in time to save this.

    I believe I have mainly solved this problem since purchasing a cycle sensor valve through suggestions on this site.

    That has worked well telling me when the well is dry and shutting off the valve, however I am now having a RAPID CYCLING problem. I have water in the well and if I turn off the RAPID CYCLING reset then the pump works fine. Otherwise it seems to go into recycle when it reaches the cut off pressure.

    I have 2 thoughts

    1. there is a hole in the pipe as before, however it is still able to pump water up
    2. the pressurized water tank has a leak, however it appears to be working fine and has good pressure

    any thoughts suggestions welcome


    I can bypass the RAPID CYCLE cut off but dont want to fry my pump again

    thanks Warren
    Last edited by warrens; 05-19-2013 at 03:28 PM. Reason: error in original

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,683

    Default

    Isolate the tank outlet and see if you are losing pressure when the pump shuts off, assuming you don't have a topside checkvalve to mask it.

    Are you sure it is recycle and not rapid cycle?

    Quoting from http://www.cyclestopvalves.com/prod_sensor_geninfo.html
    The "Rapid Cycle" feature of this relay monitors the duration of time the pump is on. If the pump "run time" is shorter than the Cycle Sensor minimum set time, the pump will be shut down before damage from cycling occurs. Length of acceptable minimum pump run time is adjustable and can be set for as little as 0 seconds to as much as 600 seconds. (Rapid cycling can be caused by water logged or improperly sized tanks, improper pressure switch settings, control malfunctions, broken check valves, and chattering contacts.)

  3. #3
    DIY Junior Member warrens's Avatar
    Join Date
    Jul 2012
    Location
    quebec
    Posts
    18

    Default

    Thanks LLigetfa

    Yes you are correct I should have said rapid cycle. I will have a look re losing pressure when the pump shuts off and get back to you

  4. #4
    DIY Junior Member warrens's Avatar
    Join Date
    Jul 2012
    Location
    quebec
    Posts
    18

    Default

    Hi

    I checked for losing pressure and it seems ok-it stays at a constant pressure

  5. #5
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,683

    Default

    Then do a drawdown test to see if the tank is waterlogged.

  6. #6
    DIY Junior Member warrens's Avatar
    Join Date
    Jul 2012
    Location
    quebec
    Posts
    18

    Default

    Thanks, can you just guide me as to what exactly in simple terms I have to do to do the drawdown test to evaluate this

    thanks

  7. #7
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,683

    Default

    When the pump reaches the shutoff pressure, draw off water from the tank into a pail and measure how many gallons you can draw down until the pump kicks back on. That will tell you how much drawdown you have. If you don't get as much drawdown as you should, then there is probably a leak in the bladder.

    For example, a 40 gallon tank should give you 12 gallons of drawdown with a 30/50 pressure setting.

  8. #8
    DIY Junior Member warrens's Avatar
    Join Date
    Jul 2012
    Location
    quebec
    Posts
    18

    Default

    Thanks again LLigetfa,

    I have done the drawdown test and it seems fine I get about 8 gallons on a 20 gallon tank at 20/40 pressure setting. I also tested the pressure of the tank empty and at the cut off and cut in and it all seems ok-One thing though.. when it gets close to the cut off, i do hear sounds from the tank, that to me sound like a bladder releasing from something, itself or the side.

    I dont know whether it always has this sound but I just assumed that it acts like a balloon and when it gets to the higher pressure there shouldnt be any notable sounds of the bladder moving?

  9. #9
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,683

    Default

    Is the pressure switch on the tank Tee or otherwise close to the tank? Does the pump start and stop normally through the pressure range? Have you timed the cycles to see how long the pump runs and how long it stops? What time is the rapid cycle set to?

    If the cycles are short and frequent, you might want to consider a larger tank or a CycleStopValve.

  10. #10
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    If you didn’t adjust the Rapid Cycle function of the Cycle Sensor, it is set at 30 seconds. If you are not getting at least 30 seconds of run time, something is wrong. Your pressure switch maybe too far from the tank, or you could have a faulty check valve. Rapid cycling and pumping the well dry are two of the worst things you can do to the pump. The Cycle Sensor will catch both of those things, but you need to solve the problem or the Cycle Sensor will keep tripping.

  11. #11
    DIY Junior Member warrens's Avatar
    Join Date
    Jul 2012
    Location
    quebec
    Posts
    18

    Default

    Hi

    My switch is close to the tank and the sensor was set at about 80, I have reduced it to 10 and it seemes to have stopped the rapid cycle error. I have tried at 40 and it still occurs but at 30 it seems ok so far

    the pump pumps for more than 30 seconds ( acouple of minutes maybe-. it seems to trip out when the pressure switch cut off activates.

  12. #12
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    Make sure your pressure switch is not double bouncing on shut off.

  13. #13
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,683

    Default

    Quote Originally Posted by warrens View Post
    ...it seems to trip out when the pressure switch cut off activates.
    Check to see if you are getting water hammer, perhaps from a bad checkvalve. That could make your pressure switch bounce.

  14. #14
    DIY Junior Member warrens's Avatar
    Join Date
    Jul 2012
    Location
    quebec
    Posts
    18

    Default

    thanks for your perseverance guys

    LLigetfa-I am pretty sure I don't have a check valve and haven't noticed water hammer anywhere
    Valveman- Double bouncing? Is that simply looking at the contacts and seeing if they release and then reattach quickly?

  15. #15
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    Quote Originally Posted by warrens View Post
    Valveman- Double bouncing? Is that simply looking at the contacts and seeing if they release and then reattach quickly?
    Yes. If it is double bouning the contacts on pump shut off, then you probably have a bad check valve, like LL said, which you must have one of somewhere.

Similar Threads

  1. Jet pump rapid short cycling at cut-out
    By FRS in forum Pumps and Tanks Well Forum & Blog
    Replies: 26
    Last Post: 06-19-2013, 12:49 PM
  2. Suggestions for rapid cycling pump
    By Hunter01 in forum Pumps and Tanks Well Forum & Blog
    Replies: 7
    Last Post: 04-17-2013, 10:42 AM
  3. Well pump short cycle
    By solman in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 01-28-2013, 05:04 PM
  4. Pump cycle question
    By boomer2 in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 07-08-2011, 08:05 AM
  5. pump struggling to get through cycle
    By Byoung5187 in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 10-02-2006, 08:50 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •