    Default How small can my service neutral be when most of the load is 240v?

    Non-residential 120/240 single phase service. 320amp meter to (2) 200 amp panels. The distance from the meter on a pole to service panels are 50ft. I'm running 3/0 copper for the phase conductors. #6 for the grounds.

    First panel will have 160 amp continuous load. Everything connected will be 240v. The second panel will have 40 amps of 120v and 120 amps of 240v.

    Even though there is no 120v equipment on the first panel, I can't go lower than the GEC, right? #6?

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    can't go lower than the GEC

  3. #3
    DIY Junior Member Glennsparky's Avatar
    Join Date
    Oct 2012
    Location
    Oviedo, FL near Orlando
    Posts
    22

    Default

    Quote Originally Posted by tkeoki View Post
    ...Even though there is no 120v equipment on the first panel, I can't go lower than the GEC, right? #6?
    Or no neutral. There's no code forcing you to bring a neutral to a box. But, then you could never use that box for a 120v load.

  4. #4
    DIY Senior Member bluebinky's Avatar
    Join Date
    Aug 2011
    Location
    Santa Clara, CA
    Posts
    354

    Default

    I thought 3/0 copper service required #4 GEC. I'm probably reading the wrong table again, though...

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by bluebinky View Post
    I thought 3/0 copper service required #4 GEC. I'm probably reading the wrong table again, though...
    You are correct about a #4

Similar Threads

  1. Replies: 2
    Last Post: 11-28-2011, 03:29 PM
  2. Replies: 2
    Last Post: 03-23-2011, 06:34 AM
  3. 240v 60amp service
    By John07 in forum Electrical Forum discussion & Blog
    Replies: 12
    Last Post: 01-30-2011, 09:51 AM
  4. service riser needs for an electrical service upgrade?
    By myladyfae in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 02-22-2010, 11:28 AM
  5. 1/2" service line too small?
    By kurtk in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 07-25-2005, 02:05 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •